See anything wrong with this wiring and breaker set-up. Ready to go.
Information: 3 panels in series, 2 in parallel Total 6 panels: 870 watts 16.1 amps wired for 36 volts, 25 foot run, Midnite Classic 150, 4-6volt batteries wired for 12 volts (440 amp hours) 12 volt xantrex inverter.
I'm going with #8 THWN wire in sealtight from distribution box on roof with a 25 amp breaker inside.
Using #8 THWN wire to inverter with 100 amp breaker
#0 gauge wire to batteries and inverter with 250 amp breaker (per xantrez manual)
#6 bare wire on the 2 panel rails to a ground rod and a lighting protector outside the house
Information: 3 panels in series, 2 in parallel Total 6 panels: 870 watts 16.1 amps wired for 36 volts, 25 foot run, Midnite Classic 150, 4-6volt batteries wired for 12 volts (440 amp hours) 12 volt xantrex inverter.
I'm going with #8 THWN wire in sealtight from distribution box on roof with a 25 amp breaker inside.
Using #8 THWN wire to inverter with 100 amp breaker
#0 gauge wire to batteries and inverter with 250 amp breaker (per xantrez manual)
#6 bare wire on the 2 panel rails to a ground rod and a lighting protector outside the house
Comments
-
Re: Last LookUsing #8 THWN wire to inverter with 100 amp breaker
This is to the charge controller?#0 gauge wire to batteries and inverter with 250 amp breaker (per xantrez manual)
This is a short run?#6 bare wire on the 2 panel rails to a ground rod and a lighting protector outside the house
Each panel needs to be grounded, you can use the weeb system with some rails, I think, or a grounding lug on each panel. Off grid is less important unless you will have to be inspected, even those I've seen inspected are typically done incorect and since it's an aluminum to tinned copper, or aluminum to SS to copper, a very high percent fail within a few years (or so I've read)
All grounds to a common point/single grounding rod, or tie the grounding points together...Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Re: Last Lookor aluminum to SS to copper, a very high percent fail within a few years (or so I've read)
I did my grounding this way, thinking it would prevent corrosion at the terminals. So far it appears to be working (5 years since I moved my panels and no signs of trouble), but once a year I've been giving the ground connections a shot of anti corrosion "Rust Check". http://rustcheck.com/index.php?option=com_djcatalog2&view=items&cid=6:aerosols-rp&cid=6:aerosols-rp&Itemid=105 (the red can)
BTW, I also give all my battery terminals and connections a yearly shot of this product and going on 11 years, all are still just like new. Seriously. -
Re: Last Look
I'm not really up yet, but I'll hunt around when I am, or tonight at work. Maybe I shouldn't have said any thing, took a while to find info last time around.
Did a quick search and this has lots of visual failures which aren't the typical problem;
http://www.solarabcs.org/about/publications/reports/module-grounding/pdfs/module-grounding_studyreport.pdfhttp://www.solarabcs.org/about/publications/reports/module-grounding/pdfs/module-grounding_studyreport.pdf
The typical problen is the different metals invite electrolisist(?) or iteraction between them, add that aluminum oxidizes almost instantaniously when exposed to oxygen and expands and contracts at different rates with SS and copper, and thread cutting bolts connections fail, copper to aluminum fail...
I think the WEEB liturature talked about some of the info I had read, I didn't see where they had a much different product, just a SS points creating a connection, much as a thread cutting bolt. figured they were comparing new connections to old when they promoted their product.
SO when doing a connection, the aluminum should be roughed up preferably under grease, and the SS thread cutting bold should be doped with dielectric grease, and you should have a nut with a star washer behind to give the connection the best chance, doesn't change any of the problems with such a connection, just gives the best chance...Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Re: Last LookThis is to the charge controller?...
I should have said controller to battery. Looking at this again for 100 amps more like #4 wire?This is a short run?
Yes. About 5 to 6 feetEach panel needs to be grounded, you can use the weeb system with some rails, I think, or a grounding lug on each panel. Off grid is less important unless you will have to be inspected, even those I've seen inspected are typically done incorect and since it's an aluminum to tinned copper, or aluminum to SS to copper, a very high percent fail within a few years (or so I've read)
All grounds to a common point/single grounding rod, or tie the grounding points together...
O.K So ground each panel. I would think one continuous unspliced wire.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed