schneider AGS I only have this to say
had to call tech support twice because the manual doesnt give a description of what the relays do during starting and running
if someone can tell me for sure how to hook this up to a durostar DS4400e ......otherwise I am gonna hook it up the way I have it figured......I will give the results later as to whether I have a $200 ornament or not and how I wired it if I am successful
Comments
-
I'll get right to it...what I did works, flawlessly (after I fixed my propane conversion bugs) (and a half case of cherry Dr.Pepper)
heres the wiring pic...wire are not correct color...use the number places...dont use the manuals diagrams...they dont work for this and you will fry your AGS
disregard where it says type 6 in the pic...in the settings use type 8......that was the only pic I saw that used wire 15
heres the setting from the defaults you need to change
in advanced settings
gen type = 8
in advance settings > cfg gen
starter cool down = 3 sec
gen cool down = 15 sec
gen spin down = 3 sec
max runtime = whatever you want
exercise stuff = whatever you want
relay 3 = not used
gen run hold time = 0 sec .....this is important because you are not using a gen run sensing so it will use the ac2 input voltage as sensing
crank delay = 0 sec
crank time = 6 sec .... you can set yours where you need it....test while it is cold and see how many seconds it takes for your gen to start
crank retry time = 3 sec ....I did this in an attempt to capture the propane that was already in the intake side ( not useful after I got my conversion bugs fixed) you can leave it at default or 10 sec
preheat time = 0 sec
gen start retries = 3 ... lets face it...if it doesnt sart after 3 tries on propane....it aint gonna start ( as I found out or it will start and run wrong)
the key switched must remain in the off position......before you use the key switch, make sure the AGS is in standby or maual off
This settings are only for a propane conversion for a durostar DS4400E
the wiring diagram is for the same generator......but it should work with a grounded coil ignition system
thats the reason this was hard to setup....to stop the generator, when the key is turned off, it grounds the coil out...and the AGS manual doesnt tell you enough about functions to let you know this will work
the reason I did this write up is because after searching the internet for a few weeks, nowhere can this info be found and I know others have been wondering or reluctant to to try
I will start another discussion about this linking to this thread
-
by the by...jimmy at schneider is the tops at solar tech support.....he was very patient with me all 4 times I called
-
Glad you got it working.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
I stay away from AGS because i just am really concerned with unattended GEN starts. They can cause really bad things to happen and it is really amazing how failures often give quite a bit of warning if someone is there to notice.
I am sort of glad you figured it out and Tech Support is really good at Schneider, I have never had problems with them."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
yeah dave....I figure if I'm gonna be gone a few days, I'll set it to standby....... if I'm not using as much power, no need to recharge the batteries and propane has a tendency to backfire when the valves get out of adjustment.....which is what I was talking about when I said I got my conversion bugs fixed, buts thats another story for another day....it's a doozy
-
I also just got to thinking, for anyone that needs to leave it on for a remote system, it would be good to invest in a good fire suppression system
-
I also think that many, not all people overthink the need to charge when they are not home for a few weeks. Your XW and the Outbacks will disconnect loads at LBCO. They will restart when the voltage comes back up.
If you are not home, all that should be on is the reefer, some lights and the internet. The daily load goes down quite a bit when the humans are not home..... Good Luck!
Always be nice to Fire People!"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
t00ls said: generator
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
I think you need "Otto" start...seen many years ago in Airplane (the movie) as "Otto" pilot.
Ralph -
Ralph Day said:I think you need "Otto" start...seen many years ago in Airplane (the movie) as "Otto" pilot.
Ralph Right! Also, "picked the wrong day to quit drinking""we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
mike95490 said:t00ls said: generator
you could come up with a starter motor with an offset disk and I'm sure you could use the same setup I did but just use the relays inside of the AGS to operate relays for the starter
how do you like the lister
-
t00ls said: how do you like the lister
http://tinyurl.com/LMR-Lister-Running
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Mike, link doesn't want work even when in FB
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Volvo made a similar saiiboat auxillary diesil engine. It was OK in the tropics but sent many to the emergency room up in the north where it is cold. Be careful or you will be on pain pills!"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
westbranch said:Mike, link doesn't want work even when in FB
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
hmmmmm
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
to date...still working
I still have 1 tiny problem that could be fixed if I knew where the to connect the motor run sensing at....currently the AGS uses AC2 input voltage sensing to see if the motor is running
sometimes the motor will start and the voltage doesnt rise quick enough, and then shuts off right away
and other times it does kinda the same as above, but then realizes the motor is running and comes back on right away
but most of the time,if the valves are adjusted right for propane (uhhg) it will start up and stay running to it hits the presets
now the other problem I have been dealing with doesnt have to do with the AGS....the damned exhaust valve keeps getting out of adjustment...getting tighter, no play in it....cant figure out why it does it
when it happens, the motor will be hard to start and sometimes backfires, which lets me know it's time to go back out ( in the cold) and readjust the valve
the intake side is not doing this...any thoughts on this -
It’s common on air cooled engines for the exhaust valve to tighten up. Anyone that’s ever owned a VW can vouch for that. Make sure there are no burrs on the lock nut surface. I usually leave the valve an extra thousand or two clearance. Hard to burn up a loose valve. Might also check to make sure the airflow on the cylinder isn’t blocked up by anything.
-
mike95490 said:t00ls said: generator
Seems we have a common problem with AGS, 10Hp single cylinder water cooled 598 cc Kubota clone diesel, 5 Kw alternator. Kubota have an electric start at double the price. Massive flywheel on the other side.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
well, that $300 3500 watt generator almost crapped out on me......so I bought a reddy 7000 watt with a honda gx390 13hp motor
with the gen support turned on to 18...I'm charging at 60 amps or less....and.....dun dun dun.......my lights dont flicker when the refrigerator compressor comes on....even when I turn on the water heater.....and the cooking stove....and my small AC unit.....all at the same time
still had to hook up the xantrex AGS the same way as the diagram shows........wires 15 and 16 go between the coil ground wire and the key switch box ( they made this one simple...just unplug the connector and run 15 to one side and 16 to the other , doesnt matter which one)
the 17 and 18 connect to the battery and solenoid ...again, doesnt matter which one goes to the battery or which one goes to the starter solenoid
set the generator type to 7 and configure the settings for your starter crank time and then configure the triggers for when it is to start up
hope this helps someone
by the by......make sure the key is off ...( yeah, I left mine on and couldnt figure out why it wouldnt shut off ).....( took me 10 minutes to figure it out because the key fell out of the switch ) -
I hate it when the keys fall out In some places if you don't have any keys, they lock you up 51/50 !"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
t00ls said:
disregard where it says type 6 in the pic...in the settings use type 8......that was the only pic I saw that used wire 15
heres the setting from the defaults you need to change
in advanced settings
gen type = 8
it should have said type 7...dont know why I put 8
and I cant figure out how to edit the original post
-
Hello
I need suport, I have a new EU70is Honda generator, and I would like to connection on Schneider Conext AGS. I have on the autostart Honda generator connector 5 pin ( remotecontrol connector ),
W/Bu -main switch –
Br/Bu-main switch +
W/G -push switch2
G/Bu – pl remote
G- Gnd .What wiring type of should I use? on manual I can not find the right type.
It should be one relay to make a contact stendby ( function of the key on ON or OFF the generator) and
relay 2 to make contact signal 0,5-1-S for the ignition of the engineI wrote to the schnaider, but the answer was, that the binding scheme ( type 13) is the same as Honda eu 6500is ( link ).
Generator EU70is not the same as EU 6500is
https://www.schneider-electric.ca/en/faqs/FA222135/
Please help if there is any other way wiring
thenks
-
slovenc said:
Hello
I need suport, I have a new EU70is Honda generator, and I would like to connection on Schneider Conext AGS. I have on the autostart Honda generator connector 5 pin ( remotecontrol connector ),
W/Bu -main switch –
Br/Bu-main switch +
W/G -push switch2
G/Bu – pl remote
G- Gnd .What wiring type of should I use? on manual I can not find the right type.
It should be one relay to make a contact stendby ( function of the key on ON or OFF the generator) and
relay 2 to make contact signal 0,5-1-S for the ignition of the engine
_____________________________________________________________________________________________________
I would need more info
what inverter
what Charge controller
if you dont have a trace/xantrex/schneider XW inverter ans XW scp at the minimum.....you cannot use the AGS from schneider
provide the info and I may be able to help
-
When you bought the Schneider gear, you should have gotten a manual which describes the control functions the AGS provides. Not all generator have the normal 3 wire interface
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
@slovenc were you able to get it to work? I just bought a XW Pro Conext with the AGS, and I have a Honda EU7000is generator sitting by. I was thinking of wiring it in, just in case batteries run low and the solar can't keep up.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed