Running my wood stove fan off panels/batteries

C_Heath
C_Heath Registered Users Posts: 23 ✭✭
Hey guys

I am a 100% wood furnace user. Last month we had a nasty ice storm and I crippled us for 12 hours. Luckily I have a generator and we didn’t freeze because I kept the fan running on the stove but during all this I got to thinking what if I didn’t have the generator??

So I did some calculations and mind you I suck as calculations but my stove fan operates at 228 Watts. It’s one speed and in the winter will run 24/7 as long as I am burning wood.

By my sometimes inaccurate calculations this ends up be 5.47kwh per day?

I will be running 4 rooftop panels at 1200 Watts into an inverter for the ac stove fan. Now, this is where I run out of talent. How many batteries and what size to power the fan for let’s say 2 to 3 days without a charge in case of clouds or no sun.

Thanks to who takes the time out for this.

C in N.C.

Comments

  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    Your calculation is correct, which makes the fan extremely expensive to run with battery backed solar, without doing a calculation, using my daily consumption of~4.5 kW you'll need approximately 16×225Ah golf cart batteries for 2-3 days autonomany. The PV would need to be sized sufficiently to recharge the batteries, being that it is a standby application 1200W would suffice, It would need 12 hours +  of charging to replenish the batteries depending on depth-of-discharge. By contrast a Yamaha EF 1000 IS generator will run the fan for ~ 24 hours on a gallon of gas, cost way less than the batteries alone, probably outlast the batteries, which  have a limited life expectancy 5-7 years, give or take, wether used or not. Not trying to discourage you in any way, but solar energy is not cheap, the only way to offset some of the costs is with a grid tied hybrid system assuming tiered rate structure where load shaving can at least recoup some of the investment in batteries, as well as using excess production, or sell if possible because in float most would go wasted. Batteries sitting  in float, waiting for an outage, would be money wasted. My opinion others may differ.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • jonr
    jonr Solar Expert Posts: 1,386 ✭✭✭✭
    Would be cheaper to buy an old fashioned wood stove that doesn't need power.    Maybe consider converting a generator to propane (easier to store for long periods).

    I am available for custom hardware/firmware development

  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,894 ✭✭✭✭✭✭
    I stopped using the fan on my wood stove 25 years ago....
    How big is the home or cabin?
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • C_Heath
    C_Heath Registered Users Posts: 23 ✭✭
    I stopped using the fan on my wood stove 25 years ago....
    How big is the home or cabin?

    My home is 2000 square feet and my stove is brand new and its piped into the ductwork. So its a furnace so to speak. Its the best heat ever so even if I have to just suck it up and use power then so be it. I just wanted to see. After some other calculations, I will probably need around 10 batteries to get the job done. That's a little too many for the application for it to be worth it to me.
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,894 ✭✭✭✭✭✭
    Mine is the "best heat ever" also. 
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    edited February 2018 #7
    Is the fan a critical element in the survival of the stove, ie it will be damaged if there is no fan?  our old wood furnace could be used with a smaller fire and removing the end panels on the fan enclosure, and let good old convection distribute the heat, not quite as efficient but  we did not freeze either....BTW this is where the term "Central Heating" is really important, it really does have to be in the CENTER of the house...
    .
    ADD:  Oh yes there are also the ECO-Fans that use a piezo generator to power the fan once the stovetop is >150*C. 
    That is all we use for 2 x 1100 sq. ft . floors
     
    KID #51B  4s 140W to 24V 900Ah C&D AGM
    CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
    Cotek ST1500W 24V Inverter,OmniCharge 3024,
    2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
    Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
    West Chilcotin, BC, Canada
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,894 ✭✭✭✭✭✭
    edited February 2018 #8
    Good question Eric!  Since we always design for winter offgrid to minimize electricity there is a flaw with this choice.
    The OP should try (if safe to do so) running without the fan. Most offgrid homes even larger than this do not need a fan to heat from a wood stove.
    The fan just makes it faster or moves air into rooms with closed doors. Open the doors and test it without the fan!  Good Luck!
    The fan here is more than the load of a  good 25 cubic foot refrigerator. Only large systems can absorb these kinds of loads and the reefer is cycling.
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • wellbuilt
    wellbuilt Solar Expert Posts: 763 ✭✭✭✭
    I've been running my house on a little champion genarator since Augest .
     We are there working 3 days a week .
     I get 3 days on a 2 gallon gas can its 50hrs in 3 days 5 bucks . 
     It burns about 11 hrs plus on a gallon of fuel . 
     I think just run a small Jenny if the power goes out
    Out back  flex power one  with out back 3648 inverter fm80 charge controler  flex net  mate 16 gc215 battery’s 4425 Watts solar .
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Because of this, we designed and built our 2300sf 2 story house with passive heat, from a Masonry Heater
    Cold days (mid 30's and below) we burn 40lb of wood. It'd really be less, but Kalifornia has a rule that a damper can now be only 70% closed.  30% of a 8" flue lets a lot of heat out.



    There are some heaters that can be added to an existing house, most are built as the house is built around it

    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,894 ✭✭✭✭✭✭
    There is masonary heater here Mike that is in a Log home from the 1880's. The place is 3,500 + and the old guy who lives there keeps it really nice. He is up at 4,200 feet and he amazes me for his age. His family has owned the place since way back. He has a full progression of Diesel gensets from when they were first sold. All the old Perkins are in his garage. I was the one who convinced him to get batteries and an XW and he is so happy now having fuel deliveries only once a year.

    The really amazing part is that the logs in his home are still quite beautiful. I doubt we can get the preservative in Kalifornia >:)
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • just starting
    just starting Registered Users Posts: 235 ✭✭✭
    I have a magic heat reclaimer uses 36 watts, I put it on this year, I have to clean my stove pipe 3 times a year now, about 1/2" build up with 24/7 burn, home stays nice and warm now
    200ah LiFePO4 24v Electrodacus Sbms40 quad breaker chest freezer to fridge- Samlex PST 1524 - Samlex pst3024  - 1hp shallow well pump-Marey 4.3 GPM on demand waterheater - mama bear Fisher wood burning stove, 30" fridgarair oven ,fridegaire dishwasher  Unique 290l stainless D.C. Fridge-unique 120l portable fridge/freezer