2 Quick Questions

Taken from the M* ts-60 manual " DAY AND NIGHT CONDITIONS ARE DETECTED BY THE TRISTAR AND NO BLOCKING DIODS ARE USED IN THE POWER PATH " , i thought they were necessary to stop the batteries draining ,at night , i know chargers i have had previously mentioned the fact and reading specks on others they mostly mention they are incorporated to stop this . Should i assume that the M* ts60 relies on the user having the diods in each pannel or somewhere in the line between them and the CC .
The other question is how can my batteries charge when the input voltage from the CC is lower than the Batteries as shown in the attached screenshot , this is the situation every day when the sun starts to go down or even days when its overcast .
The other question is how can my batteries charge when the input voltage from the CC is lower than the Batteries as shown in the attached screenshot , this is the situation every day when the sun starts to go down or even days when its overcast .
1840 Watt 24v Array . 4 x 460 Watt Panels
Victron Blue Solar MPPT Charge Controller
4 x 6v 400 Apm/Hr Trojan L16 AGM
Victron 1200w Multiplus Inverter/Charger
Victron Blue Solar MPPT Charge Controller
4 x 6v 400 Apm/Hr Trojan L16 AGM
Victron 1200w Multiplus Inverter/Charger
Comments
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
Agree with lh2 -panel specs would help.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
< 70 mA " , im assuming this means self consumption because ts switched on . I apologise for coming back with so many questions that might be obvious to many but im trying to get a fuller understanding of everything . Will look at the panels and post the info for the previous replies from Littleharbour and Estragon
Victron Blue Solar MPPT Charge Controller
4 x 6v 400 Apm/Hr Trojan L16 AGM
Victron 1200w Multiplus Inverter/Charger
There are 2 identical strings consisting of 2 x 140w x 24v ( 72 cell ) , 4 x 75w x 12v wired in pairs for 24 v (36 cell ) , 2 x 120w x 12v wired in pairs for 24 v ,(36 cell ) all poly same manufacturer and age , both strings run in parallel from the Array then 3 meters before the CC then they go into one larger 6AWG cable . The difference between the arrays is no more then half a volt open circuit approx39 - 40v .
Estragon , I assume you had loads running during the log period shown? Looks like the pv is putting out ~9a at high enough voltage to power loads, but not high enough to do much charging
The previous screenshot is when the panels are cold , late afternoon/early evening , load varies then from 50 to 250 watts ., Battery bank size is 600 amp/hr c20 is 468 amp/hr .
There is no load other then the inverter early morning prior to charging ,( screenshot attached ) but the same condition exists .
Victron Blue Solar MPPT Charge Controller
4 x 6v 400 Apm/Hr Trojan L16 AGM
Victron 1200w Multiplus Inverter/Charger
Think in the end you'll find the controller is doing exactly what it's supposed to do and the strange reading are computer software related issues.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Why are diods not required , i was always lead to understand that without them the batteries would discharge backwards when the voltage coming in was lower then there voltages .
Victron Blue Solar MPPT Charge Controller
4 x 6v 400 Apm/Hr Trojan L16 AGM
Victron 1200w Multiplus Inverter/Charger
I am a little confused at how you get 2 "identical" strings. It looks like you have 3 not identical strings, unless each string has all the panels listed x 2. Either way you are costing yourself potential power. The lower amperage, (looks like the 140 watt), panel will drag down the output of the 150 watt pairs and 240 watt pairs to whatever the 140 watt is putting out.
What, exactly is your method for connecting these panels into strings?
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
The internal circuitry of the CC blocks the battery power from feeding back to the panels, adding additional diodes would only create a volt drop during charging, thereby reducing efficiency.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Always thought diodes were only way to do that and when i read that there were none in the power path it seemed strange for M* not to use them when they use them in the Prostars however you say they are not necessary so thank you that answers my question .
Victron Blue Solar MPPT Charge Controller
4 x 6v 400 Apm/Hr Trojan L16 AGM
Victron 1200w Multiplus Inverter/Charger
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Victron Blue Solar MPPT Charge Controller
4 x 6v 400 Apm/Hr Trojan L16 AGM
Victron 1200w Multiplus Inverter/Charger
The terminology may be wrong here and that is what is throwing me.
A STRING is a group of series wired modules. That being said the lowest amperage module will dictate the overall amp output of said string.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
If this theory is correct, there is nothing wrong with what you see in logs.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
I went back and check those panels are correct for a PWM charge controller, but they are also among the lowest VMP (More important number with PWM CC)some under 17 volts.
I see you mention a diode, do you have one in line now? perhaps all combined to make for low voltage, drop across diode, distance from charge controller to batteries, already lower VMP. Add that to the higher voltage your new Rolls batteries like.
In addition 780 watts (2-140 w= 280, 4- 75w= 300, 2-120w= 240) feeding a 468 amp battery bank should likely give you a max of 32 amps on perfect, cold winter days, and more normally 24 amps on normal days about a 5% charge rate (not sure where you are seeing 30-50?). ...and you say the sun doesn't hit the panels until "midday" are you saying noon?
Looks like you are setup for chronic undercharging.
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Little harbour , your right , i said strings because i used a string calculator on one set of panels and it gave the result as 5 strings but as you point out its actually different sets of panels running in paralel , the only strings are the 12 volt ones wired into pairs .I think i confused things with saying 2 strings when actually i think there are 10 in total all running parallel , 4 single panels and 6 in pairs . Until a few weeks ago i had 2 identical sets of panels each with 8 panels running 5 positives and 5 negatives each set controlled by its own 30 amp controllers in parallel and into a bus bar . I replaced the two controllers with a single M* ts60 PWM so just before the ts60 i joined the 2 cable runs from the array to make for a single connection into the M* ts60 .
Victron Blue Solar MPPT Charge Controller
4 x 6v 400 Apm/Hr Trojan L16 AGM
Victron 1200w Multiplus Inverter/Charger
If so you have; ...820 watts (2-140w= 280, 4- 75w= 300, 2-120w= 240) 280+300+240=820 watts sorry, I ran the numbers in my head real quick, but I did "show my work" ...lol.
Perhaps we there is something we missed.
I find this interesting "...admit i dont often see Float but SG readings after the voltage in drops to less than the battery bank are 1.28 - 1.285 " Something doesn't sound right.
This definitely sounds wrong...lol "...that the sun comes up in the west and.."
I do understand, just having a little fun, I normally see close to max charging a couple hours either side of "solar noon".
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
If so you have; ...820 watts (2-140w= 280, 4- 75w= 300, 2-120w= 240) 280+300+240=820 watts sorry, I ran the numbers in my head real quick, but I did "show my work" ...lol. You and me both haha
I find this interesting "...admit i dont often see Float but SG readings after the voltage in drops to less than the battery bank are 1.28 - 1.285 " Something doesn't sound right. The float thing is no big deal im told due to the way the M* ts60 CC makes the calculations . I take SG readings after the charging has finished at night and before it starts in the morning as i understand the SG is a better indication of SOC than voltage alone .
This definitely sounds wrong...lol "...that the sun comes up in the west and , Good to see your awake and spotted that deliberate mistake , of course as everyone knows it actually comes up in the East . hehe
I normally see close to max charging a couple hours either side of "solar noon . I will only when the circumcisions are right , ie: the sun is shinning and i am still in bulk or not long into Absorption , unfortunately by the ideal time for max current in i have been in Absorption for a while so dont often get to see the higher inputs , if i were to disconnect my array until around 11am then i would see more amps coming in as Bulk would allow it all through but for me its already started tapering down in Absorption by that time . I am considering adjusting my Float cycle limit to 40% . I still have it at its default factory setting of 30% , duty cycle reaches 30% or less for a cumulative hour so raising it to 40% should help .
Victron Blue Solar MPPT Charge Controller
4 x 6v 400 Apm/Hr Trojan L16 AGM
Victron 1200w Multiplus Inverter/Charger
Could it be the controller isn't going into float because loads are taking part of the duty cycles?
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
From everything im picking up on this forum im becoming more confident through knowing and understanding more .
Victron Blue Solar MPPT Charge Controller
4 x 6v 400 Apm/Hr Trojan L16 AGM
Victron 1200w Multiplus Inverter/Charger
Victron Blue Solar MPPT Charge Controller
4 x 6v 400 Apm/Hr Trojan L16 AGM
Victron 1200w Multiplus Inverter/Charger
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Victron Blue Solar MPPT Charge Controller
4 x 6v 400 Apm/Hr Trojan L16 AGM
Victron 1200w Multiplus Inverter/Charger
Or measurements made across shunts that are not all that precise. I.e., a good, high current, shunt may cost $25 to $75 retail... (computer trimmed for accuracy, materials chosen so the resistance does not change over time and temperature, Kelvin contacts to measure the low voltage drop without errors due to resistance and current flow, etc.).
https://www.solar-electric.com/residential/meters-monitoring/shunts.html
There is also a difference in, high current, AC measurements vs DC measurements. AC current measurements can be made with a "current transformer" -- I.e., 100 amps on one side of the transformer can produce 0.10 amps on the other side (1,000:1 turns ratio). A DC current (long term accuracy) is usually done with a precision power resistor (more expensive, more heat loss/less efficient).
In the charge controller, they may just use a copper trace or a 2" wire of some sort (or even the voltage drop across a FET) to get a "useful voltage" that can be compared during MPPT "sweeps" (to find the Vmp/Imp of the panel at that point in time). Long term (repeatable readings over days/weeks/months/time temperature/operating points) accuracy does not matter to the MPPT calculations. Only the A/B comparisons for that second in time.
The manufacturer is not going to put a bunch of high precision components in their meter when it does not make it operate any better (on average).
-Bill
Victron Blue Solar MPPT Charge Controller
4 x 6v 400 Apm/Hr Trojan L16 AGM
Victron 1200w Multiplus Inverter/Charger
Aliasing (i.e., high frequency wave form, low frequency sampling example):
https://www.dataq.com/data-acquisition/general-education-tutorials/what-you-really-need-to-know-about-sample-rate.html
To measure non DC and non 60 Hz AC wave forms (somewhat) accurately, you need a "True RMS" reading meter:
http://en-us.fluke.com/training/training-library/measurements/electricity/what-is-true-rms.html
Is this the "issue" you are seeing--I am not sure--But it could be part of your measurement errors. With a smaller array, the charge controller is in "bulk" (100% on). And with a larger array, the controller is cycling at 50% (or whatever) "on time" or duty cycle--And somebody's meter (yours, the controller), is not "sampling" the average, but reading peak voltage or some variant of it.
-Bill