Will 2X Ulica 260P in parralell melt my Tristar TS-60?
ollyomm
Registered Users Posts: 10 ✭✭
Currently upgrading my mothers sytem, and Ive been told recently that the panels I have are too high in voltage for a TS 60 to handle and that these panels are made only for an MPPT contoller. But looking at the Open Circut Voltage of the panels :37.8 (I will run in parralel) and the TS60 says it can handle 125V. Have not installed panels as controller hasnt arrived yet. Located in New Zealand where we get about 40% grey days and temps between -5C and 30C
Panel Info sheet : http://www.ulicasolar.com/modules2016/5BB Double Glass Poly 250w~260w.pdf
Controller info sheet: http://www.solarelectricsupply.com/fileuploader/download/download/?d=0&file=custom/upload/tristar-charge-controller-review.pdf
Batterys 3 X AGM 12V 150AH
So questions:
1 Will this melt my controller?
2 If so what controller would you reccomend on budget?
3. Is this a good alternative : https://www.amazon.com/EPEVER-Controller-Display-Battery-Charging/dp/B01GMUPGZA/ref=cm_cr_arp_d_product_top?ie=UTF8?
Thanks in advance
Olly
Panel Info sheet : http://www.ulicasolar.com/modules2016/5BB Double Glass Poly 250w~260w.pdf
Controller info sheet: http://www.solarelectricsupply.com/fileuploader/download/download/?d=0&file=custom/upload/tristar-charge-controller-review.pdf
Batterys 3 X AGM 12V 150AH
So questions:
1 Will this melt my controller?
2 If so what controller would you reccomend on budget?
3. Is this a good alternative : https://www.amazon.com/EPEVER-Controller-Display-Battery-Charging/dp/B01GMUPGZA/ref=cm_cr_arp_d_product_top?ie=UTF8?
Thanks in advance
Olly
Comments
-
use the Morning Star string calculator http://string-calculator.morningstarcorp.com/ That will tell you yes or no!
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
I actually was curious, and ran the numbers, in theory I would think it would work, the charge controller can handle higher voltages, it will charge a 48 volt battery bank. They just say the solar panel is incompatible with the system voltage. Even if it worked (and it might) there would be huge losses, as you would charge a 12 volt battery bank (assuming you aren't running a 36 volt bank) and the TS-60would waste all the voltage above the charging voltage, between 13-15 volts normally. They do have a bit of literature here;
http://support.morningstarcorp.com/wp-content/uploads/2014/07/tech-tip-60-cell-PV-module-sizing.pdf
I would ask them directly, if this will work with the panels, and let them know that you understand that there will be tremendous losses. In essence there would be no advantage to your 260 watt delivering 8.5 amps at 30.7 volts to a 150 watt panel delivering 8.5 amps at 17.5 volts. I think it's likely to work but with huge losses. The linked Renolgy is about as minimal a charge controller as you should consider, I thought there were some other options in your corner of the world.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Actually I had the same panels, output voltage / current different manufacturer , with a TS60 but on a 24V system the issue was not too high a voltage but too low, 30.5 volts Vmp. Contacted Morningstar and asked the question if I could series 2 panels for 61 volts, they said no and advised me to use a MPPT controller explaining that the higher voltage would generate heat and damage the unit. Whilst it did work with the 60 cell panels in good sun, the voltage on cloudy days was insufficient, which left me 2 options replace the panels with 72 cell or go with a MPPT controller, went the controller route being cheaper than panels.
In essence you would be in the same predicament, the voltage would be too high, the 60 cell panel would be the same as two 30 cell panels in series, in which case your options would be change to 36 cell 12V nominal or use a MPPT controller. Hope you followed my explanation. Can't comment on the controller on the link other than the price is attractive, paid a little more than double that for a Schneider 60 150.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed