Can non-sinusoidal inverters damage household appliances
oz93666
Registered Users Posts: 2
I recently bought a grid tie inverter without checking if it was pure sine wave.
Today I plugged it in and noticed my toaster was buzzing, then my induction cooker stopped working, latter started again.
Can non -sinusoidal inverters cause problems? If so which appliances are vulnerable? Fridges ?....Thanks
Re: Can non-sinusoidal inverters damage household appliances
Yes, they can and good luck trying to figure out what is and isn't going to survive. -
If i understand that non-sinusoidal means not pure sine wave, and the non-sinusoidal grid tie inverter is supposed to tie to the grid, is the grid ignorant of this fact and allows any proper voltage and pseudo-60 cps inverter device connect, and how does that impact the grid? -
A grid-tie inverter would be pure sine wave.
I don't know what you bought, but it sounds like a cheap piece of junk. Or else it is not a grid-tie inverter but is connected to the grid anyway, resulting in even worse harmonic distortion than an MSW inverter would produce all on its own.
Get rid of it.
This is why all grid-tie installs are done with UL listed equipment plus proper plans, inspections, and approval. Somehow I suspect this is not the case here. Sounds like one of those plug-n-play pieces of junk sold all over the place that can never be legally installed. -
Sounds like something I'd run from, and fast!
I'm wondering how it could override the grid it's tied to, so much that it's causing things to buzz and fail. Something is definitely NOT right here! -
Re: Can non-sinusoidal inverters damage household applianceswaynefromnscanada wrote: »Sounds like something I'd run from, and fast!
It wouldn't be overriding the grid, it would just be filling the waveform full of distortion.
The toaster buzzing sounds very much like out-of-sync waveforms, which would mimic higher frequency and RMS Voltage and result in some interesting vibrations in the heating elements. Toaster probably wouldn't suffer, but an awful lot of electronic gear would not take kindly to such a thing. -
Boy I missed the Grid tie part,
run away quickly as a legit grid tie inverter is going to be pure sine wave as I believe that all it does is follows the utility rather than generating its own. -
Re: Can non-sinusoidal inverters damage household appliancesI recently bought a grid tie inverter without checking if it was pure sine wave......
If it is grid tie, it HAS to be pure sine, or very close to it, to be allowed to backfeed the grid.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Did AnyONE ask if it was connected to the grid when it was being used ? if it was not maybe it was in search mode of ?? who NOOS :-) , but OP didn't leave much on their first post .
VT -
Re: Can non-sinusoidal inverters damage household appliancesDid AnyONE ask if it was connected to the grid when it was being used ? if it was not maybe it was in search mode of ?? who NOOS :-) , but OP didn't leave much on their first post .
VT
Search or standby would not cause the symptoms described. -
The OP also dod not say "bought new". Maybe it is a POS and was bought used because the seller found out it was a POS.Northern NM, 624 watts PV, The Kid CC, GC-2 batteries @ 24 VDC, Outback VFX3524M -
TRUE , Could be the appliance companys have released a new way of planned obsolescence :-)
VT -
Re: Can non-sinusoidal inverters damage household appliancesIf it is grid tie, it HAS to be pure sine, or very close to it, to be allowed to backfeed the grid.
I bought this on ebay, $150 1kw new . The listing says pure sine wave..... http://www.ebay.co.uk/itm/1000W-Micro-Grid-Tie-Inverter-W-MPPT-Stackable-For-Grid-Tie-Solar-System-18V-/151484722952?pt=LH_DefaultDomain_0&hash=item2345316f08
... but in the 14 page manual it says nothing about this.
My knowledge of electronics says you are correct that it should be pure sine wave, but why does my toaster buzz, when inverter is stable and working? this must be a distorted wave surely.
If all grid ties are pure sine wave , then I guess it's OK to buy the cheapest.... as long as it has no fan, critters get in through the fan port and cause problems. -
You may have a tough time sorting out answers as many of posters on this site are based in the US where this type of direct plug in inverter is illegal. These cheap Chinese inverters do have the reputation of premature failure and other issues. When they fail, they could cause a fire so if you insist on using it better make sure its away from anything that may burn. Very soon the initial price savings will be made up by either damaged appliances, replacement inverters or loss the life an property when the house burns down. -
Anyone who expects a $150 1kW grid-tie inverter to work is dreaming.
Get rid of it before something worse happens.
Buy quality, or pay the price twice. -
Re: Can non-sinusoidal inverters damage household appliancesCariboocoot wrote: »Anyone who expects a $150 grid-tie inverter to work is dreaming.
...all those people with micro inverters???Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
Re: Can non-sinusoidal inverters damage household appliances...all those people with micro inverters???
Are $161 and not 1kW.
I shall amend my post to satisfy the annoyingly pedantic.
He bought a piece of junk which doesn't work.
Anyone who disagrees with this we shall consider to be offering to pony up the money to replace and repair any and all damage which may result from the use of same. Otherwise, shut up. -
Re: Can non-sinusoidal inverters damage household appliancesCariboocoot wrote: »Otherwise, shut up.
Sorry, just trying to make light of the comment....
...hope you didn't wake up on the wrong side of the bed!
Agreed, they are very dangerous in general...Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
I had the same question after I bought a 600W cheap (China) inverter on eBay for around $125
I then bought a used Fluke 43B hand held scope to look at the waveform with the inverter tied in
to my house and found no difference than just measuring the utility wave form: a perfect sign wave.
I know most regular (non GTE) type inverters put out a square wave which does not bother most types of loads. Not
sure about motors, though. Pretty sure all GTE put out a good sine wave, otherwise they could not
synchronize with the utility. -
If its a modified sine it will devour DeWalt battery tool chargers.
Most everything else will work, but may buzz.Island cottage solar system with approximately 2300 watts of panels, 1kw facing southeast 1.3kw facing southwest. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 32nd year. -
Re: Can non-sinusoidal inverters damage household appliancesIf its a modified sine it will devour DeWalt battery tool chargers.
I'm sorry, but this is NOT true!!! I checked when I bought my set circa 2001, to build my 'A' frame, the model being introduced then, was fine on Modified Sine wave inverters! I had read that there were problems before when checking on the web and actually contacted DeWalt for confirmation and got it! Perhaps the proof is the Framed 'A' frame and the batteries and charger still working when I built my cabin 4-5 years later. Though at that point I had switched to a pure sine wave.
FWIW many other battery chargers do have a problem with modified sine wave current. You may see 'noise' in the old analog TV's and video displays. It is 'harder' on electronics and motors will run less efficiently.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
To be destroyed - - or not - - by MSW inverters depends to a very small part on the quality of the inverter (some have outputs a bit less square than others), but mostly it depends on the design of the power supply in the device connected to the inverter. Some power supplies are more tolerant of less than a true sine wave supply.
SO - - - how to determine if MSW will cause your device to emit snaps, crackles, pops, stink and smoke, or perhaps just up and die? Simple. Connect it, turn it on and see what happens.
Of course induction motors and transformers always use more power and run hotter on MSW. -
I have 3 'identical' DeWalt chargers and on an old 400w MSW inverter one of them started to smell of the magic smoke. I quickly shut it down and now that charger still appears to work but does not do a full charge of any of the various batteries I tried..They just run out of steam in half the time......YMMV
ps have switched to Makita tools with Li batteries
Re: Can non-sinusoidal inverters damage household applianceswestbranch wrote: »I have 3 'identical' DeWalt chargers and on an old 400w MSW inverter one of them started to smell of the magic smoke. I quickly shut it down and now that charger still appears to work but does not do a full charge of any of the various batteries I tried..They just run out of steam in half the time......YMMV
The DeWalt chargers I have don't have any sort of transformer coils in them. Pick one up and it feels like an empty plastic case; just a capacitor or something inside.
Chargers with a coil inside seem to work fine on my old Trace DR1500.
Makita is one such company.
So my DeWalts stay in the city to charge off the grid and my "island" tools have coils in the chargers.Island cottage solar system with approximately 2300 watts of panels, 1kw facing southeast 1.3kw facing southwest. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 32nd year.
