Voltage drop vs wire gauge
CBHunter
Solar Expert Posts: 39 ✭
Guys, is there a way to figure out what will be the voltage drop for 100 ft of 14 awg wire? What difference a 10 awg would do?
Of course I can put a voltmeter to measure it, but is it predictible?
Re: Voltage drop vs wire gaugeOf course I can put a voltmeter to measure it, but is it predictible?
Very predictable & repeatable.
link:
http://www.uwgb.edu/nevermab/voltage_drop_calculator_.xls
Assuming 10A @ (for your 100ft (one-way) wire (@70F))
14 ga 2.54V or 2.54%
10 ga 1.00V 1.00%Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Wire Dia. Cir Ohm/1000' Vdrop
Size Mils Inch^2 @20C I max. @ 100'
00 364.8 0.1045 0.080 350.0 2.8
0 324.9 0.0829 0.100 250.0 2.5
1 289.3 0.0657 0.125 180.0 2.3
2 257.6 0.0521 0.160 150.0 2.4
3 229.4 0.0413 0.200 130.0 2.6
4 204.3 0.0328 0.250 100.0 2.5
6 162.0 0.0206 0.400 63.0 2.5
8 128.5 0.0130 0.655 63.0 4.1
10 101.9 0.0082 1.000 30.0 3.0
12 80.81 0.0051 1.600 20.0 3.2
14 64.08 0.0032 2.500 15.0 3.8
Take resistance per 1000 feet, divide actual wire length by relation to 1000' (100' = 1/10 of 1000')
Vdrop = I actual x times resistance of length of wire.
For #14 with 15amps -> (2.5ohms for 1000') x (100'/1000') x 15 amps = 3.75v drop
- 231 Forum & Website
