Hello nice people. I'm just getting started with solar and don't think I have installed the C40 correctly. The digital display indicates 0 watts. The volts average around 13. The panel is a KC120 and I am using two 6volt golf cart batteries. What should the display read for watts? Thanks.
Re: C40 questions
The c40 should have + from the pv separate from the + from the battery. The - are joined internally. Make sure you don't have the pv + in the battery + and the battery + in the pv +. -
Re: C40 questions
Does the display show anything at all, or is it completely blank? -
Re: C40 questions
Its got a bunch of 0's for everything except the volts. I checked to make sure all the wires are going to the right place and they are.
I remember last week when the sun was out, the amp and amp hours were registering but have never seen anything other than 0's for the other things. -
Re: C40 questions
So the next question is; what have you got for panels, and are they putting out Voltage? There could be a blown fuse/breaker and/or mis-wiring there. If you have a Voc that is above the battery Voltage you should be getting charging (providing the C40 is set up right). -
Re: C40 questions
with the sun shining the amps display will tell you how many amps are coming in to the c40. watts = amps X volts. example 5 amps coming in at 12 volts equals 60 watts. zero amps = zero watts. the volts you are seeing are the volts of the batteries. use a volt meter and make sure the solar panel is producing.
check all connections. hope this helps. -
Re: C40 questions
Keep in mind you need a load to see power displayed, if your batteries are fully charged, you would only have the voltages values displayed. Run the batterys down a bit and then see what you get for displayed values -
Re: C40 questions
I've got one Kyocera 120 watt panel hooked up. Last week when the sun was out it reached float stage. The green light stayed on until the sun went down. I checked all the connections. They look good to me. Thanks everyone. -
Re: C40 questions
Are you saying it used to work (green light last week), but never displayed anything but Zero Amps?
Or, you have found the problem and everything is working now?
Or, it appears to be charging but not displaying Amps?
It is possible you have a bad device. Xantrex is usually pretty good about sending a replacement unit if you think it is bad (from what I have read).
Re: C40 questions
Yes, it was charging last week but I did not see anything other than volts on the display. Correction, the amps and amp hours registered as well. The watts has always been 0. -
Re: C40 questions
Hmm... I wonder if there is a software setup issue? You are logging Amps/Amp*Hours correctly. Watts is just Amps*Volts... (I don't know anything about setting up a Cxx controller).
Re: C40 questions
Here the manual
http://www.xantrex.com/web/id/978/docserve.aspx
I seem to recall the meters minimum display is 1 amp, so 12-13 watts would be the minimum displayed. Put a good load on the battery and have the PV connected and see what you get for reading. If the battery is near fully charged you probably won;t get watts or amps displayed as the charging rate would be so low -
Re: C40 questions
Everything is showing on the display now. 14 watts and 29 watts, depending on the Sun. But, the last time I looked, the watts were 0 again. Is that normal? -
Re: C40 questionsEverything is showing on the display now. 14 watts and 29 watts, depending on the Sun. But, the last time I looked, the watts were 0 again. Is that normal?
It's normal, if the batteries are full and don't need a charge.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Re: C40 questions
Yes, the C40 when in absorb or float is basically an on/off controller. If you want to see numbers, put a good load on the battery -
Re: C40 questions
Hi from the UK
I have a C60 connected to 4x 130w Kyocera panels on a Tracker
it is designed mainly as a charge controller.
on the digital display it shows
amps the amount of amps that is being dumped
watts the amount of watts its dumping
volts the battery's are showing
underneath is the amp hours produced at this moment
and total amp hours produced so far to date since turning on.
remember that it is a battery charge controller and it only displays watts and amps that are dumped to the dump load to stop the battery's from over charging.
when the green led is lit that means the battery's are fully charged and ready to use the power from an inverter
Check out youtube.com and search for my site for an explanation look for Windysolar1 or type it into goggle. -
Re: C40 questions
But solar does not need a dump load ! I guess it's nice to see you have enough power left over to dump though. Maybe have it light up a green light, to tell you it's good to run the dishwasher, washer, dryer, vacuum cleaner, bread machine while power is aplenty.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Re: C40 questions
it says in the manual that you have to run a dump load
Water or Air with solar or wind.
otherwise you will fry your battery's
why does it have 60 amp connection posts ?
when the voltage rises to the bulk 14.6v setting when the sun shines and a lot of hours have passed.
The controller gradually reduces the voltage to the float voltage on 12v its around 13.6v.
but the battery's still have high amps and high volts pressure coming from the sun.
So where does it go
Into the DUMP LOAD
SO YOU DON'T FRY YOUR BATTERY'S
Any more questions please while I am installing Windows Xp on another Pc
Ps I dont have a house or a dishwasher but I also have a 1000w 24v Wind turbine. -
Re: C40 questions
Wind or hydro need a dump load, to keep the turbine speed down.
The C-series controllers are PWM controllers( a series FET) , and in the solar mode, they just disconnect the panels from the batteries. No excess heat. no dump load.
PV Panels don't care if they have anything connected to them or not.
If you have solar and wind and hydro all running to the battery, and have controller rigged as a voltage shunt, maybe that's why you think you need a load, but that would be a very un-usual configuration.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Re: C40 questions
yes you are correct for solar
I have to run Diversion Control mode because I use two sources of power input
I was wrong been busy lately
completely forgot about that.