battery shunt

Options
andy300z
andy300z Solar Expert Posts: 39
Hello,
I am in the process of purchasing the trimetric 2020 battery monitor . I have a 24v system which will be 4 batteries 12v appx total 400ah. This is a starter set up which i will be adding more batteries in the future. Please advise on which shunt i should get a 100a or 500a. Thanks

Comments

  • mikeo
    mikeo Solar Expert Posts: 386 ✭✭✭
    Options
    Re: battery shunt
    Please advise on which shunt i should get a 100a or 500a. Thanks
    I believe that you will need the 500 amp shunt for a system that size.
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Options
    Re: battery shunt

    Shunts are sized acording to how much current (amps) you expect to pull thru them. A 48V system that uses less current, can use smaller shunts.

    I would not try to get a shunt to match the peak surge current (motor starting), but would tend to size it to sustained loads.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • BB.
    BB. Super Moderators, Administrators Posts: 33,439 admin
    Options
    Re: battery shunt

    Remember that shunts have voltage drop too. To small of one may cause problems with surf currents.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset