Battery: Rules of Thumb & Questions
mnittler
Solar Expert Posts: 63 ✭✭✭
I am looking for simple "Battery Rules of Thumb" (Inverter Related)
Battery Charger amps required to charge X Ahr battery bank in y hours?
Battery Ahr capacity = x Minimum recommended Charge current?
Battery Ahr capacity = y Maximum recommended Charge current?
If you have 6 each 8VDC 100 amp batteries in series for 48vdc is it considered 600 amp or 100 amps?
Generator size (watts) recommended to charge X Ahr battery bank in Y hours?
Battery Amps (Ahr) required for x watts inverter output for y hours?
(Assume x=500 watts 240vac split phase, y=6hrs)
Solar Panel total x watts required to charge Y amps battery bank in z hours?
Wire size for x Ahr battery bank of Y volts with Z length?
The batteries I am looking at (C&D) are rated in amps, How does this relate to others that are rated in Ahr?
Weight of battery * x = Amp capacity?
Battery normal % max charge voltage?
Battery normal % min discharge voltage for long life?
Throw any other Battery Rules of Thumb you can think of here also so they will all be in one place.
I know that these "Rules of Thumbs" will be just that, guides, not the holy grail.
Battery Charger amps required to charge X Ahr battery bank in y hours?
Battery Ahr capacity = x Minimum recommended Charge current?
Battery Ahr capacity = y Maximum recommended Charge current?
If you have 6 each 8VDC 100 amp batteries in series for 48vdc is it considered 600 amp or 100 amps?
Generator size (watts) recommended to charge X Ahr battery bank in Y hours?
Battery Amps (Ahr) required for x watts inverter output for y hours?
(Assume x=500 watts 240vac split phase, y=6hrs)
Solar Panel total x watts required to charge Y amps battery bank in z hours?
Wire size for x Ahr battery bank of Y volts with Z length?
The batteries I am looking at (C&D) are rated in amps, How does this relate to others that are rated in Ahr?
Weight of battery * x = Amp capacity?
Battery normal % max charge voltage?
Battery normal % min discharge voltage for long life?
Throw any other Battery Rules of Thumb you can think of here also so they will all be in one place.
I know that these "Rules of Thumbs" will be just that, guides, not the holy grail.
19.76kw Solar/GT Enphase IQ7+ MicroInverters
5.40kw Solar/GT ABB/Aurora 300 MicroInverters (AC coupled to Schneider/Xantrex XW6048 output)
6.00kw Solar/Hybrid Xantrex XW6048 Inverter w/2 strings Trojan L-16E-AC Batteries (48VDC)18kw Kohler Propane Generator
Comments
-
Re: Battery: Rules of Thumb & QuestionsI am looking for simple "Battery Rules of Thumb" (Inverter Related)
Battery Charger amps required to charge X Ahr battery bank in y hours?
depends on how much batteries have been discharged. Generally requires 3-5 hrs minimum to recharge a lead acid battery from 30% SOC
Battery Ahr capacity = x Minimum recommended Charge current?
should be to produce at least 5-10% of AH rating for current.
Battery Ahr capacity = y Maximum recommended Charge current?
Charger should be able to produce 15-25% of AH rating in recharge current.
If you have 6 each 8VDC 100 amp batteries in series for 48vdc is it considered 600 amp or 100 amps?
It 100 AH when in series. You're getting the higher voltage benefit. Batteries in parallel add AH's for total.
Generator size (watts) recommended to charge X Ahr battery bank in Y hours?
Depends on charger efficiency, answer above for current X battery voltage.
Battery Amps (Ahr) required for x watts inverter output for y hours?
(Assume x=500 watts 240vac split phase, y=6hrs)
Assume 87% inverter efficiency, would be 500/0.87 = 575 watts from battery div by 48 volts = 12 amps.
Solar Panel total x watts required to charge Y amps battery bank in z hours?
just like charger requirement above with charge controller efficiency loss factored in.
Wire size for x Ahr battery bank of Y volts with Z length?
calculate inverter current, look up required wire size for acceptable voltage drop.
The batteries I am looking at (C&D) are rated in amps, How does this relate to others that are rated in Ahr?
Assume these are AGM's, max amp rating has little relation to A-H rating. AGM offer a high discharge rate capability. They are commonly used in UPS which needs short, high current discharge.
Weight of battery * x = Amp capacity?
Depends on battery type. Good deep discharge batteries have thicker plates making them heavier for same A-H rating.
Generally, about 50-70 lbs per 100 AH on a six cell (12v) battery.
Battery normal % max charge voltage?
not a simple answer. There is absorb voltage (14.4 vdc), float voltage (13.4 vdc), and equalizing voltage (15.5 vdc)
Battery normal % min discharge voltage for long life?
not a simple or useable answer. Min voltage depends on discharge current. Lower for higher current, higher for light current drain.
Throw any other Battery Rules of Thumb you can think of here also so they will all be in one place.
I know that these "Rules of Thumbs" will be just that, guides, not the holy grail.
Look throught the forum, there are a lot of references to specific gravity and battery voltage charts. -
Re: Battery: Rules of Thumb & QuestionsI am looking for simple "Battery Rules of Thumb" (Inverter Related)
I know that these "Rules of Thumbs" will be just that, guides, not the holy grail.Battery Charger amps required to charge X Ahr battery bank in y hours?Battery Ahr capacity = x Minimum recommended Charge current?
Battery Ahr capacity = y Maximum recommended Charge current?
For VRLA (AGM or gel) batteries, the practical upper limit is ~30%, IMHO. Some battery manufacturers suggest a higher limit, but this is impractical, again IMHO. A bigger charger can reduce bulk charge time, but not absorb time.If you have 6 each 8VDC 100 amp batteries in series for 48vdc is it considered 600 amp or 100 amps?Generator size (watts) recommended to charge X Ahr battery bank in Y hours?
The ability to deliver 3.5 kVA continuously would probably require a generator rated 20% higher for its surge rating and “market power rating”, or ~4.2 kVA. These are sea-level- and ~60 F ambient temp ratings, so further deratings of ~3.5% per 1,000 ft elevation and ~1 degree per 10 F above 60 F would be required.Battery Amps (Ahr) required for x watts inverter output for y hours? (Assume x=500 watts 240vac split phase, y=6hrs)500 W x 6hrs = 3 kWh / 90% = 3.33 kWh from the battery bank.
3.3 kWh / 48 V nominal = 69 Ah
50% max discharge = 69Ah / 50% = 138 AhSolar Panel total x watts required to charge Y amps battery bank in z hours?Wire size for x Ahr battery bank of Y volts with Z length?The batteries I am looking at (C&D) are rated in amps, How does this relate to others that are rated in Ahr?Weight of battery * x = Amp capacity?Battery normal % max charge voltage?
Battery normal % min discharge voltage for long life?
Battery technical references: HTH,
Jim / crewzer -
Re: Battery: Rules of Thumb & Questions
Thanks for all the helpful battery data.
http://www.cdstandbypower.com
Battery C&D: 4JC-100 can be found under batteries JC then look at 4JC-100.
I was thinking of putting together 2 strings of 6 of these batteries.
(8VDC * 6 batteries = 48VDC)
(100 amps * 2 strings = 200 amps) I guess they rate them differently.
The reason I am confused is the following from battery manufacture website:
1.78 FV/Cell
1 min = 119 amps
15 min = 87 amps
30 min = 67 amps
1 hr = 48 amps (Then is this one ahr?)
2 hr = 33 amps
3 hr = 25 amps
4 hr = 21 amps
5 hr = 18 amps
6 hr = 15 amps
8 hr = 12 amps
12 hr = 9 amps
Anyway what I wanted to know was how long will these batteries last at 500 watts output from inverter? I would just ratio this number for 1000 watts, 2000 watts, etc. From previous post then 200 amp battery bank would be 50% of amps which is 100 amps. 100 * 48 = 4800 watts for 1 hour (or 1200 watts for 4 hrs).
On the weight (this C&D battery weights 100 lbs) , I had figured that if one battery weight is 50 lbs and another of the same voltage is 100 lbs then the 100 lbs battery must be better (thicker plates or something).19.76kw Solar/GT Enphase IQ7+ MicroInverters5.40kw Solar/GT ABB/Aurora 300 MicroInverters (AC coupled to Schneider/Xantrex XW6048 output)6.00kw Solar/Hybrid Xantrex XW6048 Inverter w/2 strings Trojan L-16E-AC Batteries (48VDC)
18kw Kohler Propane Generator -
Re: Battery: Rules of Thumb & QuestionsThe reason I am confused is the following from battery manufacture website:
1.78 FV/Cell
1 min = 119 amps = 1min / 60 min per hr * 119 amps = 1.98 AH
15 min = 87 amps
30 min = 67 amps
1 hr = 48 amps = 1 hr * 48 amps = 48 amp*hours (C/1 rate)
2 hr = 33 amps
3 hr = 25 amps
4 hr = 21 amps = 4 hr * 21 amps = 84 AH (C/4)
5 hr = 18 amps
6 hr = 15 amps = 6 hr * 15 amps = 90 AH (C/6)
8 hr = 12 amps = 8 hr * 12 amps = 96 AH (C/8 )
12 hr = 9 amps = 12 hr * 9 amps = 108 AH (C/12)
Note the above chart is based on the ending cell voltage. 1.75 volts per cell is what we call "dead" (10.5 volts for 12 volt bank, 42 volts for a 48 volt bank).
As you can see, a C/20 or C/100 would have even higher AH ratings.Anyway what I wanted to know was how long will these batteries last at 500 watts output from inverter? I would just ratio this number for 1000 watts, 2000 watts, etc. From previous post then 200 amp battery bank would be 50% of amps which is 100 amps. 100 * 48 = 4800 watts for 1 hour (or 1200 watts for 4 hrs).
So, you are looking at a 48 volt bank and 1,000 watt inverter, and two parallel strings (assume 1/2 inverter current to each string):- 1,000 watts * 1/48 volt bank * 1/0,80 inverter efficiency = 26 amps @ 48 volts for the inverter
- 26 amps / 2 strings = 13 amps per string
Normally, we would tell you to only discharge the battery by 50% maximum for longer life:- 90 AH * 1/13 amps * 0.50 max discharge = 3.46 hours = 3 hrs 28 min
If you want to get more in the details... Inverters are constant power devices. When the battery is first loaded, Vbatt is high. As the battery discharges, the battery voltage falls, and the inverter draws more power.- 1,000 watts * 1/51.2 volt bank * 1/0,80 inverter efficiency = 24.4 amps @ "full" battery
- 1,000 watts * 1/42 volt bank * 1/0,80 inverter efficiency = 29.8 amps @ "dead" battery
On the weight (this C&D battery weights 100 lbs) , I had figured that if one battery weight is 50 lbs and another of the same voltage is 100 lbs then the 100 lbs battery must be better (thicker plates or something).
I am guessing that they are partially populated with lead plates (inside same battery case). As the lower capacity batteries have fewer plates, they take more electrolyte to fill. Battery capacity appears to be roughly proportional to the number of lead plates in each cell.
It looks like purely a cost of manufacturing, rack design, and product mix. It is cheaper for them to put fewer lead plates in a battery than to redesign the battery case, mounts, bus bars, racks, etc. for a physically smaller battery. Batteries have same characteristics other than simply reduced AH rating (and other capacity related differences).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Battery: Rules of Thumb & Questions
Only rule of thumb I'd like to mention, is since this is for a grid tie system, Deep cycle batteries like to be used some, so if you haven't had a need/lose of grid, every couple months I'd draw them down to 80% state of charge, just consider it exersize for the battery...Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
How to calculate the size of the deep cycle battery if you have a DC load (LED lamp) of 48w and the system voltage is 12V and the system has work for 12hrs?
-
Abuu Mohammed wrote: »How to calculate the size of the deep cycle battery if you have a DC load (LED lamp) of 48w and the system voltage is 12V and the system has work for 12hrs?
OK... Assuming you want to run the load for 12 hours and to 50% maximum discharge--The battery discharge rate would be C/24 -- Close enough to C/20 for our "standard" battery ratings (a few vendors do list C/24 rates instead).
48 Watts * 1/12 volts * 12 hours * 1/0.50 maximum discharge = 96 Amp*Hour @ 12 volt battery bank @ C/24 rate or roughly C/20 Rate
Note that battery capacity can vary by ~20% +/- ... And as a battery ages, its capacity does drop. Some vendors call a battery "dead" when it loses 20% of its capacity, others will call it dead when it loses 40% of its capacity.
For you, the battery is "dead" when it can no longer supply 50% of its capacity. Note that battery capacity does fall as batteries get cold, etc.
So, if you are in a a cold climate with an older battery, you may want to put some "fudge factors" in to ensure that your loads are reliably served for the expected life of the battery bank.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
In a nut shell this is what I have learned from this forum.
I call it Rule of Thumb for battery run time. Just an estimate using assumptions.
Inverter Run Time Calculation
Lets assume the following values just for the sake of an example. Substitute your own system parameters.
This Assumes the battery bank if fully charged and only a rough estimate.
Inverter Load = 400 watts
(This is your desired watt load) This just needs to be the average inverter load since in normal operations the loads will probably vary so most of the time it is just a good guess unless it is actually known.
Battery String Voltage = 48 vdc
(This is your system battery voltage normally it will be 6v, 12v, 24v, 48v, etc.)
In my case I have 8 each 6V batteries so the voltage is 48 vdc.
Battery String 20 Hr amp rating from the manufacture = 225 amp/hr
(This is your battery manufacture 20 Hr battery amp rating which can normally be found on the battery manufacture's web site) I have Trojan T-105 batteries so I use 225 amp hrs for the 20 hr amp rate. (20 Hr amp rating is not to be confused with CCA which is an entirely different battery rating. CCA means practically nothing for inverter run time calculations.)
Battery % of charge to be used up = 40% = .40
(If you want to use up 60% of the maximum charge then put .6 here which would leave 40% of full charge) The 40% of maximum charge that I used in this example should give you fairly good battery life. If you drain your batteries completely down to 0% of charge then your battery bank will be ruined and probably not recover. 0% of charge is a lot higher battery voltage than most people think but that is an entirely different subject.
Number of Battery Strings = 1
(Put the number of battery strings here) (This is not the number of batteries, it is the number of parallel battery strings)
Efficiency and Fudge factor = .83
(I just use this value as a combination of modern inverter Efficiency and a Fudge factor for lack of a better number.)
Another assumption is made here: The batteries are in fairly good condition, fully charged, and the manufacture 20 hr amperage rating is correct.
Formula:
Inverter Run Time Hrs = Battery string 20 hr amp rating * Battery percent charge to use up / Inverter load in watts * Battery string Voltage * Number of Battery strings * Eff & Fudge Factor
For the above assumptions here is the calculation:
Inverter Run Time hrs = 225 twenty hr amp rating * .4 percent of maximum charge to use up / 400 watts load * 48 volts * 1 strings * .83 Fudge Factor
= 8.964 run time hours (This is just an estimate for this example and will depend on battery charge, battery age, battery condition, and temperature.)
Remember this is only an estimate to get you started. Every installation will have it's own different situations and values.19.76kw Solar/GT Enphase IQ7+ MicroInverters5.40kw Solar/GT ABB/Aurora 300 MicroInverters (AC coupled to Schneider/Xantrex XW6048 output)6.00kw Solar/Hybrid Xantrex XW6048 Inverter w/2 strings Trojan L-16E-AC Batteries (48VDC)
18kw Kohler Propane Generator -
Have you done anything with ac coupling tje Xantrex to grid-tie inverters ? sara.j at embarqmail dot comhybrid: xw6848 pro with two mppt60, 6 kw pv
17 cell 280ah LiFePO4 storage 14 kw
gridtie: sunny boy sma 2x 5k
gridtie: fronius ag5100 5k
Gateway / Insight Local
xw4548 backup
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed