Need Recommendation for "Quiet" Inverter

Options
jmb
jmb Registered Users Posts: 42 ✭✭
It is time for me to look into getting a bit larger inverter for our off-grid cabin.

Current configuration:

2.9 KW Panels
2 IOTA 12V 45A chargers in series
MidNite Solar Classic 200SL
800 AH LiFePO4 battery bank
Samlex PST-1500-24 PSW inverter

Everything works well but I need a bit more juice for the air conditioner so I am thinking somewhere in the 2.5 - 3 KW size. My issue with the current inverter, besides being a bit under powered, is the amount of RFI generated on the HF bands.  I run a HF HAM radio rig at the cabin and the noise generated by the Samlex inverter is about +20 on the meter so i have to turn it off whenever i want to operate.  The radio is running off 12V so it's not ingesting any "dirty" power.

I am hoping for a recommendation, based on experience, of an inverter that will meet my needs.

73,

Justin B.
KI5GKD
Justin B.
Cabin - 9 Mission Solar 310 watt panels, MidNite Solar Combiner, Iron Ridge mounting, 4 Speciaized Power 200 AH 24V LiFePO4 batteries, Samlex PST-1500-24 inverter, MidNite Solar Classic 200SL CC

Barn - 9 Renogy 100W panels, Generic Chinese 40A MPPT CC, 6 Universal 12V 100 AH AGM batteries, Reliable 3KW 12V PSW inverter

«1

Comments

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Options
    Is your inverter a "heavy" inverter with a big power transformer ?   Those generally run at lower frequencies than transformer-less inverters - which are known for "rich harmonics".
    I have nothing but praise for the Schneider XW series, and I know it does not interfere with AM band DX'ing, in my case.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • jmb
    jmb Registered Users Posts: 42 ✭✭
    Options
    Really not sure about the Samlex but it is most likely a high frequency switcher of some sort.  I will look t the Schneider.  I operate mostly on 40 Meters and a bit on 20.  
    Justin B.
    Cabin - 9 Mission Solar 310 watt panels, MidNite Solar Combiner, Iron Ridge mounting, 4 Speciaized Power 200 AH 24V LiFePO4 batteries, Samlex PST-1500-24 inverter, MidNite Solar Classic 200SL CC

    Barn - 9 Renogy 100W panels, Generic Chinese 40A MPPT CC, 6 Universal 12V 100 AH AGM batteries, Reliable 3KW 12V PSW inverter

  • jmb
    jmb Registered Users Posts: 42 ✭✭
    Options
    Just looked at them and really need something a bit smaller. and don't need 240V.
    Justin B.
    Cabin - 9 Mission Solar 310 watt panels, MidNite Solar Combiner, Iron Ridge mounting, 4 Speciaized Power 200 AH 24V LiFePO4 batteries, Samlex PST-1500-24 inverter, MidNite Solar Classic 200SL CC

    Barn - 9 Renogy 100W panels, Generic Chinese 40A MPPT CC, 6 Universal 12V 100 AH AGM batteries, Reliable 3KW 12V PSW inverter

  • Vic
    Vic Solar Expert Posts: 3,208 ✭✭✭✭
    Options
    Hi Justin,

    Name-brand inverter/chargers are generally RFI quieter than are MPPT CCs,   because,  if nothing else,   they tend to try to meet  FCC Part 15 Line-Conducted emissions regs.   MPPT CCs,  generally do not need to comply with Line conducted emissions regs,  because they do not "connect" to the Line (which means the AC power Line/s).   And are usually not tested,  and are considered to not need to limit emissions below 30.0 MHz.

    An LC AC line filter might be worth a try  --  these are usually Differential Mode filters.

    If you have any of the Mix 31 ferrites left,  you might try running the AC cables right at the output of the inverter,  to see if this helps any.

    As you know,   generally,  trying to isolate your antennas from the power equipment,  PV array,  and power cables can be a large help.

    If your antenna is coax-fed,   try a common mode choke on the coax,  near the radio's antenna jack.

    The venerable Xantrex SW+ 5548s (low frequency) inverter/chargers in use here are very quiet.   We run common mode chokes on their AC outputs,  even though the differential filters would be more effective,   there seems to be absolutely NO RFI on the HF bands from then,   so that is moot.

    Sounds like you have tamed the RFI from the Classic   ...    73,  Good Luck,    Vic
    Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  25 KVA Polyphase Kubota diesel,  Honda Eu6500isa,  Eu3000is-es, Eu2000,  Eu1000 gensets.  Thanks Wind-Sun for this great Forum.
  • Photowhit
    Photowhit Solar Expert Posts: 6,003 ✭✭✭✭✭
    Options
    It might be worth asking over at the Midnite forum as well, several 'hams' there as well. 
    Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites,  Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
    - Assorted other systems, pieces and to many panels in the closet to not do more projects.
  • jmb
    jmb Registered Users Posts: 42 ✭✭
    Options
    Thanks, Vic, this is about to drive me nuts.  You remember from the MidNite forum (Vic there too?) what I've tried...  Right now I wound my coax through a mix 31 toroid 12 turns right before the radio with no change.  The Classic puts out a helluva squeal efery 25 KHz or so but I can work around that.  The inverter blankets the entire band with "hash" and I have to turn it off to operate.  Does not make wife happy as that kills AC, her freezer, lights in her "she shack," among other perils to my health...

    So, since I need to upgrade inverter anyway should I look at low freq inverters?  From what I can tell the RFI from the inverter is radiated as I am running the radio off DC.  I will lengthen the romex between the inverter and breaker panel and wind it through a mix 31 toroid a few turns and see what happens.
    Justin B.
    Cabin - 9 Mission Solar 310 watt panels, MidNite Solar Combiner, Iron Ridge mounting, 4 Speciaized Power 200 AH 24V LiFePO4 batteries, Samlex PST-1500-24 inverter, MidNite Solar Classic 200SL CC

    Barn - 9 Renogy 100W panels, Generic Chinese 40A MPPT CC, 6 Universal 12V 100 AH AGM batteries, Reliable 3KW 12V PSW inverter

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Options
    And try putting a low impedance RF cap at ALL the inverter leads - even rounding the edges of the hash, will reduce the harmonics
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • softdown
    softdown Solar Expert Posts: 3,824 ✭✭✭✭
    Options
    You might find the needed data here: https://www.solar-electric.com/lib/wind-sun/FXR_A_specsheet.pdf

    Looks like they have 10% off this week. Makes sense that a higher end inverter would be "quieter". 

    What state are you in? I may have an interest in a back up inverter since my Cotek 1500 inverter is powering three freezers. I think Cotek preceded the Samlex name.  Could have swore I bought a case of those inverters but there are none to be found. 
    First Bank:16 180 watt Grape Solar with  FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
  • Vic
    Vic Solar Expert Posts: 3,208 ✭✭✭✭
    Options
    Hi Justin,

    Yep  we have conversed on the MN Forum.   And some additional remedies were mentioned there.

    LF inverters are essentially dinosaurs.    Every part of them is much more expensive to build,   than are Hi Frequency inverters.   There is a lot of steel,   and more copper in them than HF units.  This makes them fairly large,   and heavy.   Much  more freight  and material cost incoming to the manufacturing facility,   and larger heavy boxes going into Distribution and to the ultimate customer.   All of this adds a lot to the cost.

    The LF inverters here are large,   and heavy (about 130 Lps for each,   and two are required for 240 VAC).   They are solid performers,   but   you should be able to tame your existing HF inverter,  with chokes on the input,  and perhaps a choke on the output (for now,  as an experiment)   An old-fashioned  Pi-type LC filter in a metal can,  would probably be the best,  for filtering the 120 VAC output of the inverter.

    One other thing that was mentioned elsewhere,   is that running DC and AC cables in metal conduit (usually EMT is fine).   This can be a large help,  but can be a bit difficult to retrofit.

    More later.   WIsh I had more experience with modern-day HF  inverters,  vs RFI.   This is a good Forum for your question,   as it is well-attended by folks with broad experience (IMO).   73   GL.      VIc
    Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  25 KVA Polyphase Kubota diesel,  Honda Eu6500isa,  Eu3000is-es, Eu2000,  Eu1000 gensets.  Thanks Wind-Sun for this great Forum.
  • petertearai
    petertearai Solar Expert Posts: 471 ✭✭✭✭
    Options
    Outback inverters ,,,, have a transformer in them , are they high frequency ? 
    2225 wattts pv . Outback 2kw  fxr pure sine inverter . fm80 charge controller . Mate 3. victron battery monitor . 24 volts  in 2 volt Shoto lead carbon extreme batterys. off grid  holiday home 
  • Vic
    Vic Solar Expert Posts: 3,208 ✭✭✭✭
    Options
    Outback inverters ,,,, have a transformer in them , are they high frequency ? 
    Hi peter..,

    Searched with the term: "   difference between HF and LF power inverters  "

    This is the first hit.

    https://www.magnum-dimensions.com/knowledge/high-vs-low-frequency-inverters/inversion-methods-explained-high-frequency-vs-low

    There are many fine-points in just how each manufacturer chooses to implement the design of each of these general types of inverters.   Am no expert at that.   FWIW,    Vic
    Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  25 KVA Polyphase Kubota diesel,  Honda Eu6500isa,  Eu3000is-es, Eu2000,  Eu1000 gensets.  Thanks Wind-Sun for this great Forum.
  • jjdh
    jjdh Registered Users Posts: 9 ✭✭
    Options
    > Just looked at them and really need something a bit smaller. and don't need 240V.

    You probably saw, but Schneider has a smaller line below the XWs as well. Eg. Conext SW 2524. Still almost twice as large as your Samlex: 2500W output; but in case that's helpful.
  • softdown
    softdown Solar Expert Posts: 3,824 ✭✭✭✭
    Options
    Ham radio board perhaps? I know spark plugs used to be available with and without suppression - for radio purposes. Based on that, getting suppression of electrical noise was simple. 
    First Bank:16 180 watt Grape Solar with  FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
  • jmb
    jmb Registered Users Posts: 42 ✭✭
    Options
    I think my next step will be to run the cable between inverter and breaker panel in metallic flex conduit.
    Justin B.
    Cabin - 9 Mission Solar 310 watt panels, MidNite Solar Combiner, Iron Ridge mounting, 4 Speciaized Power 200 AH 24V LiFePO4 batteries, Samlex PST-1500-24 inverter, MidNite Solar Classic 200SL CC

    Barn - 9 Renogy 100W panels, Generic Chinese 40A MPPT CC, 6 Universal 12V 100 AH AGM batteries, Reliable 3KW 12V PSW inverter

  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,752 ✭✭✭✭✭✭
    Options
    Forgive me if it has been posted. Have you looked at the physical distance between your inverter and you ham station?
    Even the Schneider inverters with FCC spec listings need to be a minimum of 5 feet from your transceivers. Use of a pocket AM radio is useful for this.
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • softdown
    softdown Solar Expert Posts: 3,824 ✭✭✭✭
    Options
    Forgive me if it has been posted. Have you looked at the physical distance between your inverter and you ham station?
    Even the Schneider inverters with FCC spec listings need to be a minimum of 5 feet from your transceivers. Use of a pocket AM radio is useful for this.
    With Schneifer's gigantic global presence I would imagine they spend  the most on R&D - thus staying staying a step ahead? Perhaps charging for two steps? 

    Outback is still a fine name I think. Their core line has not changed much from appearances. They seem to have focused on introducing much larger and more sophisticated equipment. Which their "best/most experienced techs" likely assemble. 

    Have any thoughts on changing the inverter output to 125 volts? I feel like maybe it consumes a scosh more power now. Considering trying 118V to see if their is a measurable difference in power consumed. 

    The FlexPower really does seem like it consumes ample power to me. I have been pulling out all  the stops in energy conservation and can not see more than 50.4 volts at 6am. Even with the 24V forklift battery system powering the freezers. Even de-commissioned the Samsung Energy Star at 565 kWh.

    The savings are hardly worth it for most people - my quest is for my own reasons. 
    First Bank:16 180 watt Grape Solar with  FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
  • jmb
    jmb Registered Users Posts: 42 ✭✭
    Options
    Dave - Radio is currently about 10' from inverter.  As I mentioned, next time I head to town I will get some metallic conduit and I will eventually move the inverter into the enclosure I built to house the batteries, bus bars, and other stuffs.  I have thought about lining this enclosure with heavy-duty aluminum foil as well...

    I had a back and forth with Samlex Support a couple of years ago and they were not much help and pointed out the FCC Type Acceptance testing does not cover lower frequencies.
    Justin B.
    Cabin - 9 Mission Solar 310 watt panels, MidNite Solar Combiner, Iron Ridge mounting, 4 Speciaized Power 200 AH 24V LiFePO4 batteries, Samlex PST-1500-24 inverter, MidNite Solar Classic 200SL CC

    Barn - 9 Renogy 100W panels, Generic Chinese 40A MPPT CC, 6 Universal 12V 100 AH AGM batteries, Reliable 3KW 12V PSW inverter

  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    I would suggest that you use metallic conduit, and not the flex/spiral type (I don't think that it makes that good of connection between "coils").

    In general, for 30 MHz and above signals (typically to ~ 180 MHz, as I recall--But it is has been decades since I have done RF control on computers), about 10 feet of shield for cabling usually does a good enough job to capacitively shunt the higher frequency signals to ground (metal conduit/shield)... Beyond 10 feet did not really matter.

    AC is nice because you can use common mode chokes (as well as differential mode chokes/filtering). The common mode chokes will not saturate.

    With DC power lines, you cannot use common mode chokes (one wire through a ferrite bead, for example). The DC current will saturate the ferrite core and kill its usefulness as a common mode choke.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Vic
    Vic Solar Expert Posts: 3,208 ✭✭✭✭
    Options
    BB. said:
    I would suggest that you use metallic conduit, and not the flex/spiral type (I don't think that it makes that good of connection between "coils").

    In general, for 30 MHz and above signals (typically to ~ 180 MHz, as I recall--But it is has been decades since I have done RF control on computers), about 10 feet of shield for cabling usually does a good enough job to capacitively shunt the higher frequency signals to ground (metal conduit/shield)... Beyond 10 feet did not really matter.

    AC is nice because you can use common mode chokes (as well as differential mode chokes/filtering). The common mode chokes will not saturate.

    With DC power lines, you cannot use common mode chokes (one wire through a ferrite bead, for example). The DC current will saturate the ferrite core and kill its usefulness as a common mode choke.

    -Bill


    Hi Bill,

    Completely  agree about EMT (or  IMC/Rigid, for that  matter)  is far   superior to  FMC  (Metal  Flex), as,   the contact between  all of  those  spiral windings is uncertain.  Al Flex is probably the  worse,    in that  regard.

    But,    for DC Common Mode  chokes,  seems.  of  the positive AND  negative cables (to an inverter,  CC,  etc)  are wound through a  toroidal core (Bifilar),  that  the currents  flowing  in opposite directions  cancel,   so the  only current  remaining current is   the  noise current,   with  little chance  of core saturation.  Is that not   the case?

    Thanks,     Vic

    Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  25 KVA Polyphase Kubota diesel,  Honda Eu6500isa,  Eu3000is-es, Eu2000,  Eu1000 gensets.  Thanks Wind-Sun for this great Forum.
  • jmb
    jmb Registered Users Posts: 42 ✭✭
    Options
    OK, will use galvanized solid conduit...  This is making me almost want to take down my new multi-band inverted Vee antenna and put the little dinky MFJ 2240 back up!  I still had some RFI but not as much...
    Justin B.
    Cabin - 9 Mission Solar 310 watt panels, MidNite Solar Combiner, Iron Ridge mounting, 4 Speciaized Power 200 AH 24V LiFePO4 batteries, Samlex PST-1500-24 inverter, MidNite Solar Classic 200SL CC

    Barn - 9 Renogy 100W panels, Generic Chinese 40A MPPT CC, 6 Universal 12V 100 AH AGM batteries, Reliable 3KW 12V PSW inverter

  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    If you can wind/pass both + and - DC power cables through a single core--Yes that is correct, it will not saturate.

    If you have a "typical" car type DC AM radio or such... There is a + power lead and the chassis of the radio is the negative power connection. Not really easy to pass + and - power through a single choke/core.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • jmb
    jmb Registered Users Posts: 42 ✭✭
    Options
    Just about have all of my conduit stuffs rounded up and hope to do this in the next day or so.  I am also looking at bigger inverters and the Outback VFX3524A-01 looks nice.  Although we are strictly off-grid and wouldn't need a hybrid inverter the specs and price on this look good.  Does anybody have experience with this and would RFI be manageable?


    Justin B.
    Cabin - 9 Mission Solar 310 watt panels, MidNite Solar Combiner, Iron Ridge mounting, 4 Speciaized Power 200 AH 24V LiFePO4 batteries, Samlex PST-1500-24 inverter, MidNite Solar Classic 200SL CC

    Barn - 9 Renogy 100W panels, Generic Chinese 40A MPPT CC, 6 Universal 12V 100 AH AGM batteries, Reliable 3KW 12V PSW inverter

  • softdown
    softdown Solar Expert Posts: 3,824 ✭✭✭✭
    Options
    I'm the guy who linked their spec data awhile ago. Don't know about RFI. Keep me in mind should you decide to sell the Samlex. 

    Thought I had a case of Cotek 1500 watt inverters. I remember opening the box and selling one in fact. Does anybody know to refine the search function for "case of cotek inverters"? Geez - I get robbed so often I lose count. Like almost every month - somewhere. 
    First Bank:16 180 watt Grape Solar with  FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Softdown,

    I am not sure what you are looking for, but you can use the "site:" tag to limit searches (google, duckduckgo, Bing, etc.) to one website:

    site:https://forum.solar-electric.com case for cotek inverters

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • jmb
    jmb Registered Users Posts: 42 ✭✭
    Options
    Soft - I will likely keep the Samlex as an emergency spare.  Looking around on Amazon I see that Cotek is still available and I'm thinking about one of their 3KW models...
    Justin B.
    Cabin - 9 Mission Solar 310 watt panels, MidNite Solar Combiner, Iron Ridge mounting, 4 Speciaized Power 200 AH 24V LiFePO4 batteries, Samlex PST-1500-24 inverter, MidNite Solar Classic 200SL CC

    Barn - 9 Renogy 100W panels, Generic Chinese 40A MPPT CC, 6 Universal 12V 100 AH AGM batteries, Reliable 3KW 12V PSW inverter

  • softdown
    softdown Solar Expert Posts: 3,824 ✭✭✭✭
    Options
    jmb said:
    Soft - I will likely keep the Samlex as an emergency spare.  Looking around on Amazon I see that Cotek is still available and I'm thinking about one of their 3KW models...
    I wonder if the Cotek's are simply older models that have been sitting on shelves. I believe that Cotek and Samlex merger. My Cotek 1500 has a dumb design flaw. There is little room for large wire connective lugs - I had to grind them down severely to fit. Using 2/0 wire as I recall - almost surely larger than I needed. 
    First Bank:16 180 watt Grape Solar with  FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
  • jmb
    jmb Registered Users Posts: 42 ✭✭
    Options
    Making progress!  I have finished moving my inverter down into the battery cabinet and have ran the AC wires up to the breaker box in EMT conduit.  I also wrapped both hot and neutral 3 turns through a mix 43 oval core right after the wires exited the conduit in the breaker box.  I didn't have time to do an exhaustive test but it seems the inverter generated RFI has been significantly reduced!  My noise floor dropped to an S9 but I didn't have time to determine if that was natural noise or RFI.  Of course, that did nothing for the CC noise but that is another story...
    Justin B.
    Cabin - 9 Mission Solar 310 watt panels, MidNite Solar Combiner, Iron Ridge mounting, 4 Speciaized Power 200 AH 24V LiFePO4 batteries, Samlex PST-1500-24 inverter, MidNite Solar Classic 200SL CC

    Barn - 9 Renogy 100W panels, Generic Chinese 40A MPPT CC, 6 Universal 12V 100 AH AGM batteries, Reliable 3KW 12V PSW inverter

  • Vic
    Vic Solar Expert Posts: 3,208 ✭✭✭✭
    Options
    Hi Justin,

    The Outback inverters  --  Fx and VFXes  -- have been reported as having fairly significant high frequency ripple riding on the AC output waveform.

    OB introduced the FXR series several years ago.  Do not know how well suppressed, are their HF emissions.

    It would be a good idea to ask on the OB Forum,  and perhaps on the MN Forum.    Ask Hams with interests in HF communications,   for their actual experience with the OB inverters,   or,  really for real hands-on experience with any inverter that you are seriously considering.

    I have no personal experience with OB inverters.

    But please ask Hams that have been running your target inverter,   as opposed to those,  like me,  who have NO experience trying to listen through possible emissions.  Ask,  also what measures were taken to reduce any emissions,   and how effective this was in reducing them.

    Sounds like you are on the right track with your choke.   Mix 31,  should generally do a better job reducing emissions in the 1.8 - 15 Mhz (or so) range.

    73,  GL,   Vic   .   .
    Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  25 KVA Polyphase Kubota diesel,  Honda Eu6500isa,  Eu3000is-es, Eu2000,  Eu1000 gensets.  Thanks Wind-Sun for this great Forum.
  • softdown
    softdown Solar Expert Posts: 3,824 ✭✭✭✭
    Options
    Would ya'll speak English?  B)
    First Bank:16 180 watt Grape Solar with  FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Vic is speaking "Hammish". :)

    MX31 is a type of Ferrite... Different magnetic properties (need to match to the frequencies you are interested in blocking):


    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset