Watching youtube podcasts has led me to believe that lithium tool batteries (think DeWalt, Makita, Milwaukee etc) are packed with standard laptop type lithium batteries, they are designated 18650 and are significantly larger than a AA battery - guessing approx. 66% larger.
I'm guessing that it is routine with some experience and the proper accessories. Probably a bit of a challenge the first time.
Hoping to find a member to advise on what to expect.
I'm guessing that it is routine with some experience and the proper accessories. Probably a bit of a challenge the first time.
Hoping to find a member to advise on what to expect.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
Comments
-
Generally, batteries are spot welded to the bus straps (soldering generates too much heat for too long of period). And they use a spot welder for this (some random spot welders on Amazon):
https://www.amazon.com/battery-spot-welder/s?k=battery+spot+welder
You can make your own spot welder too. One example is using a transformer from a scrap microwave:
https://www.instructables.com/id/Spot-Welder-from-a-microwave-oven-transformer-and-/
Would that work for spot welding a battery? No idea--Just an example of a DIY welder.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Also, here is a link to a forum that deals a lot with DIY battery projects (a "flashlight" forum):
https://www.candlepowerforums.com/vb/forum.php
They have a good amount of information on Li Ion batteries too.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Very useful information BB - thanks! Plus it seems one needs these nickel tabs that are pretty inexpensive: https://www.amazon.com/0-15x6x50mm-Soldering-Capacity-Lithium-Battery/dp/B07PQP55CM/ref=sr_1_24?dchild=1&keywords=battery+spot+welder&qid=1595957853&sr=8-24
Somewhat decent spot welders cost about $200 and don't have a lot of reviews - while getting about 4.0 stars. More mainstream welders can be had for about $50 less and offer much better ~ 4.5 star reviews.
That's my preliminary take on it. I don't see much usage for a spot welder outside of battery assembly - so far. Guess I'll pass on this adventure for a bit.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
On the other hand - no serious prepper should be unprepared for a lack of replacement battery packs. I just wish we had a member who had luck replacing lithium 18650 tool batteries with an affordable spot welder. I might, and I might not, try this one for ~
$24: https://www.amazon.com/KKmoon-Integrated-Welding-Automatic-Accessory/dp/B085GF7PM7/ref=sr_1_21?dchild=1&keywords=battery+spot+welder&qid=1595981676&sr=8-21
EDIT: Such pens are accessories for spot welding machines. The vendors, to date, tend to gloss over that important detail. Few have been sold so far.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
This one has a good chance of getting a $130 job done - I think: https://www.amazon.com/BoTaiDaHong-Battery-Welding-Machine-control/dp/B07RGTTTF4/ref=sr_1_2?dchild=1&keywords=JD-IIS+Pulse+Spot+Welder+Welding+Soldering+Machine+for+Battery+Packs+3kw+110V&qid=1595983380&sr=8-2
What does this mean? "Note: Please match the air switch above 30A to prevent tripping."
Does it need a 30 amp power supply? That can't hardly be on a 120 volt tool.
Nothing wrong with 47 hobbies? Right?First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
As far as I can tell--That is just the spot welding tool. You have to still purchase another power supply to supply the current for the "pen".
A "supply" like this (just guessing):
https://www.amazon.com/Mophorn-Battery-Soldering-Portable-Batteries/dp/B07MZP2BK6
Or a "kit" like this:
https://www.amazon.com/737G-Soldador-Bater%C3%ADa-Bater%C3%ADas-Funciona/dp/B07M9JSQ7L
Not sure that any of these are really that "good"... Your mileage may vary.
There are lots of small spot welder videos/kits/methods of making a spot welder (even using Lipo batteries as a power source, etc.).
Just depends on how far down the rabbit hole you want to do...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Yes - I figured out the above pens are accessories for machines.
My next post has a complete machine that gives me a decent vibe. Here is the "power supply" for the pens I was looking at - the pens BB is referring to. This is the back of the spot welder I am close to trying out.
I could recover that much money from fixing a few power packs. 18650 batteries are quite affordable. Roughly $6 for pretty good ones as I recall. I probably have well over $1500 invested in lithium power packs for tools. They last 5-10 years - or so.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
You got me on the air switch. I see no connection for an air line, maybe they mean the foot pedal remote ?
Does the electrode move down to the battery pack, or does the user grasp the pack and stuff it up to the electrodes and then mash the pedal?
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Getting close to giving this a whirl. Ordered a batch of Samsung batteries already.
Noting the machine in BB's link requires that batteries be within very close proximity to the machine. The machine I linked offers a lot more space.
My next question: Everybody specifies a 10 year life span for 18650 lithium batteries. Now that Duracell D, C, and AA batteries come with "10 year life spans" - it does seem like lithium would do much better. Then again, these are rechargeable lithium batteries. Ten years is not bad but my how the years do fly by!First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Will you be matching cells by internal resistance or tested capacity ?
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Buying new Samsungs made in Korea, matching cells is not a currently anticipated issue.
As always this endeavor is opening up to more possibilities. Seems that Battery Management Systems should be used on lithium batteries. A subject I know nothing little about.
It should be nice to replace lead batteries with lithium when size and weight are issues. Size and weight are potential prepper issues.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Didn't we have a brave soul, or two, endeavor to make their own solar bank batteries out of 18650s? While most of us marveled at the combination of characteristics the endeavor required.
I mean - Tesla does it. Called the Power Bank? I'd like to see the material used to connect the batteries. I believe each cell has a fuse? That BMS must be a $ight to behold.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Wish we had more experience on this. There is a huge problem with calling nickel plated strips - pure nickel. Plus one seem to have a choice between ~$10 worth of nickel plated strips/pure nickel and ~$80 worth. This endeavor got complicated pretty fast.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
There are "bare" 18650 cells, and protected 18650 cells (each cell has an over/under voltage and sometimes over current protection disc on one end of the cell).
You should look at the battery box and figure out if the original cells were protected or not (the pack can have extra connections to monitor each battery for over/under voltage and "commercial" battery packs probably do not used "protected batteries"). And if they are LiFePO4 3.7 volt or other chemistry battery.
Battery Manufactures generally do not sell "bare cells" to hobbyists. Worried about cells being stressed/damaged/catching fire/etc. if not correctly used.
Placing two or more cells in series, and unprotected, you do run the risk of "unmatched cells" behaving badly during charging/use. Many (some/most/all?) power tool batteries should have separate connection points for each battery in the series string so that the charger can monitor/equalize the batteries.
Charging the batteries to the same starting voltage (if needed) should be done too.
Here is a simple video showing what is in a 12 volt Dewalt LiFePO4 battery.
https://www.youtube.com/watch?v=CZVr2B4GMvM
Just so that you can see what is in a "typical" battery pack. Note--The person making the video did solder the batteries instead of spot welding the battery connections--Not good (overheats the ends of the batteries, one end usually has an over pressure vent which can be damaged by excessive heat from soldering).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Some cells have "protection" it's a tiny BMS built into a dime sized wafer at the end of the battery, to prevent overdischarge. Overdischarge is the really dangerous thing, it sets the cell up to grow dendrites at some random point in the future, and the dendrites short out the cell and you get a firebomb in the middle of your battery bank, which triggers the rest !!
https://batteryuniversity.com/index.php/learn/article/bu_304b_making_lithium_ion_safe
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Here is a nice web page that lists many of the "protections" that can be "fitted" to a Li Ion 18650 Cell:
https://batterybro.com/blogs/18650-wholesale-battery-reviews/18306003-battery-safety-101-anatomy-ptc-vs-pcb-vs-cid
Hate to harp on this--But if you do rebuild your own Li Ion packs... I highly suggest that you recharge them outdoors/sheltered location on a fire proof surface (at least the first few times).
Not that YOU will have a fire--But if a Li Ion battery does catch fire/spill its guts out/etc., you don't want that to happen in your home or work shop (sometimes, a very hot fire and/or some very hazardous chemicals can be created/expelled from a failing Li Ion cell and create a very expensive/difficult to clean mess.
LiFePO4 is one of the safer Lithium chemistries (the 3.7 volt type you purchased??). But I don't suggest taking any chances.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Seems the key to safely employing lithium ion batteries is the BMS systems. Nice thing about repacking is the ability to reuse the manufacturers BMS system.
Changing the subject now. Doing more than two in parallel is generally discouraged due to safety. Think I have seen up to 11 in parallel. I need to study Li Ion BMS systems a lot more. Seem to mostly concern over charge and under charge conditions.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
generally nowdays, actual battery failures are rare, unless the BMS fails. Most failures seem to be related to over/under charge or car crash damage
And what's the wisdom of a $5K battery with a cheesy $30 "BMS" ??
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
mike95490 said:generally nowdays, actual battery failures are rare, unless the BMS fails. Most failures seem to be related to over/under charge or car crash damage
And what's the wisdom of a $5K battery with a cheesy $30 "BMS" ??
Lithium advantages:
Long life
Efficient charge and discharge
Deep discharge is safe
Light and small
Disadvantages:
Toxic fumes if they catch fire
Destroyed if charged when frozen
Perform poorly when cold
Expensive
Need BMS
Not friendly to recycling
Sellers still ask high prices for lithium battery packs that are for "parts only". Takes an optimistic buyer.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
mike95490 said:generally nowdays, actual battery failures are rare, unless the BMS fails. Most failures seem to be related to over/under charge or car crash damage
And what's the wisdom of a $5K battery with a cheesy $30 "BMS" ??
Here is a $4.49 BMS preceeded by 37 pages of even cheaper BMS boards. It doesn't look bad either: https://www.ebay.com/itm/25A-Li-ion-Lithium-Battery-BMS-18650-Charger-Protection-Board-12V-Cell/114292277400?hash=item1a9c59c098:g:dK8AAOSwaSpfBBD7
Super cheap BMS boards are quite likely to fail. But it seems like a savvy user could easily replace the board - knowing that is the likely issue.
If we could get quality BMS boards for sub $50 I would be inclined to make my own 12 volt batteries. But the issue of being compatible with serial connections is a huge one.
Much of the attraction of off grid solar is the independence from the grid. The same attraction likes with making ones own batteries. But one has to really know what they are doing. Even many of the manufacturers make stupid errors which are easily avoidable.
What does it take to make lithium battery packs compatible with serial connections? Battle Born is one of a select few that seems to know what they are doing.
Renogy, for example, is a large force in solar. Yet their lithium battery packs say this: These batteries can not be wired in series they can only operate at 12 volts. Odd.
Changing the subject a bit but I don't see why someone would pay somewhat similar money when Battle Born offers a 10 year warranty and serial connections. 12 volt solar systems are toys in my opinion - OK for RVing and part time cabin use etc.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
mike95490 said:Will you be matching cells by internal resistance or tested capacity ?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed