Tripplite UPS and Conext XW+ don’t play nice

Hi All,

Was wondering if anyone here has experienced this issue. I have Tripplite UPS’s on two different computers on load circuits for XW6848.  Essentially double backup. Twice on my computer it just shut off the Tripplite completely failing in its uninterruptability. And last night, there was a power flicker and the Tripplite connected to my wife’s computer had shut off. Also at this time the XW+ goes into bulk charge mode even though battery nearly full. This has happened a couple other times too. We have since removed the Tripplites. Any ideas on this? Thanks.

Comments

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Is this On Grid, or Off ?

    The XW should switch to battery as fast as UPS's do.  Are the batteries good in the UPS's  - I've seen UPS batteries go bad in 2 years, I've got a replacement one sitting on the table at the radio station now.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    There is no logical reason the UPS would be affected by the inverter, try unplugging the UPS to verify the batteries are good. The bulk charging may be occurring because the battery voltage is below the rebulk setting value.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,894 ✭✭✭✭✭✭
    Not many reasons an XW would go into bulk, again, unless your battery voltage is really low.

    There is alot missing in your post and any help you get, or how long it takes for advice, depends on the effort you put into the post.
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • ZimInSeattle
    ZimInSeattle Registered Users Posts: 10 ✭✭
    edited September 2020 #5
    Noted XW+ reported grid under voltage at the time of the power flicker. Grid under voltage has triggered bulk charge several times over the last couple months even though battery nearly full. Don’t know why this would affect UPS’s. Batteries in UPS’s appear good as unplugging from wall just sounds alarm, but whatever being powered by UPS keeps running. System is AC coupled & grid tied. 39 x SW290 panels, 32 x Enphase M250, 7 x IQ7’s microinverters.