Inverter refrigerators and their interactions with search mode energy conserving DC /AC inverters
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Comments
-
Are you testing an SW 2524 230 ?
The SW 2524 230 online manual states, the minimum Search Load = 25 watts.
Maybe, this manual is not for your inverter or your have updated firmware?
Also, can you try a resistive 5 Watt Load, an old C7 Incandescent Christmas Bulb 5 Watt, to see if that works?
Maybe, your loads are only drawing current during a too narrow portion of the PEAK AC Voltage or
the pulse voltage is too low to even get enough current flowing through your non-resistive loads.
Schneider may need to look into their Search Algorithm, 'cause we don't have very many resistive type loads vs 1 decade ago.
-
I had a similar problem with Rennai on demand water heater and Morningstar inverter. Turning on a light woke it up, but otherwise nada.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
It sounds like you may have mis-read the minimum current required to activate it through the search. Might want to re-check that.
-
mvas said:Are you testing an SW 2524 230 ?
The SW 2524 230 online manual states, the minimum Search Load = 25 watts.
Maybe, this manual is not for your inverter or your have updated firmware?
Also, can you try a resistive 5 Watt Load, an old C7 Incandescent Christmas Bulb 5 Watt, to see if that works?
Maybe, your loads are only drawing current during a too narrow portion of the PEAK AC Voltage or
the pulse voltage is too low to even get enough current flowing through your non-resistive loads.
Schneider may need to look into their Search Algorithm, 'cause we don't have very many resistive type loads vs 1 decade ago.
It is a SW 2524-230, the minimum search watts is 5W, it will wake up with a simple restive load, just not with the inverter refrigerator or led lights, could be as you say, just clipping the peak, if the pulse was longer in duration than the 0.25 second (estimated) and more like 2 seconds ,it may be enough to get things started, but that is just speculation.at this point. Will experiment futher using a clamp on ammeter, to time how long it takes to actually draw current, an adjustment to the algorithm may be all that is required , yes a decade has brought more challenges to the engineers who rely on feedback, which I certainly will provide, pending futher investigation.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Good information, I will be following this.
Marc
I always have more questions than answers. That's the nature of life. -
Back when solar was expensive and people were new at solar this was a valuable feature. Adding the incandescent or using an external thermostat was often done. I am sorry to not be of much help but there is little chance you will get a change to be made for this. It just is not used and on the Outback forum they basically said the same thing with slow start circuits. More solar is the fix along with a battery that can support it."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Thanks Dave, there are other ways around this dilemma that have been floating around my mind, all theoretical at this point, how about using a digital time clock to provide a resistive load for, let's say one minute every hour, which will wake up the inverter, thereby allowing any load which can't wake it up, to begin operating, if required, otherwise it would return to sleep mode. Not perfect, but just ideas that may trigger the brains of others.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I think if you wake up with spoiled food your wife will not smile! That may trigger the brains of others also!"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
More or less, in my humble opinion, once you have chosen to run a refrigerator off of solar, you are in a whole 'nother ball game of higher loads, more variable loads, high starting surges, etc... A refrigerator can draw 100% more for a day than planned power just if you put a bunch of warm food or unfrozen stuff in the freezer, or even running the ice maker.
Many things can be rescheduled... Washing clothes, vacuuming, cooking with electricity (using wood/propane/etc.). Many of these loads are ones that you run when you are home/at the cabin. Refrigeration is a (relatively large) automated load, if you don't have enough power and your food warms, your freezer defrosts, etc.... That is it.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Running a refrigerator off grid is the major consumer which is why planning is so important with regards to when items are put into the freezer, mornings only to opportunity load, along with the other loads mentioned, my wanting to use the search mode is more for night time when there is no opening of the doors. Setting the thermostat to minimum, brings the temperatures down to 1°C refrigerator and -20°C freezer, after an hour of no openings, the temperatures are 3° and -17 respectively,so still within the safe range , tested with a Fluke DMM with a thermistor inside, ambient, 25°C.
My battery is large enough to support the refrigerator, no problem there, the purpose of the post is mainly to share results of experiments, so others might not make the assumption that an inverter type refrigerator will work with search mode, by thinking it dose, only to discover later, with spoiled food perhaps, that their wonderful energy saving purchase could actually cost more to run, energy wise , due to the DC /AC inverters self consumption needed to support it at all times, is higher than that of a regular refrigerator used in conjunction search mode.
The question was asked in this thread, didn't want to derail
http://forum.solar-electric.com/discussion/351398/lg-inverter-refrigerators#latest1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Pity they can't be made to run on DC and bypass the external inverter entirely.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
DC wiring in living space would never pass a code inspection for a new home. Thinking more on this, it might"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
They probably could run on DC because the AC is rectified anyway, catch is the polarity would have to be correct and the battery voltage would have to meet the input parameters, so a 120VAC unit would need a 120VDC battery, which is not that common.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Could use a dc/dc converter, but hacking their shiny new fridge probably isn't on for most folks, and would no doubt void warranty.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
The one I have allows 110-270VAC, 50 or 60 Hz,, no mention of DC, probably for polarity reasons??1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
In the US/Canada, and in all the new homes I have installed a power system in (over 100 including some old ones) if there is an inspection, the home must be wired for normal AC wiring. Absolutely no DC except at the battery to inverter and solar connections.
I know you do not care so much for warranty in Thailand so go ahead. It would be nice to know. A friend did this with a mini-split heat pump and saved about 3% of the energy so do not expect much other than fixing the search. If all of this has value to you, go for it!"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
A "one minute per hour resistive load" sounds like a great idea to get a refrigerator to start. Perhaps inverters should include this feature (ie, normally scans for loads, but occasionally fires up to see if loads are waiting).
Almost every AC->DC circuit uses a bridge rectifier. So when applying DC, the polarity doesn't matter. But the peak voltage does - so for a 120VAC device, apply ~170VDC. But only after checking the circuit to verify that the 120VAC is only fed to a rectifier.I am available for custom hardware/firmware development
-
I faced a similar situation with my Magnum MS4448PAE inverter and the search mode requiring a minimum of 5 watts to "wake-up". I would try to turn on a 9.5 watt LED light and it would just flicker according to the search pulses put out by the inverter. The key here is that it takes a 5 watt resistive load, like others in this thread have alluded to. I'm guessing you're facing much the same thing with your inverter refrigerator...an LED with a power supply acts as an inductive load, not a resistive load. The search mode on the inverter can much more accurately sense a resistive load than it can an inductive load. I ended up having to turn on multiple LEDs to get the inverter out of the search mode...in the end I just turned the search mode off and dealt with the tare loses. Hope this helps!
100% Off-grid with: 8 Solarworld 275 Watt Panels, 8 Concorde SunXtender 405aH 6v AGM Batteries, MS-4448PAE 48v Inverter, MidNite Solar Classic 200 Charge Controller, 10,000 gallon rainwater collection system, etc. -
This discussion makes me wonder if there is a similar reason that GE put a filament bulb in our 3 yr old fridge, instead of LED, for an interior light? My Cotek inverter is in 'search ' mode... and no problems starting, but I can not find any info on the compressor, it's not soft start at 30A 24V is it? at least not to me. I would expect ~ 5A to be called soft start...
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
westbranch said:This discussion makes me wonder if there is a similar reason that GE put a filament bulb in our 3 yr old fridge, instead of LED, for an interior light? My Cotek inverter is in 'search ' mode... and no problems starting, but I can not find any info on the compressor, it's not soft start at 30A 24V is it? at least not to me. I would expect ~ 5A to be called soft start..
.
With a clamp on ammeter on the DC input to the DC /AC inverter, the inverter refrigerator will climb slowly to about 5.4 amps above the tare load on start up, this takes about 5 seconds, the duration of the pulse is too short to recognize the load. Unfortunately only the frequency and watt recognition can be programmed, not the duration of the pulse, which is less than a second.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Turning off search mode..... in the end isn't a big deal . Most inverters need to run for lights at night tv . washing machine etc.
so in effect your not running the inverter unnecessarily for 24 hours a day but maybe only 12 hours a day . An extra pv panel will easily sort that .2225 wattts pv . Outback 2kw fxr pure sine inverter . fm80 charge controller . Mate 3. victron battery monitor . 24 volts in 2 volt Shoto lead carbon extreme batterys. off grid holiday home -
Great responses to the original question re LG Inverter Fridges. Good behavior on search mode is really useful for weekend cabins that keep the fridge/freezer going full time but no one is home opening doors, adding food etc. There was a post on the other thread that the LG fridges woke up successfully but I didn't catch much in the way of details - i.e. search mode settings that made the fridge work.
We are looking forward to getting our main solar system up and running soon and getting off of noisy construction gensets.
Just wired a separate (alternate) fridge power outlet to the utility room so I can run an LG Inverter Fridge off of small always on low tare sine wave invertor if search mode operation doesn't work out well.
Thanks! Yrs, Graham and Laurie
Offgrid in cloudy PNW
Full Schneider system with 18 REC 420W panels, 100A-600V controller, XWPro, Insight Home, six Discover AES Rackmount 5kW batteries, Slimline enclosure, Lynk II, AGS, H650, H2200, H3000 (On Victron AutoTrans with Gen Line 2 wire AGS on AC1), Kubota 4500, Onan 7500 (on second AGS and AC2).
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed