Battery Bank not charging properly
Apica
Registered Users Posts: 35 ✭✭
Good day everyone, I'm having problems full charging 1 string/bank in my 450AH 24V battery bank which I have wired in a series/parallel configuration. I have no problem achieving 1.265 -1.275 SG from each cell in one bank but the no more than 1.250 from the second bank. I installed a Trimetric which will display 100% full but I'm not convinced that this is correct based on my hydrometer readings. What could be causing this? Any information will be greatly appreciated.
System A
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor.
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor.
Comments
-
Are they the same size, age and type of batteries?
Have they been wired so that they have equal resistance across each string Since they are connected together they are 1 battery bank made up of 2 strings. This is usually achieved by being sure that each connecting wire is the same gauge and length and connecting the bank to the system with wires from the positive terminal of one string and the negative terminal of the other.
There is more information here;
http://www.smartgauge.co.uk/batt_con.html
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Classic symptoms of imbalance, remove the good string and allow the lower string to reach the SG of the good string, don't apply any loads..Parrallel the two correctly, diagonally as pre link provided above, then equalize to bring everything into alignment before connection of loads.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Thank you for your fast replies.
PhotoWhit, The batteries are FLA and are all the same size however there is a 6 month age difference between both strings. The are all connected using 2/0 cable of the same length.
System A
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor. -
Mcgiver, I followed your suggestion and separated the strings this morning and left the bank to charge with no load. I'll check the SG later and update.System A
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor. -
Also, use a voltmeter and measure the voltage across each battery (during charging/discharging/resting). You have 8 identical batteries and they should all be nearly the same voltage (something like 0.1 volts or less ideally). If you have one "higher voltage" battery or electrical connection, it will greatly reduce current flow in that string.
And check the battery connections/cabling too. If you have one poor connection in a string, it will stop or greatly reduce current flow and prevent charging (and prevent discharging too).
If you do not have one yet, you might want to get a DC Current Clamp Meter. You can measure the current flow in each battery string during charging/discharging--Again you are looking for "differences" between otherwise identical strings/batteries.
Here is a mid-priced AC/DC Current Clamp meter:
https://www.amazon.com/gp/product/B019CY4FB4
Note--You can DC Current clamp meters from $50 to $350+. And any of them are "good enough" for our needs (debugging/understanding our systems). Note there are many AC only current clamp meters too... You do not want that for working on DC power systems (sometimes the descriptions are a bit confusing because you can have an AC only Current Clamp meter with AC+DC DMM (digital multimeter) to measure AC&DC volts--That is different.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
This is my battery bank design. The top string is the newer of the two that does not get any higher than 1.250.
System A
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor. -
Thank you BB, I'll check the voltage across each battery and connections as advised. Unfortunately I don't have a DC Clamp meter but I'll definitely look into getting one asap.
System A
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor. -
After a full day of charging 1 string with no load the specific gravity has risen to 1.265 in some of the cells, the others still remain at 1.250.
A voltage check across each battery this morning from left to right gave the following readings:
At Rest
6.17, 6.19, 6.18, 6.25
While Charging
6.43, 6.47, 6.46, 6.54
I'll post discharging voltage readings later on today.
System A
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor. -
The charging voltage seems low... Either the batteries are quite discharged--Or there is not much current flow (do you know how much current was flowing while charging?).
In general, referencing 12 volt battery--Around 13.6 to 14.8 volts (or 6.8 to 7.4 volts @ 6 volt battery) if the battery string is "actively" charging (something like 5% to 20% of rated capacity--I.e., 10% suggested nominal charge rate on a 220 AH rated battery would be ~22 amps under full sun or on genset/utility charger).
All the battery voltages added together should give you the bus voltage (i.e., 6.43+6.47+6.46+6.54=25.90 volts bus voltage), plus any voltage drop on wiring... Compare that to the voltage measured directly on the charge controller terminals (looking for too much voltage drop in wiring--I.e., small diameter wiring, long wire runs, loose/corroded connections).
25.9 volts on an FLA battery bus is either just after charging is completed (surface charge voltage--Around 29.4 to 29.8 volts for fully charged resting voltage is typical).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB, the Flexmax 80 was putting out 13.3amps while charging. The measurements where done at 7:45am.
I'll do measurements at various times of day on Sunday when it will be more convenient.
System A
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor. -
Apica, also, double check your voltmeter (check car battery, check AC house voltage, etc.). I have seen DMMs (digital multimeters) with weak/bad batteries give very consistent/weird results.
Those battery voltages are showing low voltage when charging... Typically that is because they are at a lower state of charge... Typically when a FLA battery hits >~80% state of charge, you should be much closer to ~14.4 to 14.75 volts (7.475 volts @ 6 volts) when you have significant charging current.
Here is a nice graph that estimates the voltage of a FLA battery vs various current flows (charging/discharging) and battery state of charge:
http://www.scubaengineer.com/documents/lead_acid_battery_charging_graphs.pdf
Note that these are estimates and may not apply to your setup... For example, a battery with C/20 (5%) rate of charge, a 13 volt @ 12 volt (or 6.5 volts @ 6 volt bank) should be around 50% state of charge.
Obviously, I am not measuring your system and I don't know about your meter/tools/conditions/age&conditions of batteries/etc..... But when something does not "look right", I suggest going into the details and get independent confirmation when possible (2nd meter, using current clamp meter to confirm sharing of current in parallel battery strings, etc.).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Hi . What size is your pv .. maybe not enough amps for your battery bank .2225 wattts pv . Outback 2kw fxr pure sine inverter . fm80 charge controller . Mate 3. victron battery monitor . 24 volts in 2 volt Shoto lead carbon extreme batterys. off grid holiday home
-
petertearai said:Hi . What size is your pv .. maybe not enough amps for your battery bank .1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Ahhh . I don't see a signature on my phone . Must check on laptop .2225 wattts pv . Outback 2kw fxr pure sine inverter . fm80 charge controller . Mate 3. victron battery monitor . 24 volts in 2 volt Shoto lead carbon extreme batterys. off grid holiday home
-
mcgivor said:petertearai said:Hi . What size is your pv .. maybe not enough amps for your battery bank .
Yesterday I purchased 1 more 270W Intenergy Panel. Now I have 6 x 260W panels (1560W) connected to the FM80 and 2 x 255W & 1 x 270W (780W) connected to the FM60 for a combined total of 2370W.System A
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor. -
At 6:00am these are the measurements I gathered :
At Rest
Trimetric: Battery Voltage 24.5, SOC 80% Power being drawn from bank 11.5W
FM80 LED Display Voltage 24.5V, Voltage at terminals 24.5V
FM60 LED Display Voltage 24.5V, Voltage at terminals 24.5V
Individual battery voltages: 6.10, 6.12, 6.11, 6.18
Total string voltage 24.51
at 7:00 I will switch power from grid to PV and update during the course fo the day.
System A
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor. -
BB, my DMM seems to functioning well. Thank you for sharing that lead acid battery charging chart.System A
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor. -
Apica said:mcgivor said:petertearai said:Hi . What size is your pv .. maybe not enough amps for your battery bank .
Yesterday I purchased 1 more 270W Intenergy Panel. Now I have 6 x 260W panels (1560W) connected to the FM80 and 2 x 255W & 1 x 270W (780W) connected to the FM60 for a combined total of 2370W.
Secondly the bulk/absorption voltage of 28.8V is probably too low for FLA, assuming there is temperature compensation, it should be somewhere in the mid 29V regon, depending on manufacturers recommendations, which may themselves be based on grid supply with extended charging times available, something not applicable to solar applications. Basically it's a fine ballancing act, using a higher voltage to force the current into the bank in the limited time available and "one size doesn't fit all".
Thirdly, if depth of discharge is 50% on a regular basis it only reinforces the need to increase the charging rate by increasing the voltage.
I'll leave now to see what others have to offer.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Excellent points Mcgivor. I recently purchased 2 Outback BTS but haven't gotten around to installing yet, so no temperature compensation at the moment.
My greatest challenge has been obtaining charging parameters for these Trace batteries, my research online has turned up nothing. I'm just being cautious using 28.8V for absorption. I have increased the bulk/absorb voltage to 29.6V before but was concerned about the high rate of water loss.
System A
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor. -
Apica said:At 6:00am these are the measurements I gathered :
At Rest
Trimetric: Battery Voltage 24.5, SOC 80% Power being drawn from bank 11.5W
FM80 LED Display Voltage 24.5V, Voltage at terminals 24.5V
FM60 LED Display Voltage 24.5V, Voltage at terminals 24.5V
Individual battery voltages: 6.10, 6.12, 6.11, 6.18
Total string voltage 24.51
at 7:00 I will switch power from grid to PV and update during the course fo the day.
Update
10:20 am and Batteries are now in absorbing
Trimetric : Battery Voltage 28.6, SOC 91%
FM80 LED Display Voltage 28.8V, Voltage at terminals 28.8V, Amps Out 43.1A, @ 1130KW
FM60 LED Display Voltage 28.8V, Voltage at terminals 28.8V, Amps Out 24.9A @ 680KW
Individual battery voltages 7.05, 7.06, 7.05, 7.16
Total String voltage 28.32 ( How can this be possible?)
System A
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor. -
It looks to me like there's about a half volt of voltage drop between CC and bank. What size and length is the wire?
That much drop means the bank likely isn't getting proper absorb voltage, so settings should be increased to compensate.
Temp compensation is quite important for proper charging if ambient is more than +/- a few degrees off 25°C, and to limit charge related heating (and excess water loss) if warm.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Measure the voltage at the FM 80 terminals vs Battery Bank bus bars with the same DMM.
Note that if your temperatures are greatly different than ~75F, I have seen some charge controllers give a "corrected" temperature reading to ~20C/70F... Don't know about Outback specifically.
Assuming the FM 80 gives actual battery bus voltage reading, many controllers can be adjusted to the match a reference DMM reading (always raises the question is your DMM or FM 80 more accurate).
Wikipedia: Segal’s law
Segal’s law is an adage that states:
“A man with a watch knows what time it is. A man with two watches is never sure.”
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Estragon said:It looks to me like there's about a half volt of voltage drop between CC and bank. What size and length is the wire?
That much drop means the bank likely isn't getting proper absorb voltage, so settings should be increased to compensate.
Temp compensation is quite important for proper charging if ambient is more than +/- a few degrees off 25°C, and to limit charge related heating (and excess water loss) if warm.
I just installed the Outback RTS to the FM80, left the default setting (WIDE) and noticed the absorb voltage dropped from 28.8V to 28.6V but the FM60 was still absorbing at 28.8V. Should I attach the second sensor for the FM60 to the same battery or wait until I connect the other string and attach to anther battery?System A
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor. -
6awg over a 4' run at 40a current should only drop maybe 1/10th volt. Like Bill suggests, maybe try measuring at both ends (with good current flowing). Maybe a connection needs retorquing?
My classics are networked, so they share a RTS (also charge stage changes). I assume FMs can be networked, but maybe yours aren't set up to share? I have my RTS stuck to a middle battery about 1/2 way down. If room temp gets much different than batteries, some people tape a chunk of insulation over the sensor to get a better reading.
If not networked, I'd put the other sensor next to the first on the same battery. Ideally, you want both controllers in the same state at about the same time, which they likely won't do if they have different target absorb voltages.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Definitely install both if not networked, the controller without a RTS will raise the voltage above the target of the other with the RTS essentially shutting it down. They need to both act as a team with the same goal plan, the compensated voltage being target, the RTS should be programmed to reduce the voltage by 0.005V (5mV) per cell per °C or by 60mV for every °C on a 24V nominal system.
The reverse occurs as temperature drops below 25°C, increasing the voltage inversely proportional to the > than 25°C value.
As an example let's say the bulk/absorb setpoint is 29.6V, at 35°C (95°F) the target voltage would be reduced to 29.0V, this is important because it's a dynamic function, the battery temperature is not constant, self heating whilst under charging conditions due to the inherent inefficiencies of lead acid batteries. Conversely the battery temperature will drop overnight meaning the target voltage value may well differ throughout the day, it really takes a lot of guesswork out of the equation when using a RTS.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Today was very sunny so I took the opportunity to do some tests still using 1 string (225AH) which were discharged to 54% SOC the night before. I decided to use only the FM80 CC which now has the RTS installed to charge the batteries and increased the absorption voltage to 29.6V for 2 hours.
After a full day of charge with no load and a maximum current of 41.2A. I observed that the absorption voltage had decreased to 29.2V At the end of day I took measurements across the battery bank at rest, FM80 Led Display & Terminals, Bus bars and Trimteric voltage and all were the same for the first time... 26.1V. However a SG check of the battery cells left me disappointed. They were either 1.265 or 1.250. I'm right back where i started. I'm beginning to wonder if these batteries are defective.
Tomorrow I will do a Equalization at 31V and measure again.System A
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor. -
The difficulty with monoblock batteries is if there is a weak cell (low SG ), is the other cells reach a higher voltage not allowing the low cell to increase sufficiently to gas so the SG remains low at the expense of the other cells. This phenomenon is even more difficult whth long strings, 12 cells in your case, more cells to form the aggregate voltage, this is where equalization is used to provide enough voltage to overcome the deficit seen during normal charging. Cycling of the battery will only make the process take longer, two steps forward, one step back.
Before equalization the battery should be fully charged, if the cells in question begin to gas, that means the voltage is high enough, check the SG every 30 minutes, when it matches the other cells or fails to increase after 3 hours there is little point in continuing as it would be more harmful to the ballance of cells. Use the temperature sensor, the battery temperature will increase, the compensated voltage is sufficient.
FWIW, when I switched to lithium my lead acid bank had low SG cells, nothing outrageous just something like yours, they remained essentially unused but on charge for weeks, only load was an on demand 100W water pump. After this time had passed all cell SG's were perfectly matched without any EQ, time it seems is all it took.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Just an update.
After equalizing the problem string for 4 hours I was able to get SG on each cell in the bank to 1.275. Both strings have been paralleled, absorb time and voltage has been increased to 3 hours and 29.2 Volts and things have been going smoothly. My only concern is that 1 string (i.e the one that previously had no issues achieving high SG readings) uses up much more water.System A
1500W Samlex Pure Sine Wave 24V Inverter. 2080 Watts Total Intenergy Panels. Outback Flexmax 80A. 4 Rolls 6V 445AH Batteries Wired in series for24V. Trimetric 2030. Midnite E-Panel. Tycon Tpdin Remote Monitor.
System B
Trace DR1524 MSW Inverter 24V. || 2080 Watts Intenergy Panels. || Outback Flexmax 80A. || 1 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Tycon Tpdin Remote Monitor. -
Apica said:Just an update.
...... My only concern is that 1 string (i.e the one that previously had no issues achieving high SG readings) uses up much more water.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 607 Discussion Forums/Café
- 301 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed