Best type of battery for well pump?
I will be the first to say that I know very little about batteries in general, but here is my question: the main item being powered by my small system (see description below) is to power my well pump at my home. We live in the country in SW Missouri that gets a lot of bad weather, and this seems to me to be the best answer to make sure we always have water available if the power goes out. I know true deep cycle batteries are best for solar setups, but since the well pump has such a high starting surge, does it make sense to use commercial grade marine deep cycle batteries that should be able to handle the powerful surges, but still have some attributes of deep cycle?
My system is 24v, 1100 watt sin solar panels and a wind generator going in to a Morningstar MPPT 60 amp controller, and then in to an AIMS 7000 watt 24v-to-240v power inverter. I currently have 4 12v marine deep cycle batteries set up in 2 banks of 24v, each battery is rated at 225ah.
Any thoughts on this would be greatly appreciated!
Comments
-
What are the pump specs and run times? Would be helpful, along with any other intended loads.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Sorry about leaving out that information... it is a 1.5hp 220v pump about 350 feet deep. We mainly try to use it during the day when the system can do most of the work, but at times we need to run the washing machine or take a shower at night, so we are depending on the batteries to keep it going. There are only 4 of us in the house, so it doesn't get a lot of continual use - maybe once every couple of hours.
I notice when the pump kicks on that the battery voltage level will go from around 28.6 to 25.2 while the pump is running, then will charge back up to the 28.6 level within a relatively short period of time.
-
Could you not pump during the latter part of absorption, thereby utilizing otherwise wasted energy to a holding tank and use a small on demand pump for nightime use. The specs for the inverter, if I'm looking at the correct model, claim a 200 MA draw at no load, which seems pretty low for a 7000 W inverter, but a smaller pump would not stress the battery as much when there is little or no input.
The logic behind using marine "deep cycle " makes sense in that it has the capability to provide high surge currents and as long as the depth of discharge is minimal they may work, personally I've no experience with them, perhaps others will have some opinions.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I've taken complete showers on a pressure tank alone.
I am available for custom hardware/firmware development
-
Voltage sag under high load is normal.
That said, it would help to know wire sizes and lengths between batteries, and from battery to inverter. Also, I would check connections with an IR thermometer when the pump is running to see if any are heating up under load.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
7000 watt inverter on 4 small batteries? Yikes!Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year.
-
I know it is overkill, but better than not getting one too small. The AIMS was the only 24v to 240 I could find at the time. As for the cables, I have 12" 2-gauge cables connecting the batteries in serial to make the 24v banks, then 18" 4-gauge cables tying the banks together. I use 24" 2-gauge to connect them to the inverter.
Also, I try to run the pump off of the solar 24-7 as much as I can, and have a switch box to move it back to the grid when necessary.
I appreciate all of the input, and would love to hear about the cables I am using.
-
You have about 1/2 the battery I have, with the same inverter capacity.
I understand the overkill idea. That's why I have the inverter headroom. In my case, it's to handle the unlikely event lots of large loads get going at once (like visitors... one has a shower, another makes toast at the same time, etc.).
Marine batteries are kind of a comprimise between a true deep cycle battery and one designed to supply high current for a short time, and get promptly recharged. They tend toward the latter than the former, and you may find they don't last long in a deep cycle application. When the time comes to replace them, I would rethink overall system design.
You haven't posted pump current specs, but the current at 24v is likely to be significant. Perhaps in the interest of overkill, I use 4/0 between batteries, and to the inverter. I suspect some of the voltage sag is wire loss, and I would replace with heavier, at least for the parallel connection between strings, and to the inverter.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
I appreciate the feedback; I will look into replacing the smaller cables with heavier ones, and I am going to put them on to a bus bar instead of just using the cables. Hopefully I will get a little more performance.
Here is a link to the batteries I am considering buying my next time around: http://www.interstatebatteries.com/p/interstate-batteries/interstate-batteries-srm-4d-srm-4d?dsNav=N~2147384903
I would appreciate any thoughts on these.
Thanks!!!
-
The link isn't working for me, but it could be crappy inet at the cabin on the weekend. A 4d 12v battery probably isn't the right solution, but I don 't know enough about the situation to say.
When the time comes, look at the overall balance of system and decide from there.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Sorry that the link isn't working; here are the specs for this battery. It is an Interstate commercial grade, found on their website under the Deep Cycle section: (again, for is for a well pump which has short bursts of high usage.
Product ID: SRM-4D Cranking Amps: 1645 Cold Cranking Amps: 1314 Voltage: 12 Termination: Common Code M Weight (lbs): 117 Width (in): 8.25 Length (in): 21.00 Height (in): 10.38 ReserveCapacity-25: 390.00 WET/DRY: W
-
All that's needed now are the pump specs.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Well, I am not going to be able to supply the pump specs; we bought this house 11 years ago, and the pump was put in probably about 10 years before that. I can't find any info in the well house - all I know is what the previous owner told me, and that was what I had stated earlier.
-
Looking inside your motor control box should give you a good idea of your pump size. They are sized by horsepower. If necessary google your control box info for specs.
-
Do you have a clamp on ammeter with inrush current capability to measure the demands, nice to know for calculation purposes, understandably not everyone has one.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
seymoursteve said:
I know true deep cycle batteries are best for solar setups, but since the well pump has such a high starting surge, does it make sense to use commercial grade marine deep cycle batteries that should be able to handle the powerful surges, but still have some attributes of deep cycle?
The number of deep cycles for a Marine Battery is less than half of a True Deep Cycle.
True Deep Cycle batteries can handle the brief surge from the pump.
You need a True Deep Cycle battery like the 6 Volt GC2 or 12 Volt GC12.
Quantity and Size (AH) per your needs.
-
Most pumps will be pretty close to this Franklin motor chart.
Beware - Power Factor - my inverter logs about 1,000 w load when my 1/2 hp pump is running. Your inverter must be able to handle this load.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
mike95490 said:Most pumps will be pretty close to this Franklin motor chart.
Beware - Power Factor - my inverter logs about 1,000 w load when my 1/2 hp pump is running. Your inverter must be able to handle this load.
So, per your chart he needs an inverter to support (up to) 15,000 Watts starting & 3,000 Watts running ...
a) 62 Amps starting / 13.1 Amps running @ 240 VAC for 2 wire OR
b) 45.9 Amps starting / 11.6 Amp running @ 240 VAC for 3 wire
A possible surge of 460 - 620 amps on the batteries and cables. -
Also, to the OP, I suspect the term "commercial" may refer more to the size the battery more than anything to do with quality of construction or suitability for your intended use. A 4d size is likely intended for commercial/industrial/farm use, though they're also sometimes used in rv/marine applications.
I wouldn't be quite as quick to dismiss the battery as @mvas though. I do agree with his comment, but would add a couple of caveats.
First, the fact that these batteries specify cranking and cold cranking amps tells me that the battery has relatively thin plates. This allows for a relatively large surface area of plate to be exposed to electrolyte, which in turns allows for the chemical reaction producing current to happen quickly. In your application (assuming the pump is the main/only use), this is useful.
The flip side of this is the battery's thin plates won't likely stand up to shedding from deep cycling, and because the reactions happen quickly, it also has to be recharged relatively quickly. If it regularly sits around deeply discharged, it won't last long.
My deep cycle batteries (admittedly a bigger 48v bank) run pumps fine. They don't have a CCA rating, but do okay. I've also used a much smaller 12v deep cycle bank to start the diesel on a boat.
So if all you're using the batteries for is running the pump during power outages and can get them charged within a few hours, there is some logic to using them. If you're also running smaller loads and will be doing so for more than a few hours, a bank of deep cycle might make more sense.
In the meantime, I'd try the heavier cable. At 24v there's some serious currents involved.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
-
I have, and I agree they're a comprimise that likely ends up not doing either application well.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Have you looked into AGM batteries?
-
Yes, for the boat among other things. AGMs have several advantages for that application including; less likely to vent potentially explosive gas in the confined cabin space, the ability to recharge more quickly with limited engine run time, limited possibility of acid spill in rough or heeled conditions, and lower self-discharge during seasonal layup. In the end I replaced with flooded again though as they have worked okay in the past and were ~1/2 the price of AGMs. Hopefully next time some form of lithium will be affordable and well tested enough.
I did buy an AGM as a starting battery for my diesel generator though. It doesn't get used much, and I'm likely to forget to charge it, so low self-discharge was the deciding factor.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
I thank everyone for their input. I spent time last week changing the cables, as suggested, and have already found an increase in efficiency. I will stick with what I have for now, and when the time comes to get new batteries, I will definitely go with true deep cycle, either golf cart or L16.
-
That sounds like a sound plan, good luck.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed