series or parallel configuration
Comments
-
You will need them to be in series so that the MTTP charge controller can work properly, They need about 30% above the charging voltage to work properly. 24v batteries charge at around 29 volts.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
I have a related series/parallel question.
If you wire panels in series, the current stays at a minimum. How does this affect what size MPPT controller you need? I have a feeling it doesn't help that the input is low amperage because it will be converted to high amperage going to your batteries, and the controller still has to be able to handle that.
For example, I'm looking at 3x 175 W "12 V" panels. Vmp = 19.06V. Imp = 9.18A. If I string three in series, that's 57.18V and 9.18A. In parallel, it's 19.06V and 27.54A. I'm assuming that even in series configuration, I'd need at least a 30A controller because the MPPT controller is going to convert all of that voltage into high amperage going to the batteries. The rating is not just for the input, right?
I've seen a lot of mentions that the maximum current for bulk charging should be C/5. (Which I understand to mean the C20 amp hour rating of the battery divided by 5, in amps) With a 225 Ah battery, that would be 45 amps. I can't reach that with those three panels. Even if they reached their peak in perfect sun, and the controller were 100% efficient at converting it to 14.8V it would only yield 35.5 A. But that still suggests that I need at least a 30 amp controller, and probably more like 45 amp.
Does this all sound about right?
-
Sort - of...
Charge controllers are rated on output amps, So a 30 amp MPPT type charge controller with your 3 panels would take in max about 175watts x3 panels or 525 watts, Your max output would be around 525 ÷ 14.8 charging voltage = 35 amps in a perfect world. In reality your panels will produce about 75% of their panels rating so you will be around 26 - 27 amps. Most MPPT type can be and even suggest 'over paneling' by as much as 30%.
Speaking to batteries, they vary by type, but flooded lead acid batteries should be comfortable with 13% charge of their C/20 rating. So a 225 amp battery should be fine with a 225 x .13 = 29.25 amps charging. Check with your battery manufacturer.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
To add a bit to what @Photowhit noted, one input number you do need to pay attention to is the maximum input voltage of the controller, at the maximum temperature adjusted Voc (not Vmp) of the string of panels, for the record low temp at your location.
Three nominal 12v panels in a string (Voc ~70v) should be fine on most controllers in that amp range, but something to check.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Many inexpensive controllers are limited to 50-100V PV string input. Larger controllers can accept up to 150V string input. A few go to 600V inputs. Lots of spec sheets to read and compare - panels vs controllers
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
I was just looking at the MorningStar TS-45 spec, which also covers the TS-60, and I found this quote:Ratings to 60A at 48VDC will handle solar arrays up to 4kW.
4 kilowatts? How is that possible?
https://www.marlec.co.uk/wp-content/uploads/2015/10/TriStar-Datasheet-English.pdf
At any rate, someone in the comments said they've been using it for 17 months with 600W of panels and 6x T-105 batteries. That's very close to what I had in mind, except I was only planning on 4 T-105's. Six is a heck of a lot with only 600W.
Is there any advantage running a PWM controller with your panels in series like there is with MPPT? The Voc Max is 125V, so it seems like you could do it. I'd think the higher voltage is good if your wires are long and you didn't want them to be huge.
-
Configuring a good quality MPPT charge controller, you can use a 77% or 75% derating of panels (Vmp depression as panels become hot on bright/sunny days, with a bit of dust on panels, and controller losses) and very easily have a nicely working system with an array of:
- 60 Amps * 59 volts batt charging voltage * 1/0.77 panel+controller deratings = 4,597 Watt array "typical cost effective maximum array"
A major reason for MPPT on large systems... >200 Watt (Vmp~30+ volts) panels are 1/2 the price vs 140 Watt (Vmp~18 volt) panels (Vmp~18 volts are the "optimum voltage" for charging a 12 volt battery bank with an PWM controller). (on the negative side, MPPT controllers are much more expensive than PWM controllers).
And there is that you can use (for example) a Vmp-array~100 VDC and much smaller diameter wire (and longer distance runs from Array to battery shed) vs trying to make an "18 volt" Vmp-array with a PWM controller charging a 12 volt battery bank.
That an MPPT controller can "get more power" from solar panels--For properly designed PWM vs MPPT systems, MPPT controllers only harvest substantially more power from solar installations with lots of cold (typically sub freezing) weather (when Vmp rises due to cold cells).
Another "nice" thing about MPPT controllers, you can run a "higher voltage" array in hot climates and fully/quickly charge the battery to higher voltages (and higher Equalizing charging voltages--When Vmp-hot have lower array voltages).
Also, high end MPPT controllers have more options (like communications/Internet) and more programmability/charging configurations than PWM (less expensive) controllers.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
MysteriousFoundation said:Is there any advantage running a PWM controller with your panels in series like there is with MPPT? The Voc Max is 125V, so it seems like you could do it. I'd think the higher voltage is good if your wires are long and you didn't want them to be huge.
So if you have panels that are 17.5 vmp and your charging voltage is 14.8, the voltage above 14.8 volts is simply moderated by Moderating a pulse to the battery. If you had higher voltage coming in you would just lose the higher voltage (if the charge controller can handle it) So a string of 3 panels producing 17.5 volts and 6 amps each, or a string of 52.5 volts and 6 amps would produce a charging current of just 6 amps.
A MPPT type charge controller does down convert DC to DC so you would get a bit more current (amps) than 3x the 6 amps.MysteriousFoundation said:I was just looking at the MorningStar TS-45 spec, which also covers the TS-60, and I found this quote:Ratings to 60A at 48VDC will handle solar arrays up to 4kW.4 kilowatts? How is that possible?
So at 12 volts charging, a charge controller that can handle 60 amps can handle 60 amps x 14.8 volts = 888 watts, 888 watts x 1.3 = @1150 watts.
As the voltage doubles with a system voltage of 24 volts, the same charge controller can use twice the watts at 24 volts systems charging voltage of 29.6 volts...
And double again at 48 volts!
This is one of the advantages of higher system voltages.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
MysteriousFoundation said:
Is there any advantage running a PWM controller with your panels in series like there is with MPPT? The Voc Max is 125V, so it seems like you could do it. I'd think the higher voltage is good if your wires are long and you didn't want them to be huge.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
MysteriousFoundation said:I was just looking at the MorningStar TS-45 spec, which also covers the TS-60, and I found this quote:Ratings to 60A at 48VDC will handle solar arrays up to 4kW.
4 kilowatts? How is that possible?
https://www.marlec.co.uk/wp-content/uploads/2015/10/TriStar-Datasheet-English.pdf
At any rate, someone in the comments said they've been using it for 17 months with 600W of panels and 6x T-105 batteries. That's very close to what I had in mind, except I was only planning on 4 T-105's. Six is a heck of a lot with only 600W.
Is there any advantage running a PWM controller with your panels in series like there is with MPPT? The Voc Max is 125V, so it seems like you could do it. I'd think the higher voltage is good if your wires are long and you didn't want them to be huge.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Photowhit said:...Charge controllers are rated on Output amps and can handle about 30% over paneling due to the nature of how panels are rated and what they can actually produce when hot.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed