384 volt lithium-ion battery... for solar storage?
humboolay
Registered Users Posts: 4 ✭
Say one of these 900lb LiFePO monsters was left in a basket on your doorstep one night:
Nominal Voltage: 384 VDC/110 Ah
input charge 20kw; 60 amp max
output 414-348 VDC
Is it a viable option as solar energy storage in a residential setting? Could it be? Should it be? Again, assuming the cost of the battery itself is zero or not far from it. Battery is new as well...
Nominal Voltage: 384 VDC/110 Ah
input charge 20kw; 60 amp max
output 414-348 VDC
Is it a viable option as solar energy storage in a residential setting? Could it be? Should it be? Again, assuming the cost of the battery itself is zero or not far from it. Battery is new as well...
Comments
-
There is (was?) a push towards 380 VDC powered data centers. Many standard 120/240 VAC computer power supplies can take 380 VDC input power. And for AC inverters, 380 VDC can be more efficiently "switched" to 240 VAC when needed.
http://dc-nexus.com/wp-content/uploads/2016/01/dcF-THE-BENEFITS-OF-380V-dc-summary.pdf
If you have the need for lots of power, and can find loads that will take 380 VDC battery bus (plus charging equipment, etc.) it can be used nicely.
HOWEVER--380 VDC from a large battery bank is also dangerous too. Shock, Arc Flash, etc. are things that somebody not trained and not have the right tools/protective gear (and locked rooms/buildings/etc.) can work support.
This was a being pushed for data centers 10 years ago or so... Not sure where the industry is at today.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
humboolay said:Say one of these 900lb LiFePO monsters was left in a basket on your doorstep one night:
I'd have to check it out. I know the native voltage of LiFePo4 is 3.2-2.6 volts, so it' string of cells to get to that high voltage.
I'd figure out if I could reduce it safely to 48v nominal strings and look at finding a BMS that would work for it and how many parallel strings would be acceptable.humboolay said:Is it a viable option as solar energy storage in a residential setting? NOT AS IS, I DON'T KNOW OF ANY AC INVERTERS THAT TAKE 380VOLT Could it be? CERTAINLY IF BROKEN DOWN INTO SMALLER STRINGS Should it be? NOT ON MY DOORSTEP, NOT MY CALL Again, assuming the cost of the battery itself is zero or not far from it. Battery is new as well...
Big questions...
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Just try getting a 384V MPPT solar charge controller
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Yeah.. if you happen to come across one in the 400v range let me know!
-
Here's one, 300- 384 vdc Higher voltage pv input.
Power Inverters, DC To AC Inverters & Solar Panels | AIMS Power (aimscorp.net)
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
I think he is looking for a 400vdc battery charging output...BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
BB. said:I think he is looking for a 400vdc battery charging output...Bill
- Voltage: 384V
- Max VOC of PV arrays: 700V
- Max charging current: 100A
- Inputs: 1 group
- Equalize charging point: 460.8V
- Float charging point: 441.6V
- Over voltage: 512V
- Over voltage recovery: 480V
- Equalize charging recovery: 422.4V
- Stand-by consumption: <.5 Watt
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 885 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 606 Discussion Forums/Café
- 300 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed