Inverter not starting
vsrenergy
Registered Users Posts: 4 ✭
Hi folks,
Required technical advise.
we installed the 10 MW Solar Power Plant in Morocco. inverter is not starting at morning time when even radiation required level?. please advise to troubleshoot this issue. for more claification find below information.
1. site has high relative humidity its around 93%
2. PV panels are cleaned
3. plant is tracker type. tracker starting at 8:30
4. inverter make is ingeteam and starting at 10:30 when radiation is more than 200 w/m2
Required technical advise.
we installed the 10 MW Solar Power Plant in Morocco. inverter is not starting at morning time when even radiation required level?. please advise to troubleshoot this issue. for more claification find below information.
1. site has high relative humidity its around 93%
2. PV panels are cleaned
3. plant is tracker type. tracker starting at 8:30
4. inverter make is ingeteam and starting at 10:30 when radiation is more than 200 w/m2
Comments
-
I'd advise you to call the installer / dealer / vendor / Mfg.How old is the gear? do logs show any degradation in the days/weeks before the failure ?Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
mike95490 said:I'd advise you to call the installer / dealer / vendor / Mfg.How old is the gear? do logs show any degradation in the days/weeks before the failure ?
its newly commissioned plant. we are facing this issue in commissioning. showing isolation fault. whether high moisture will affect the circuit? -
Hi humidity should not a affect an installation , except posibly, after some time . Water ingress will of course be a problem .
Are you the installer ?
Posting a list of the equipment you have installed will help get reply that may be of some use .2225 wattts pv . Outback 2kw fxr pure sine inverter . fm80 charge controller . Mate 3. victron battery monitor . 24 volts in 2 volt Shoto lead carbon extreme batterys. off grid holiday home -
It seems to me that at 93% humidity it wouldn't take much of a temp change for condensation to form and bad stuff to happen.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
I'm guessing the installation is coastal with that sort of humidity, basically a saltwater fog. In lower overnight temps, the fog condenses on wiring and components. In higher daytime temps, the water evaporates off, leaving a salty crust behind. The next night brings more salt fog, and more salty deposits. Eventually, you get enough condensation and enough salt to make a good short circuit.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Estragon said:I'm guessing the installation is coastal with that sort of humidity, basically a saltwater fog. In lower overnight temps, the fog condenses on wiring and components. In higher daytime temps, the water evaporates off, leaving a salty crust behind. The next night brings more salt fog, and more salty deposits. Eventually, you get enough condensation and enough salt to make a good short circuit.I'm partially agree with your point. if it is positive, what will be solution. please guide.
-
petertearai said:Hi humidity should not a affect an installation , except posibly, after some time . Water ingress will of course be a problem .
Are you the installer ?
Posting a list of the equipment you have installed will help get reply that may be of some use
inverter - ingeteam power max 1164 kw
module - astronergy
SMb- trinity touch india -
An Isolation fault would likely have to do with the transformer that provides galvanic isolation from the grid.
Do you feed into a transformer before the grid?
Humidity rating of the unit is 95% non condensing
Below is an excerpt from the manual.These units are equipped with the necessary filtering elements to comply with EMC requirements for industrialapplications in order to prevent disturbances in other equipment outside the installation.All of these units are connected to the grid through a low to medium voltage transformer. This transformer givesthe unit galvanic isolation that affects its good performance in terms of noise emission (see Section “7.6.1. Gridconnection transformer”). This is why:Any auxiliary element must be connected to the low voltage network powering the units via a galvanicisolation transformer (see Section “7.6.2. Auxiliary transformer”)1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed