What would be the best DC TO DC SSR amp rating to keep heating losses the lowest?( or any other method for that reason)
Thanks
Thanks
Boondocking is my game
640 Watts Mono Bogart TM2030 and SC2030 Controller GC 6V 208 AH Costco batteries 300 Watt Inverter and 2000 watt inverter 100AH LIFEPO4 2P4S
640 Watts Mono Bogart TM2030 and SC2030 Controller GC 6V 208 AH Costco batteries 300 Watt Inverter and 2000 watt inverter 100AH LIFEPO4 2P4S
Comments
-
There are Solid State Relays SSR
and there are DC-DC converters. which are you asking about ?
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
If you are talking about SSR's... There are a lot of fake/counterfeit versions out there:
https://www.google.com/search?q=counterfeit+ssr
Some of which are built well (and may even be just wrongly/falsely labeled) with smaller/lower current rated devices inside.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Solid state relays inherently generate heat and the larger the switched current, the more heat generated. Subsequently using a larger capacity rating for a smaller load will generate less heat, as it will not be running near it's limitations, but will still have losses. Using mechanical DC rated relays would be the best way to eliminate these losses at the expense of slower switching times. As suggested, use name brand SSR's such as Omron if you do decide on using them, beaware that fakes exist, best to purchase from a reputable distributor rather than unknown vendors. All too often, people go broke trying to save money, on Ebay and the like.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:Solid state relays inherently generate heat and the larger the switched current, the more heat generated. Subsequently using a larger capacity rating for a smaller load will generate less heat, as it will not be running near it's limitations, but will still have losses. Using mechanical DC rated relays would be the best way to eliminate these losses at the expense of slower switching times. As suggested, use name brand SSR's such as Omron if you do decide on using them, beaware that fakes exist, best to purchase from a reputable distributor rather than unknown vendors. All too often, people go broke trying to save money, on Ebay and the like.
Thanks
Boondocking is my game
640 Watts Mono Bogart TM2030 and SC2030 Controller GC 6V 208 AH Costco batteries 300 Watt Inverter and 2000 watt inverter 100AH LIFEPO4 2P4S -
BothPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
For solid state relays--It is probably mostly the level of current flow and the basic resistance of the device (I^2*R heating losses--current squared * resistance = Watts of heat) that is the heating effect (and possibly needing to mount the SSR on a good heat sink/metal surface).
For high frequency switching, there is gate capacitance that lowers efficiency--But that usually does not apply here (very low frequency switching) where switching is occurring seconds to minutes to hours apart--Vs kHz to MHz of switching frequency. I.e.., there is little to no heat when low current is passed through SSRs, but lots of heat at high current (whether DC or AC current).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Most efficient is a latching relay. With a DC SSR, higher voltages help (ie, less power lost and heat at 48V than 12V for a given wattage).
I am available for custom hardware/firmware development
-
jonr said:Most efficient is a latching relay. With a DC SSR, higher voltages help (ie, less power lost and heat at 48V than 12V for a given wattage).
I considered a latching relay but I worry of burning contacts during the closing event. I am setting up two solar/battery systems that will tie together during high load events (inverter)Boondocking is my game
640 Watts Mono Bogart TM2030 and SC2030 Controller GC 6V 208 AH Costco batteries 300 Watt Inverter and 2000 watt inverter 100AH LIFEPO4 2P4S -
grizzzman said:jonr said:Most efficient is a latching relay. With a DC SSR, higher voltages help (ie, less power lost and heat at 48V than 12V for a given wattage).
I considered a latching relay but I worry of burning contacts during the closing event. I am setting up two solar/battery systems that will tie together during high load events (inverter)
Use a DC rated contactor which is rated for the current, such as these http://www.ametekswitch.com/products/dc-contactors-list
Always use a contactor with 20% or higher rating, than actual current, SSR's have their place, holding high currents for extended periods is not one of them, short durations are fine.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Agreed. Use SSRs for short durations, lower currents (common with higher voltages), fast switching, lots of cycles.
I am available for custom hardware/firmware development
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed