Flooded Acid Charge Rate
bigbrovar
Registered Users Posts: 32 ✭✭
Hi guys,
I changed cities and decided to restart my offgrid setup from scratch after selling of components from the former system (cheaper than transporting) I have 9 x 335w Yingli Solar panels, a Victron 150/100 mppt controller and a Axpert 3kva 24v inverter. I planned on getting a 4 24v 400AH battery but I am undecided on which of FLA and AGM to go with
I naturally prefer flooded acid battery due to their longivity when compared to AGM. Howvever my issue is the charge current.
Most FLA batteries are rated to be charged at 10% - 15% OF c20 at bulk stage or about 40A - 60A in my case. Based on my configuration, I might be getting close to 90A -100A during peak generation and my fear is this might affect or damage the flooded acid. I plan to offset the current dgoing into the battery by using oppotunity loads but that might not be enough to bring the charge current to the rated level required. On average my night load is about 90Ah - 100Ah so those batteries would be cycled at about 25% dod on a daily.
I quess my question is, can I, should I still go for the flooded battery? I might be charging the battery at 20% of c20 or even more. The alternative is to get an AGM battery which would cost a lot more and probably not last as long but which would be able to take everything my system throws at it in way of charging.
I want to make the most of my shallow depth of discharge and get the most from my battery while getting the most bang for my buck. Right now flooded allows me do this... but the charging rate issue.
I changed cities and decided to restart my offgrid setup from scratch after selling of components from the former system (cheaper than transporting) I have 9 x 335w Yingli Solar panels, a Victron 150/100 mppt controller and a Axpert 3kva 24v inverter. I planned on getting a 4 24v 400AH battery but I am undecided on which of FLA and AGM to go with
I naturally prefer flooded acid battery due to their longivity when compared to AGM. Howvever my issue is the charge current.
Most FLA batteries are rated to be charged at 10% - 15% OF c20 at bulk stage or about 40A - 60A in my case. Based on my configuration, I might be getting close to 90A -100A during peak generation and my fear is this might affect or damage the flooded acid. I plan to offset the current dgoing into the battery by using oppotunity loads but that might not be enough to bring the charge current to the rated level required. On average my night load is about 90Ah - 100Ah so those batteries would be cycled at about 25% dod on a daily.
I quess my question is, can I, should I still go for the flooded battery? I might be charging the battery at 20% of c20 or even more. The alternative is to get an AGM battery which would cost a lot more and probably not last as long but which would be able to take everything my system throws at it in way of charging.
I want to make the most of my shallow depth of discharge and get the most from my battery while getting the most bang for my buck. Right now flooded allows me do this... but the charging rate issue.
Comments
-
So, this is not the "right" answer, but I'll throw some real life at you.The larger the difference between battery voltage, and charging voltage, along with the internal resistance, sets how much current the battery will "draw". By lowering the voltage, you can reduce the amount of current it pulls from the charge source.if you hit a deeply discharged battery with a 15V 300A charger, you might get 200A for a minute or two. But as the battery voltage comes up, the charge amps start to taper off. Some controllers have a Max Amp limit you can program.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
As Mike suggests, a charge controller with current limiting is the logical solution.
Rolls recommends up to 20% (which is 80A) with heating listed as the concern if you go higher. My guess is that you could sometimes go to 100A if there is a way to limit temperature.I am available for custom hardware/firmware development
-
With 9 × 335 W panels you would likely see a maximum of 80A or 20% charge rate, this would only occur at peak sun in optimal conditions with discharged batteries. Because the array will ramp up as the sun climbs higher, the amount of time you would actually see that amount of current would not be extensive because the voltage would have increased to the point where current begins to drop.
Flooded batteries can take 20% charge rate for a limited time, the recommendations are generally based on grid charging from completely discharged state over an extended period of time. In a solar application it is probably benificial to use a higher current due to the limited window of opportunity.
If there is a need or concern, a controller with limiting capability could be used as stated above, or alternatively a load could be applied to the inverter to divert some current. Personally I think having 20% charge rate available with a 25% discharged bank would be fine and extremely benificial during less than ideal conditions.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Midnite Classic and "Kid" versions both support a remote shunt "Wizbang Jr" to allow control of charging current to the battery bank:
https://www.solar-electric.com/residential/charge-controllers.html?manufacturer=39&nav_pwm_mppt=411
https://www.solar-electric.com/midnite-solar-whiz-bang-jr-current-sense-module.html
Outback may also have an add-on that can measure/limit charging current--But I am less sure how well that works/how easy to configure.
If you size your battery bank for 2 days of storage, and 50% maximum discharge... That allows you to recover after a day or two with 10%+ rate of charge (typical 75% back to 90%+ charging).
If you have a very small FLA bank, (1 day of storage, 50% discharge), it usually takes closer to 2 days of sun to fully recharge the bank from 50% to 100% SoC. AGM and Li Ion can charge faster--So smaller AH battery banks can be OK as they will take more current to recharge back to full.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I have pv capacity to theoretically put ~100a into a 370ah flooded bank. Being normally colder than 25°C, effective capacity runs more like 300ah, so about C/3.
I've never seen anything like 100a in actual use, but having the extra pv is useful on lightly overcast days.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Thanks guys for the inputs. I went for the flooded acid batteries 200ah x 4 at 24v which would give me a bank of 24v 400AH I intend to discharge them over night at 90AH Max (Based on energy audit) so by morning I would need to put back about 90AH +- 10AH back to the bank.I am hoping that the system would be past the absorption stage before the panels hit peak generation mostly due to the size of my array (3kw). The opportunity load in the house is a fridge and freezer and both use less than about 10A combined. My fear is for the relatively high current not to damage the battery over time especially for period where the battery was drawn down to 50-60% (due to bad weather) only for they to be a burst of sunshine. It would be so nice if victron support integration with a remote shunt to allow it control current floor to the battery (this might happen in future firmware upgrades) for now blanket reduction of the rated currents outoput of the controller is not something I want to do.
-
What you could do is use a DC current sensor with a dry contact which drives a DC rated relay, the contacts of which would disable a string of the PV at a pre determined current threshold, thereby limiting charging current when needed. During periods of cloudy weather the full limited potential would be available because the threshold wouldn't be met.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I really doubt you're going to see "too much" current in bulk. Re-reading several manufacturers charging recommendations, it seems clear to me that C/10 charge capacity is recommended for grid charging, as total charging time exceeds available solar pretty much anywhere on earth. For solar applications, Rolls recommends 10-20% as a minimum pv/controller capacity, and gives no maximum.
The only time I see "high" (>~C/5) charging current is when I'm bulk charging with the genny, and the sun pops out unexpectedly. When this has happened, I haven't seen any material heating of batteries or other ill effects. With roughly similar pv to bank capacity ratio as you, I've never seen "high" current on pv alone. Maybe a mountain top location could, but I don't.
Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
bigbrovar said:I am hoping that the system would be past the absorption stage before the panels hit peak generation mostly due to the size of my array (3kw).
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed