I need help please. Emergency R&R SI6048

I've got a problem. I've got an SMA Sunny Island SI6048 that has been replaced under warranty... well, the replacement is here, I've got to do the actual removal and replacement. I really need to be able to R&R this unit with everything else in situ, and will be in the dark for the duration of this process.

It is mounted, hanging on a hook attached to a MidNite Solar backplate with a matching MidNite Solar E-panel below and two MidNite Classic 250V charge controllers to the left. Installation was - the plate went to the wall, the hook (SMA's plate) went to the plate, the SI6048 was hefted (it's 143 pounds) up onto the hook by two really big dudes who don't work for me. Then the E-panel was mounted below the Si-6048 and wired in, along with the 2 charge controllers. Attached to the conduit, to a box, and passthru to the outside panel.

I as you can probably well imagine, don't want to do this in the reverse order unless I really, really have to. I need to figure a way to R&R the SI6048 without removing/unhooking (except the inverter/charger) the E-panel. I asked MidNite Solar (in their forum) and was told they put a 2x6 between the inverter/charger and the E-panel, but I guess they forgot they built this with .5MM clearance minimum and along the sides an average of 1.5MM above what might as well be a knife-edge when you are talking 143# above it - a real finger amputation hazard.

That leaves the two handle-etts up top in the vents, and maybe the front lip of the bottom of the inverter/charger but I'd rather have it hefted into place with the cover on, so scratch that... maybe a nylon strap under it and some D-rings? 

Does anybody have an idea? 
I need help, the clock it ticking for the return of the old unit (still in use) to SMA or I'll owe for the new one - less than 2 weeks left. 

Thanks in advance!
Bear
SMA Solar Sunny Island SI6048
JA Solar 330W 'Cypress series' 72 cell panels (18)
MidNite Solar Classic 250 MPPT charge controllers (2)
MidNite Solar MODBUS/Canbus communications adaptor for Sunny Island
MidNite Solar SMA-OG E-panel
MidNite Solar WhizBang Jr current sensor
MidNite Solar MNSPD300V surge protection device (3)
MidNite Solar MNSHUNT 50mv/500A DC shunt
MidNite Solar MNSOB3R-4P PV array shut off box
MidNite Solar Birdhouse 1 RSS initiator
MidNite Solar Battery disconnect module
MidNite Solar Disconnect PSB
Atkinson GSCM mini-i generator start module
Cummins Onan Quiet Diesel QD-8000 8HDKAK diesel inverter generator
Cummins Onan Quiet Diesel QD-3200 3.2HDZAA diesel cycloconverter generator
24-125-11 Monterey Industrial 'Big Sur' 986Ah 48V battery
285-gallon diesel fuel tank
Off the grid on the PNW coast

Comments

  • Trukinbear
    Trukinbear Registered Users Posts: 77 ✭✭
    Hmmm, I wonder if removing that top front plate on the E-panel might provide enough clearance for a couple of hands?
    SMA Solar Sunny Island SI6048
    JA Solar 330W 'Cypress series' 72 cell panels (18)
    MidNite Solar Classic 250 MPPT charge controllers (2)
    MidNite Solar MODBUS/Canbus communications adaptor for Sunny Island
    MidNite Solar SMA-OG E-panel
    MidNite Solar WhizBang Jr current sensor
    MidNite Solar MNSPD300V surge protection device (3)
    MidNite Solar MNSHUNT 50mv/500A DC shunt
    MidNite Solar MNSOB3R-4P PV array shut off box
    MidNite Solar Birdhouse 1 RSS initiator
    MidNite Solar Battery disconnect module
    MidNite Solar Disconnect PSB
    Atkinson GSCM mini-i generator start module
    Cummins Onan Quiet Diesel QD-8000 8HDKAK diesel inverter generator
    Cummins Onan Quiet Diesel QD-3200 3.2HDZAA diesel cycloconverter generator
    24-125-11 Monterey Industrial 'Big Sur' 986Ah 48V battery
    285-gallon diesel fuel tank
    Off the grid on the PNW coast
  • Vic
    Vic Solar Expert Posts: 3,208 ✭✭✭✭
    edited October 2020 #3
     

    Trukn,


    From the pics,  it is not really to get  a  picture  of what is above the Si.

    Could you use a lever hoist,  block and tackle,  connected to something above the Si,   like some ceiling member.    Use a strap under the Si,  to connect to the lifting device,  or,  possibly a ratchet strap to do the lifting,  too   ...    I do   not (or,  perhaps cannot)  see what is the big deal.

    There must be   site-specific things that are an impedance  (?).

    Back  to  the woodwork.  Good Luck,   Vic

    Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  25 KVA Polyphase Kubota diesel,  Honda Eu6500isa,  Eu3000is-es, Eu2000,  Eu1000 gensets.  Thanks Wind-Sun for this great Forum.
  • Trukinbear
    Trukinbear Registered Users Posts: 77 ✭✭
    Nothing above to lift from. My issue is the lack of clearance with the bottom panel. It went up with 2 big dudes who could get under it, this way (up and down) will have to be via the 2 handles at the top which are 6' above the floor. A hand underneath would lose fingers, I was thinking maybe 3 feet of 3-inch strap and some 'D' rings might give them something lower to lift with. IDK I don't see how unless I find a couple of NBA draftees this is going to work, has to go straight up to above the E-panel, out in front of the E-panel, then go to the wall 6+' up, and straight down. Either way I've got to pay these guys for travel time (we're remote) and a couple of hour minimum. If they drop it, as they say - I'm el screwd-o. 
    SMA Solar Sunny Island SI6048
    JA Solar 330W 'Cypress series' 72 cell panels (18)
    MidNite Solar Classic 250 MPPT charge controllers (2)
    MidNite Solar MODBUS/Canbus communications adaptor for Sunny Island
    MidNite Solar SMA-OG E-panel
    MidNite Solar WhizBang Jr current sensor
    MidNite Solar MNSPD300V surge protection device (3)
    MidNite Solar MNSHUNT 50mv/500A DC shunt
    MidNite Solar MNSOB3R-4P PV array shut off box
    MidNite Solar Birdhouse 1 RSS initiator
    MidNite Solar Battery disconnect module
    MidNite Solar Disconnect PSB
    Atkinson GSCM mini-i generator start module
    Cummins Onan Quiet Diesel QD-8000 8HDKAK diesel inverter generator
    Cummins Onan Quiet Diesel QD-3200 3.2HDZAA diesel cycloconverter generator
    24-125-11 Monterey Industrial 'Big Sur' 986Ah 48V battery
    285-gallon diesel fuel tank
    Off the grid on the PNW coast
  • Trukinbear
    Trukinbear Registered Users Posts: 77 ✭✭
    Lifting by the upper handles from the floor to over 6 feet up would seem to involve some sort of maneuver in the middle.
    SMA Solar Sunny Island SI6048
    JA Solar 330W 'Cypress series' 72 cell panels (18)
    MidNite Solar Classic 250 MPPT charge controllers (2)
    MidNite Solar MODBUS/Canbus communications adaptor for Sunny Island
    MidNite Solar SMA-OG E-panel
    MidNite Solar WhizBang Jr current sensor
    MidNite Solar MNSPD300V surge protection device (3)
    MidNite Solar MNSHUNT 50mv/500A DC shunt
    MidNite Solar MNSOB3R-4P PV array shut off box
    MidNite Solar Birdhouse 1 RSS initiator
    MidNite Solar Battery disconnect module
    MidNite Solar Disconnect PSB
    Atkinson GSCM mini-i generator start module
    Cummins Onan Quiet Diesel QD-8000 8HDKAK diesel inverter generator
    Cummins Onan Quiet Diesel QD-3200 3.2HDZAA diesel cycloconverter generator
    24-125-11 Monterey Industrial 'Big Sur' 986Ah 48V battery
    285-gallon diesel fuel tank
    Off the grid on the PNW coast
  • Trukinbear
    Trukinbear Registered Users Posts: 77 ✭✭
    Along the sides, you can see that gap is no larger than the machine screw head in the photo, and at one point you can just barely see light thru the gap. Next to that, you could almost get something under it, but if you notice the bottom of the Sunny Island is curved downwards almost touching the upper cross-member of the E-panel. The one coming down I don't mind them doing it with the cover off which might give them some small handhold in the front, but the big yellow cast aluminum cover that I really want to be in place before anybody so much as touches the new one curves to follow that curve at the bottom into the E-panel. The E-panel would not safely support the weight of this unit should it miss the hook, and they have no room just to come up from the bottom until they just passed the hook - this way they've got to pass the hook some 12-18" away from it then go horizontally over to the wall, and down to the hook. I'm just having trouble visualizing how two people will do this. 
    SMA Solar Sunny Island SI6048
    JA Solar 330W 'Cypress series' 72 cell panels (18)
    MidNite Solar Classic 250 MPPT charge controllers (2)
    MidNite Solar MODBUS/Canbus communications adaptor for Sunny Island
    MidNite Solar SMA-OG E-panel
    MidNite Solar WhizBang Jr current sensor
    MidNite Solar MNSPD300V surge protection device (3)
    MidNite Solar MNSHUNT 50mv/500A DC shunt
    MidNite Solar MNSOB3R-4P PV array shut off box
    MidNite Solar Birdhouse 1 RSS initiator
    MidNite Solar Battery disconnect module
    MidNite Solar Disconnect PSB
    Atkinson GSCM mini-i generator start module
    Cummins Onan Quiet Diesel QD-8000 8HDKAK diesel inverter generator
    Cummins Onan Quiet Diesel QD-3200 3.2HDZAA diesel cycloconverter generator
    24-125-11 Monterey Industrial 'Big Sur' 986Ah 48V battery
    285-gallon diesel fuel tank
    Off the grid on the PNW coast
  • Trukinbear
    Trukinbear Registered Users Posts: 77 ✭✭
    Going up without the E-panel it was a simple clean and jerk, with the unit against the wall/plate, and the two guys squatted, stood up then got under it and hefted it above the hook. The clearance is too tight to put it on the hook while at an angle allowing 4 hands underneath then letting it swing to the wall, this will have to go to the wall and down.
    SMA Solar Sunny Island SI6048
    JA Solar 330W 'Cypress series' 72 cell panels (18)
    MidNite Solar Classic 250 MPPT charge controllers (2)
    MidNite Solar MODBUS/Canbus communications adaptor for Sunny Island
    MidNite Solar SMA-OG E-panel
    MidNite Solar WhizBang Jr current sensor
    MidNite Solar MNSPD300V surge protection device (3)
    MidNite Solar MNSHUNT 50mv/500A DC shunt
    MidNite Solar MNSOB3R-4P PV array shut off box
    MidNite Solar Birdhouse 1 RSS initiator
    MidNite Solar Battery disconnect module
    MidNite Solar Disconnect PSB
    Atkinson GSCM mini-i generator start module
    Cummins Onan Quiet Diesel QD-8000 8HDKAK diesel inverter generator
    Cummins Onan Quiet Diesel QD-3200 3.2HDZAA diesel cycloconverter generator
    24-125-11 Monterey Industrial 'Big Sur' 986Ah 48V battery
    285-gallon diesel fuel tank
    Off the grid on the PNW coast
  • Trukinbear
    Trukinbear Registered Users Posts: 77 ✭✭
    It all fits closely together. The countertop to the right removes with three latches and serves as the cosmetic portion of the cover for the battery some 30ish inches out of frame to the right. 

    SMA Solar Sunny Island SI6048
    JA Solar 330W 'Cypress series' 72 cell panels (18)
    MidNite Solar Classic 250 MPPT charge controllers (2)
    MidNite Solar MODBUS/Canbus communications adaptor for Sunny Island
    MidNite Solar SMA-OG E-panel
    MidNite Solar WhizBang Jr current sensor
    MidNite Solar MNSPD300V surge protection device (3)
    MidNite Solar MNSHUNT 50mv/500A DC shunt
    MidNite Solar MNSOB3R-4P PV array shut off box
    MidNite Solar Birdhouse 1 RSS initiator
    MidNite Solar Battery disconnect module
    MidNite Solar Disconnect PSB
    Atkinson GSCM mini-i generator start module
    Cummins Onan Quiet Diesel QD-8000 8HDKAK diesel inverter generator
    Cummins Onan Quiet Diesel QD-3200 3.2HDZAA diesel cycloconverter generator
    24-125-11 Monterey Industrial 'Big Sur' 986Ah 48V battery
    285-gallon diesel fuel tank
    Off the grid on the PNW coast
  • littleharbor2
    littleharbor2 Solar Expert Posts: 2,102 ✭✭✭✭✭
    I know that the grid tie models this size allow you to slip a pipe through the vent holes and it becomes a double handle. still need a couple people unless you are really strong.

    2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old  but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric,  460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.

  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    You could use wooden wedge shims, the kind found at hardware stores used when installing door frames, keep adding and tapping into the gap until the hook is cleared, that will take care of the dead weight narrow access problem.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • Trukinbear
    Trukinbear Registered Users Posts: 77 ✭✭
    mcgivor said:
    You could use wooden wedge shims, the kind found at hardware stores used when installing door frames, keep adding and tapping into the gap until the hook is cleared, that will take care of the dead weight narrow access problem.
    Thanks, I'm afraid my real issue will be in the other direction - installation of the new one.
    SMA Solar Sunny Island SI6048
    JA Solar 330W 'Cypress series' 72 cell panels (18)
    MidNite Solar Classic 250 MPPT charge controllers (2)
    MidNite Solar MODBUS/Canbus communications adaptor for Sunny Island
    MidNite Solar SMA-OG E-panel
    MidNite Solar WhizBang Jr current sensor
    MidNite Solar MNSPD300V surge protection device (3)
    MidNite Solar MNSHUNT 50mv/500A DC shunt
    MidNite Solar MNSOB3R-4P PV array shut off box
    MidNite Solar Birdhouse 1 RSS initiator
    MidNite Solar Battery disconnect module
    MidNite Solar Disconnect PSB
    Atkinson GSCM mini-i generator start module
    Cummins Onan Quiet Diesel QD-8000 8HDKAK diesel inverter generator
    Cummins Onan Quiet Diesel QD-3200 3.2HDZAA diesel cycloconverter generator
    24-125-11 Monterey Industrial 'Big Sur' 986Ah 48V battery
    285-gallon diesel fuel tank
    Off the grid on the PNW coast
  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    Then reverse the process put sufficient  shims on top of the e panel to clear the hook then remove them slowly to lower whilst someone maintains pressure against the back plate. This is something I've done when installing motor control centers to align bolt holes.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • Trukinbear
    Trukinbear Registered Users Posts: 77 ✭✭
    mcgivor said:
    Then reverse the process put sufficient  shims on top of the e panel to clear the hook then remove them slowly to lower whilst someone maintains pressure against the back plate. This is something I've done when installing motor control centers to align bolt holes.
    The E-panel is affixed to the backplate with 4-#8 sheet metal screws and itself weighs over 50#, I wouldn't trust it with another 143# on it, and if it fails it has all kinds of potential for calamity, not to mention was over $1000 and has another $1500 in electronics inside of it. 
    SMA Solar Sunny Island SI6048
    JA Solar 330W 'Cypress series' 72 cell panels (18)
    MidNite Solar Classic 250 MPPT charge controllers (2)
    MidNite Solar MODBUS/Canbus communications adaptor for Sunny Island
    MidNite Solar SMA-OG E-panel
    MidNite Solar WhizBang Jr current sensor
    MidNite Solar MNSPD300V surge protection device (3)
    MidNite Solar MNSHUNT 50mv/500A DC shunt
    MidNite Solar MNSOB3R-4P PV array shut off box
    MidNite Solar Birdhouse 1 RSS initiator
    MidNite Solar Battery disconnect module
    MidNite Solar Disconnect PSB
    Atkinson GSCM mini-i generator start module
    Cummins Onan Quiet Diesel QD-8000 8HDKAK diesel inverter generator
    Cummins Onan Quiet Diesel QD-3200 3.2HDZAA diesel cycloconverter generator
    24-125-11 Monterey Industrial 'Big Sur' 986Ah 48V battery
    285-gallon diesel fuel tank
    Off the grid on the PNW coast
  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    The shear strenth of 4 #8 screws is ~400 lbs. enough of a safety margin I would think.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • Trukinbear
    Trukinbear Registered Users Posts: 77 ✭✭
    And the strength of the self tapped screw holes in the mild steel backplate? I appreciate your suggestions, but at that point I'd have right around half my annual income, and my fingers on the line. I think the E-panel would fold like origami - 143 pounds on those two little thin blades of sheet metal, IDK. 

    SMA Solar Sunny Island SI6048
    JA Solar 330W 'Cypress series' 72 cell panels (18)
    MidNite Solar Classic 250 MPPT charge controllers (2)
    MidNite Solar MODBUS/Canbus communications adaptor for Sunny Island
    MidNite Solar SMA-OG E-panel
    MidNite Solar WhizBang Jr current sensor
    MidNite Solar MNSPD300V surge protection device (3)
    MidNite Solar MNSHUNT 50mv/500A DC shunt
    MidNite Solar MNSOB3R-4P PV array shut off box
    MidNite Solar Birdhouse 1 RSS initiator
    MidNite Solar Battery disconnect module
    MidNite Solar Disconnect PSB
    Atkinson GSCM mini-i generator start module
    Cummins Onan Quiet Diesel QD-8000 8HDKAK diesel inverter generator
    Cummins Onan Quiet Diesel QD-3200 3.2HDZAA diesel cycloconverter generator
    24-125-11 Monterey Industrial 'Big Sur' 986Ah 48V battery
    285-gallon diesel fuel tank
    Off the grid on the PNW coast
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Any way to thread rope thru the vent holes on the top, and hang it from ceiling ?

    or, install 2 of the front cover strews, with big washers, and a cable and hang  it from 2 screws ?   The look possibly too small, and I might go with trying to thread rope thru the chassis - maybe use a giant 2' long zip tie as a probe to fish the rope thru with ?  Any internal parts that might get ripped off a PCB when the rope tightens up ?
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    And the strength of the self tapped screw holes in the mild steel backplate? I appreciate your suggestions, but at that point I'd have right around half my annual income, and my fingers on the line. I think the E-panel would fold like origami - 143 pounds on those two little thin blades of sheet metal, IDK. 

    Definitely not a one man job, perhaps it would be better to remove the E panel to gain better access as shortcuts often slow you down and you don't want to injure your fingers or back for that matter. 

    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • wellbuilt
    wellbuilt Solar Expert Posts: 763 ✭✭✭✭
    I used a bucket and 2 small step ladders to hang my out back flex power one by my self . 
      Lifted the whole unit on to the bucket , then up to a 3’ step ladder then on a 4 ‘ ladder and pushed it to the wall
     I used 4 small lag bolts  in to 3/4 ply wood to hold it . 
     My out back weights 100 lbs + 
      
    Out back  flex power one  with out back 3648 inverter fm80 charge controler  flex net  mate 16 gc215 battery’s 4425 Watts solar .
  • Trukinbear
    Trukinbear Registered Users Posts: 77 ✭✭
    I've removed as many obstacles as possible, fashioned a lifting bar to thread thru the top, and have 3 guys showing up at 3 tomorrow. Wish me luck - I'll take pictures. 
    SMA Solar Sunny Island SI6048
    JA Solar 330W 'Cypress series' 72 cell panels (18)
    MidNite Solar Classic 250 MPPT charge controllers (2)
    MidNite Solar MODBUS/Canbus communications adaptor for Sunny Island
    MidNite Solar SMA-OG E-panel
    MidNite Solar WhizBang Jr current sensor
    MidNite Solar MNSPD300V surge protection device (3)
    MidNite Solar MNSHUNT 50mv/500A DC shunt
    MidNite Solar MNSOB3R-4P PV array shut off box
    MidNite Solar Birdhouse 1 RSS initiator
    MidNite Solar Battery disconnect module
    MidNite Solar Disconnect PSB
    Atkinson GSCM mini-i generator start module
    Cummins Onan Quiet Diesel QD-8000 8HDKAK diesel inverter generator
    Cummins Onan Quiet Diesel QD-3200 3.2HDZAA diesel cycloconverter generator
    24-125-11 Monterey Industrial 'Big Sur' 986Ah 48V battery
    285-gallon diesel fuel tank
    Off the grid on the PNW coast
  • littleharbor2
    littleharbor2 Solar Expert Posts: 2,102 ✭✭✭✭✭
    I've removed as many obstacles as possible, fashioned a lifting bar to thread thru the top, and have 3 guys showing up at 3 tomorrow. Wish me luck - I'll take pictures. 
    So does a 3/4" or similar pipe fit through the vent area as I suggested? The inner louvres look a bit different than a grid tie version.

    2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old  but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric,  460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.

  • BB.
    BB. Super Moderators, Administrators Posts: 33,613 admin
    edited October 2020 #21
    Best of luck and take care.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Trukinbear
    Trukinbear Registered Users Posts: 77 ✭✭
    Ready to shut down as soon as I'm sure my guys aren't no-shows!

    SMA Solar Sunny Island SI6048
    JA Solar 330W 'Cypress series' 72 cell panels (18)
    MidNite Solar Classic 250 MPPT charge controllers (2)
    MidNite Solar MODBUS/Canbus communications adaptor for Sunny Island
    MidNite Solar SMA-OG E-panel
    MidNite Solar WhizBang Jr current sensor
    MidNite Solar MNSPD300V surge protection device (3)
    MidNite Solar MNSHUNT 50mv/500A DC shunt
    MidNite Solar MNSOB3R-4P PV array shut off box
    MidNite Solar Birdhouse 1 RSS initiator
    MidNite Solar Battery disconnect module
    MidNite Solar Disconnect PSB
    Atkinson GSCM mini-i generator start module
    Cummins Onan Quiet Diesel QD-8000 8HDKAK diesel inverter generator
    Cummins Onan Quiet Diesel QD-3200 3.2HDZAA diesel cycloconverter generator
    24-125-11 Monterey Industrial 'Big Sur' 986Ah 48V battery
    285-gallon diesel fuel tank
    Off the grid on the PNW coast
  • Trukinbear
    Trukinbear Registered Users Posts: 77 ✭✭
    Whew, finally over and just in time as darkness falls. For the system shutdown, we used this opportunity to fully test the Rapid Shutdown System - it disconnected the solar panels, turned off the generator, turned off the Inverter/Charger, and disconnected everything from the 986Ah 48V battery well within the 30 seconds required. After I turned off the voice announcements it made noises that sounded like a zombie gasping for air every few minutes until everything leveled out - kinda disconcerting until you figure out where it's coming from.
    SMA Solar Sunny Island SI6048
    JA Solar 330W 'Cypress series' 72 cell panels (18)
    MidNite Solar Classic 250 MPPT charge controllers (2)
    MidNite Solar MODBUS/Canbus communications adaptor for Sunny Island
    MidNite Solar SMA-OG E-panel
    MidNite Solar WhizBang Jr current sensor
    MidNite Solar MNSPD300V surge protection device (3)
    MidNite Solar MNSHUNT 50mv/500A DC shunt
    MidNite Solar MNSOB3R-4P PV array shut off box
    MidNite Solar Birdhouse 1 RSS initiator
    MidNite Solar Battery disconnect module
    MidNite Solar Disconnect PSB
    Atkinson GSCM mini-i generator start module
    Cummins Onan Quiet Diesel QD-8000 8HDKAK diesel inverter generator
    Cummins Onan Quiet Diesel QD-3200 3.2HDZAA diesel cycloconverter generator
    24-125-11 Monterey Industrial 'Big Sur' 986Ah 48V battery
    285-gallon diesel fuel tank
    Off the grid on the PNW coast