Testing actual power of Panels
cswaite
Solar Expert Posts: 46 ✭
Ok. Quick question. If my charge controller shows for example 5.5 AMPS coming in on the display of the controller, but when I put my multimeter leads to the positive and negative screw going into the controller it shows 6.5 AMPS, would the correct Amps, be the reading from the meter rather than the controller (which I think is probably not so accurate). I bought one of the Juta controllers, I know they arent the best controllers, was just wondering what others think my correct AMPS would be in this situation.
Thank You
Thank You
Re: Testing actual power of PanelsOk. Quick question. If my charge controller shows for example 5.5 AMPS coming in on the display of the controller, but when I put my multimeter leads to the positive and negative screw going into the controller it shows 6.5 AMPS, would the correct Amps, be the reading from the meter rather than the controller (which I think is probably not so accurate). I bought one of the Juta controllers, I know they arent the best controllers, was just wondering what others think my correct AMPS would be in this situation.
Thank You
I would place more trust in the multimeter testing the wiring from the panels directly than I would in the display of the controller.
Are the screws tight on the wiring going into the controller? (Just checking.) -
Yes, the screws are tight. I might buy a higher quality charge controller.
Do you think even if the controller is displaying approx. 1 amp below what the meter says I am still getting that 1 amp to the batteries? -
Re: Testing actual power of PanelsYes, the screws are tight. I might buy a higher quality charge controller.
I doubt it. More likely the controller display is showing what is going into the batteries, while the missing 1a is what the controller is consuming. -
Re: Testing actual power of PanelsOk. when I put my multimeter leads to the positive and negative screw going into the controller
This is the incorrect way to test amps. That is the way to test for voltage.
To test for amps/current, you need to remove one wire from the panel going to the controller. Then take one wire from meter and attach it to that wire from panel. Now take the other wire from the meter and attach it to the controller lug you just removed the wire from.
This is called a series connection, this is how you measure amps. -
Re: Testing actual power of PanelsThis is the incorrect way to test amps. That is the way to test for voltage.
Ok, ill give it a try. Thank you. -
I suggest that you read the manual for your multi-meter as many can only handle some number of milliamps, not full current 6.5 amps!
A good way to toast a meter if you do it incorrectly.
Icarus
PS. that is what shunts are for! -
Re: Testing actual power of PanelsI suggest that you read the manual for your multi-meter as many can only handle some number of milliamps, not full current 6.5 amps!
Icarus
My meter has a 10AMP DC setting. -
Re: Testing actual power of PanelsMy meter has a 10AMP DC setting.
You may also have to move one of the meter leads, to a jack on the meter
labeled 10APowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
- 234 Forum & Website