Conext ComBox - Firmware update released
Argh, the last few days, my logging has been squirrely and incomplete. I found the uSD card in the combox was corrupted and reformatted it, Reinstalled the same card and rebooted the combox, and tonight, got
Internal Memory Full - Directories: nand:0:\Energy\2015\08.nand:0:\2015\08. Purged.
So a quick google gives me:
Why has my Combox stopped logging system energy graphs?
Energy graphs are stored in the Combox's internal memory. Older firmware would cause the Combox to quit logging once internal
memory was full. Uprading the firmware of the Combox will allow the data to "wrap", allowing the oldest data to drop off, making room for more data.
The latest Combox firmware can be uploaded to a thumb drive from our website.
http://solar.schneider-electric.com/...conext-combox/
I'm running
Application Version Ver02.01BN0673
Application Build Date 2014-09-19_10-40-25
and the latest version is now
Conext Combox Firmware (3.00 Build 707) – NEW
http://cdn.solar.schneider-electric....ld-707-new.zip
So tomorrow I try updating, wish me luck
Release Notes For Conext Combox/Conext Modbus
Converter
Version: 03.00 Build 707 [14 Feb, 2015]
New Features
• CSW Upgrade support on new configurations, warnings and faults.
• Added support for users to perform custom data logging on Modbus device
parameters.
• Added support for AGS auto start/stop based on Battery SOC.
• Added support to emulate USB device connect/disconnect from software.
Bug Fixes
• Updated boot loader to version (Ver01.03BN0118 ) to support watchdog timer
in boot loader mode.
• Added support to update watchdog timer during application initialization
stages.
• Added support to display negative load power for CSW.
• Changed timestamp from GMT to local time in the portal_test script.
• Added support to display normalized Battery bank SOC readings on WebUI
home screen.
• Updated cloud push scripts to use content-length meta data instead of using
chunked transfer encoding which has shown to cause problems on some sites
on web portal.
• Ensures that the associations on CSW are not allowed to be changed during
operation mode.
Note
• The new bootloader (Ver01.03BN0118 ) might be incompatible with
application firmware prior to V03.00. Therefore, it is not recommended to
downgrade the application firmware upon the upgrade of the new bootloader.
Version: 02.01 Build 673 [19 Sep, 2014]
New Features
• Energy odometer (KWh meters) nightly backup to an installed SD card
• Removed unused run-time counters in email report
• Changed GVS and GFS configuration settings to two decimal places
• Added Battery Monitor “Synchronize Now” command
Bug Fixes
• Fixed configuration issues which causes System Configuration Fault on startup
• Fixed overflow bug in energy calculation for battery monitor power flow
• Fixed dashboard corruption when updating from an earlier firmware version
• Removed unused curtailment percentage from system Modbus map
• Fixed AC Transfer switch delay settings
• Fixed GVS and GFS configuration settings
• Fixed schedule timing error when using data push to cloud service
////// update
all seems to have gone well,
WAS
Bootloader Version Ver01.01BN0058
Bootloader Build Date 2013-05-01_17-34-02
after upgrade:
Application Version Ver03.00BN0707
Application Build Date 2015-02-14_02-44-31
Bootloader Version Ver01.03BN0118
Bootloader Build Date 2014-12-16_12-18-33
Sadly, while the error message is gone now, the logging still seems inoperable, Maybe it will "cure" itself after a 24 hour cycle (unlikely) Looks like I'm calling schneiderPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Interesting I can;t sync my battery monitor with the new firmware, says the value can;t be changed...or in this case enabled.XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array
apparently this is fatal, and they asked for proof of purchase to ship me a new one.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
II
Under tech pubs for the ComBox on the Schneider site reset logs script!!GT3.8 w/4600W Trina 230W, TX5000 w/5000W ET-250W, XW4024 w/1500W ET-250W, 4 L16, 5500W Gen. (never had to use) Yet!! -
I've tried the script, and hope it works, the results file says the right things happened. Just waiting a day now to see if it's working.
Thanks for the tip SkiDoo55Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
OldI've tried the script, and hope it works, the results file says the right things happened. Just waiting a day now to see if it's working.
Thanks for the tip SkiDoo55GT3.8 w/4600W Trina 230W, TX5000 w/5000W ET-250W, XW4024 w/1500W ET-250W, 4 L16, 5500W Gen. (never had to use) Yet!! -
yes, the reset script worked, I am happy again. But there is a replacement in the mail, and I was sent a return postage label, so I'll test them both for a bit, before sending one back.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
I hope you can help. I am about to buy a Conex Combox but the part number I require, 865-1058, seems to be very hard to get. There are a other part numbers for the combox eg 809-0918 that is more readily available. Is it a firmware difference and is the firmware interchangeable?
I wish I could help you but I just don;t know, Schneider told me they were different on the phone.
XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array -
A new ComBox firmware release on the Schnieder site. Haven't flashed mine yet, been busy.
They also have a new script tool to clear the internal memory with instructions for users that are getting a internal memory full error. Maybe the new firmware might take care of that. Hope they put the ability in to log energy etc to external card?GT3.8 w/4600W Trina 230W, TX5000 w/5000W ET-250W, XW4024 w/1500W ET-250W, 4 L16, 5500W Gen. (never had to use) Yet!! -
Tinbum said:I hope you can help. I am about to buy a Conex Combox but the part number I require, 865-1058, seems to be very hard to get. There are a other part numbers for the combox eg 809-0918 that is more readily available. Is it a firmware difference and is the firmware interchangeable?"we go where power lines don't" Sierra Nevada mountain area
If its just a firmware change buy the cheaper box and flash it, what is the issue with doing that?
Go ahead and try it.! It is a different model number for a reason."we go where power lines don't" Sierra Nevada mountain area
So the schneider tech was correct, the xw needs the correct part number to work.
Good that you looked into it. Not good to tell people to do the wrong thing even on the internet."we go where power lines don't" Sierra Nevada mountain area
Thanks for the replies. I did buy one of these but had to have it shipped to a friend in New York who was then sending it to me in the UK with an MPPT 80 600. I'd asked him to put it within the MPPT box but in his wisdom he didn't and despite me having only ordered on parcel for collection the courier took the two saying it was ok. It was never seen again and because I had only ordered one collection the courier wont pay out as one was delivered- good old DHL. I can't seem to find them in the UK and no one want to send one from USA and if the do they want a ridicules amount to do it.
Keep looking in the UK. I have client their and I will ask him also. We drop shipped from Sacramento into London so I know it can be done."we go where power lines don't" Sierra Nevada mountain area
There is another version of the combos firmware uploaded at the Schneider site. There also appear to be a couple updates posted for the CSW, AGS, BattMon that I haven't seen before, although the dates indicate they are not totally new.
Combox is up to 3.03 BN 830 at: ComBox Firmware VER 3.03 BN 830
Rob -
Some good things here maybe for folks using AGS."we go where power lines don't" Sierra Nevada mountain area
thanks. I see nothing there that benefits me, so I'll pass on this round, But the recovering for bricked gear looks nice.
SkiDoo55 said:II
http://solar.schneider-electric.com/product/conext-combox/
Downloads
TechPublications
You want- Conext Combox Application Note Reset Logs (976-0682-01-01_Rev-A-Scripts)
- Conext Combox Application Note Reset Logs (976-0682-01-01_Rev-A)_ENG
- Conext ComBox Application Note Copy Settings (976-2105-01-01_Rev-A)_ENG
- ComBox-App-Note-Copy-Settings(976-2105-01-01_Rev-A)-scripts
After you backup your data, the firmware update may fix all the issues,
And get a microSD card for the box. That's how I do the backups
Pay attention to EVERY Word in the doc for the scripts, The wording and sequence is not consumer friendly,
these are technical documents.
I don't know any way to capture / save the existing data unless you do each one manually (painful)
Hello I know this is an old post but I need your help, just bought conext combox and the default firmware is
Device Info: Conext ComBox - Freedom SW by Xantrex
Model Number: 809-0918
Serial Number: B12946247
Hardware Revision: Rev-HDevice Name: ComBox-B12946247
MAC Address: 00-00-54-FE-0D-8C
IP Address: 192.168.1.12
Hostname: cb-B12946247
Software ID: 150-0288
Kernel Version: 1.33
Application Version: Ver01.00BN0044
Application Build Date: 2014-02-27_16-18-42
Boot Loader Version: Ver01.02BN0087
Boot Loader Build Date: 2013-08-23_09-40-38
Modbus Map Version: A.2
with this firmware I can see two MPPT60 perfect but I can´t see the 2 inverters and AGS, can anyone have the Application Version: Ver01.00BN0044 or other version before 3.0 or someone can tell me if its possible backup the firmware from combox??, thanks a lot.
Combox for Freedom SW is not the same as Combox for XW and CSW. I do not believe there is a way to get this to work correctly.
Combox for XW & CSW is model 865-1058 and is for renewable energy inverters. Your is for Marine Inverters.
You must have me confused with someone else"we go where power lines don't" Sierra Nevada mountain area
Dave Angelini said:You must have me confused with someone else
What is GFS Enable in the ComBox
hybrid: xw6848 pro with two mppt60, 6 kw pv
17 cell 280ah LiFePO4 storage 14 kw
gridtie: sunny boy sma 2x 5k
gridtie: fronius ag5100 5k
Gateway / Insight Local
xw4548 backup -
Thats under Active Power Control for the XW device
xw4548 backup -
Also connot find documentation for Generator Support Plus under Advanced Features in the ComBox
xw4548 backup -
Would love it I anyone could post a link to any manual that has these items in it. Thanks.
xw4548 backup
- 653 Solar Water Pumping
- 628 Discussion Forums/Café
