Dead batteries mean no power?
stockoneder
Registered Users Posts: 7 ✭
I have a question regarding how a grid-tied hybrid system with a battery bank would work if the batteries were basically dead.
Would the system still provide power to connected loads if the batteries
were so dead they barely held a charge during the day, while the solar panels were making electricity?
Would the system still provide power to connected loads if the batteries
were so dead they barely held a charge during the day, while the solar panels were making electricity?
Comments
-
Re: Dead batteries mean no power?
Solar Guppy would have to give you the exact answer...
But my guess is that there still is a 120 Hz current ripple in the battery bank as the inverter "inverts".
As the battery fails, it will supply less of the peak current and absorb less of the peak charge current--basically turning into a giant, poorly operating, capacitor.
I would guess that the Vmax/Vmin of the ripple will become worse and worse as the battery fails--and that both the charge controller (may mess up MPPT function) and the inverter (Vmin may cause inverter to stop GT feed) will have problems with the large voltage swings. Plus the battery may begin to overheat as its internal resistance rises.
You may also have other failing battery issues... Shorted or open cells--which will have their own secondary effects (open output, overheating cell(s), excessive hydrogen outgassing etc.).
Lastly, a dying battery bank may have losses of 2% per day (and probably worse as the battery approaches dead)--so you are throwing away more or more energy into battery losses (and the GT Inverter may end up trying to "charge" the battery at night to keep it alive enough for the solar charge controller to work--charge controllers typically won't start charging if the battery voltage is too low).
And I would guess that you may have to keep adding water as the battery just starts doing electrolysis instead of actual charging.
Why the question?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Dead batteries mean no power?
A grid tied battery hybrid inverter is just like a power plant generator tied in parallel with the grid. The inverter is syncronized (frequency, phase, and voltage) to the grid before the relay is engaged to tie it in parallel with the grid.
Most all these inverters use the battery supply to run the electronics that generate the waveforms and syncronization necessary to connect to the grid. So without battery capable of at least running the electronics within the inverter they won't even power up.
Once the inverter is syncronized to the grid and tied in parallel with it, it can push to grid (sell from battery or PV pushing at battery) or push to battery (charging) with just slight adjustments to inverter output voltage relative to grid voltage. Inverter a little higher voltage pushes to grid, a little lower voltage and it sucks from grid and pushes to batteries.
A grid tie battery-less inverter electronics are powered from grid to do the initial syncronization. It acts more like a current source then a voltage source of a battery equipped inverter. Because the PV panels are a variable current source they are unreliable as a reference voltage like a battery. Without the resevoir tank of a battery, the battery-less grid tie inverter must shut down if grid A.C. supply is lost. -
Re: Dead batteries mean no power?
wouldn't battery based GT shut off the inverter till the batteries come up to some sort of charge before re-enableing the inverter? Just a WAG.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Dead batteries mean no power?
Inverter is the charger. These battery based, grid tied inverters are bi-directional design. The switching FET's allow the power to flow in or out of the inverter that is syncronized to the AC line. -
Re: Dead batteries mean no power?
Ihave a question regarding how a grid-tied hybrid system with a battery bank would work if the batteries were basically dead.
Would the system still provide power to connected loads if the batteries
were so dead they barely held a charge during the day, while the solar panels were making electricity? -
Re: Dead batteries mean no power?
How did the batteries get dead?
The inverter should keep them charged as long as there is grid power or sufficient solar. It should only draw off them when the grid is down and there's not enough sunlight to counter load demands. Unfortunately the low voltage shut-down is usually too late to prevent severe depletion, but even so good batteries should charge back up once power is restored. -
Re: Dead batteries mean no power?How did the batteries get dead?
-
Re: Dead batteries mean no power?
"Yes the inverter will continue to push power into the grid as long as the charge controller can maintain the battery bank above the sell voltage."
don't forget that the controllers themselves need battery voltage to operate and if it goes too low it will not allow the controller to function and prevent the power from the pvs from being passed on to these doa batteries. the only hope of functionality in that case is if the built-in charger keeps the voltage on the batteries high enough to allow controller functionality. the batteries that failed will boil water (even if agm as the vent will be wide open) like there's no tommorrow and the good ones will soon fail from feeding their power into the bad battery(s).
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed