LA versus lithium battery sizing
Comments
-
It also depends on the battery design along with best practices!
Many can go to zero from 100% as they save some charge and shut down the battery until charge begins. They close the loop and protect them self at 100% Soc and run loads.
Probably the biggest loss of warranty is high heat and charging below 32. Quality designs take that into account and log temperature extremes, cycles, and save data in non volatile memory.
Many have 10 year power warranties and specify how much capacity is left after the 10 years. A few can be closed loop with your solar, grid, or genset to really save energy when charging. A few actually output their BMS data into inverter based power systems. This then can go out to your phone, system monitor, or the cloud. There is no external Battery Monitor required and installation is simple."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
MichaelK said:I've often heard the claim that Li batteries can be drained down to 0%, but is that really true? I've seen recommendations from BattleBorn that their battery's lives are severely shorten once drained past 80% (I read a 5 fold reduction in life expectancy), and I've also read that Li batteries don't like routine charging all the way to 100%, and 90% is a recommended target.So, in the real world, if people should be managing their Li batteries between 20-90% charge, it seems you are comparing a 70% battery to a traditional 50% lead-acid battery. Is that conclusion off-base? It appears to me that totally draining a Li battery shortens it life as much as 100% draining shortens lead life?
The only reason that it is wise to keep the SoC on LFP between 95% and 10% is really that it is between the "knees" of the very flat voltage curves of FLP. You can make sure all the cells in the battery remain between 0% and 100% if the pack stays between 10% and 95%, because the voltage curve for LFP is so flat. When charging, it is almost completely flat until you get to about 98%-99% SoC, then it rises dramatically. Similarly, it is very flat on discharge until you get to about 10% SoC, then it drops dramatically.
I have read (but can't confirm) that the reason Battleborn says you can go to 0% is really that they size their battery for something over (e.g. 110%) what is spec'd. So if you run it down to 0% SoC it is really still at 10%. If you have a good BMS - and I'm sure Battleborn does - it does no harm to the battery.Off-grid cabin: 6 x Canadian Solar CSK-280M PV panels, Schneider XW-MPPT60-150 Charge Controller, Schneider CSW4024 Inverter/Charger, Schneider SCP, 8S (25.6V), 230Ah Eve LiFePO4 battery in a custom insulated and heated case. -
mike95490 said:
I see no thermal sensors, air gaps and no thermal separators in the pack, everything is all cuddled together, with the cells in the middle, likely 5 degrees warmer than the outer.
edited for clarity: mine would be a 2 cells x 16 rectangle, approximately 1136 x 364 where as Ricks is a 4 cells x 8 rectangle and if our cells are the same size that would give him roughly a 568 x 728 footprint... much more compact and heat dense possibly which is good for me. even in the summer months where it does it a bit hotter (hottest recorded was 30°C I could just simply pull the top off of my battery box and it should be fine. we get down to -14°C regularly but inside my old battery box it rarely got below °5C but when it does it drops as low as -5°C hence me planning on a battery warmer for the morning charge cycle. and extra 5 degrees would mean less energy being used to heat the batteries. plan was to hold them between 8 and 10°C70kw LiFePo4 battery bank, 18 JA solar 200 watt panels, 20 sharp 200 watt panels, morningstar controller(s) and a magnum 4448 inverter with all the usual junk that goes with it. -
Your thermal gain is mostly going to be cell internal resistance, If used gently, and charged slowly, you may not see any thermal gain,
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Oh well i had some hope!
70kw LiFePo4 battery bank, 18 JA solar 200 watt panels, 20 sharp 200 watt panels, morningstar controller(s) and a magnum 4448 inverter with all the usual junk that goes with it. -
LFP can be a PITA in cold climates if you want the costing pay out over a long lifetime. Many of my clients in Alaska and Canada keep them in a controlled environment and even then have triple redundancy for heating.
If they have to leave home in winter, they use fossile fuel heating as a failsafe.
Many just use LA and keep their life simple in cold climates. Less is often more Offgrid."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
@KenMorgan
Yeah, there is not much temperature rise charging at common solar rates. My tests have shown only 1°F higher temp at the center of the bank while charging at 60 amps, which for my bank, is .17C. So I wouldn't count on that being a significant source of heating.
Rick4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
Yep... Lithium Ion batteries are very efficient. Yea! >98% efficient
But that means they will not "self heat" like lead acid batteries which can keep warm in an insulated box during normal cycling.
As flooded cell lead acid batteries approach 90%+ state of charge--gassing--they get down to 80% to 50% efficiency in terms of self heating--Gassing is also a loss, but not to heat.
Plus Lead Acid batteries are just fine when cycling below 0F (-18C) as long as reasonably charged (i.e., electrolyte is not turning to slush/ice).
One quick chart I could find:
https://heartlandowners.org/showthread.php/43227-Battery-electrolyte-freezing-temperature-vs-battery-charge-and-electrolyte-specific-gravitySpecific Gravity of Electrolyte Freezing Point (degrees F) 1.265 -75 F 1.225 -35 F 1.200 -17 F 1.150 +5 F 1.100 +18 F 1.050 +27 F
Since we suggest keeping your lead acid battery >50% State of Charge during normal operation, then you are looking at "good down to" -10F or so.
Nice FLA manual:
http://www.trojanbattery.com/pdf/TrojanBattery_UsersGuide.pdf
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Horsefly said:. So I think the valid comparison to FLA is more like 95%-10% vs the 50% SoC for FLA.
The only reason that it is wise to keep the SoC on LFP between 95% and 10% is really that it is between the "knees" of the very flat voltage curves of FLP. You can make sure all the cells in the battery remain between 0% and 100% if the pack stays between 10% and 95%, because the voltage curve for LFP is so flat. When charging, it is almost completely flat until you get to about 98%-99% SoC, then it rises dramatically. Similarly, it is very flat on discharge until you get to about 10% SoC, then it drops dramatically.
-
Awe you guys are just breaking my itsy bitsy teenie weenie little heart (j/k) so its back to heater pads in a depth in defense layered approach as well as the 4" thick foam insulation with charge and discharge settings designed to keep her off her knees (and that really sucks) ha ha ha. good thing is when its cold here... its cold here. power goes out and food will not spoil so as long as the BMS stops cold/over discharge and prevents cold/overcharging ... worse case is the magnum does not fire up the genset and I have to manually do it.
So I have not asked this particular question yet to avoid being clowned... Us Marines have issues with being made fun of (just keep your booger hooks away from my crayons ya hear?)
just spitballing with no actual experience other than spending the money and currently top balancing the batteries... so no actual experience with the BMS yet.... What would happen, if I took two identical BMS units and wired the common ports in series. IE one BMS fails (for whatever reason does not disconnect the batteries) since they are in series as long as the second unit is functioning it should (theoretically) disconnect as long as its battery sense leads are all hooked up properly... yes...no... overly complicated? sorry not much of an artist in the colloquial use of the word, but I would think that since the BMS (Daly common port in this scenario) so the battery plus and the P - (minus) wires in series. if either unit fails to disconnect the second one in line reading the same readings from the battery should disconnect giving me defense in depth as I can monitor via Bluetooth and if one is power goes down and one BMS is reading wonky I can remove and replace
70kw LiFePo4 battery bank, 18 JA solar 200 watt panels, 20 sharp 200 watt panels, morningstar controller(s) and a magnum 4448 inverter with all the usual junk that goes with it. -
KenMorgan said:Awe you guys are just breaking my itsy bitsy teenie weenie little heart (j/k) so its back to heater pads in a depth in defense layered approach as well as the 4" thick foam insulation with charge and discharge settings designed to keep her off her knees (and that really sucks) ha ha ha. good thing is when its cold here... its cold here. power goes out and food will not spoil so as long as the BMS stops cold/over discharge and prevents cold/overcharging ... worse case is the magnum does not fire up the genset and I have to manually do it.
So I have not asked this particular question yet to avoid being clowned... Us Marines have issues with being made fun of (just keep your booger hooks away from my crayons ya hear?)
just spitballing with no actual experience other than spending the money and currently top balancing the batteries... so no actual experience with the BMS yet.... What would happen, if I took two identical BMS units and wired the common ports in series. IE one BMS fails (for whatever reason does not disconnect the batteries) since they are in series as long as the second unit is functioning it should (theoretically) disconnect as long as its battery sense leads are all hooked up properly... yes...no... overly complicated? sorry not much of an artist in the colloquial use of the word, but I would think that since the BMS (Daly common port in this scenario) so the battery plus and the P - (minus) wires in series. if either unit fails to disconnect the second one in line reading the same readings from the battery should disconnect giving me defense in depth as I can monitor via Bluetooth and if one is power goes down and one BMS is reading wonky I can remove and replace
Use a digital temperature sensor to power a relay, over a normally open contact of the relay run one leg of the remote temperature sensor, when a low temperature is detected by the temperature sensor it cuts power to the relay, this in turn breaks the RTS sensor input which faults the controller in an invalid input, thus terminating charging.
Multiple temperature sensors in series powering the relay would add to redundancy, the controller may need to be rebooted after such a fault, as is typical on other faults, Morningstar support endorses this as a method of charge cut-off, they will tell you if a reboot is required, or you could experiment by removing a RTS wire from the input even with the current LA batteries.
Hint. When wiring relays or temperature sensors as safeguards, always use normally open contacts (open without being powered) to safeguard against outside influences, such as a broken wire from rendering the safety null and void.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed