Jackery Explorer 5000
nschizzano
Registered Users Posts: 48 ✭✭
Anyone with a jackery explorer 5000 here? If so did you construct your own PV array? And what did you do? Seems series with about 400w panels is most suitable. What voltage did you end your string at? Thanks
Comments
-
Nope not me but I have set a few up. As for panels you need panels with enough MPPV to charge the max battery voltage plus some extra V for clouds/loss. You could use, for example, A string of (3) 200W panels that have a MPPV of 23 V wired in series. You could use (2) of the 400 watt panels that have a MPPV of 31V in series. Good Luck !"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
I have 11 400w axitech panels on series. Each one has has 31 vmp and 39voc and I live in minnesota where it gets negative 30. Although for winter in could take one or two out of the series string easily.
Should i add up vmp or voc?
Jackery takes a max of 450v from the panels -
Both... Voc added up for cold weather, and maximum array voltage--That can damage/ruin your solar charge controller (or other solar controller types connected to the array).
Vmp is added up to ensure that the array matches the solar array input voltage for the solar --Both Cold and Hot. Too low or too high of Vmp voltage and the solar controller may not work efficiently.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Okay good to know thanks
So I am sitting at 418v VOC with this series string of 11 panels. About 39voc each.
I have to call it good there because one more will bring it to about 458voc. The cold in minneosta likely goes past VOC I think is what I read. So 418voc panel array may be dangerous although jackery has informed me the jackery system has a multi layered shut off if voltage passes 450. How true I do not know.
-
The coldest recorded temp in Brainerd MN is -54F. (1996) That may have been in town, so I would plan for -60F if the site is out of town in the country.1000W panels Kid CC 184 ah battery bank @ 48vWeekend cabin, 250w inverter.
Looking to upgrade inverter!
Categories
- All Categories
- 233 Forum & Website
- 140 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 181 Solar Information links & sources, event announcements
- 893 Solar Product Reviews & Opinions
- 252 Solar Skeptics, Hype, & Scams Corner
- 22.5K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.6K Off Grid Solar & Battery Systems
- 428 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 656 Solar Water Pumping
- 816 Wind Power Generation
- 620 Energy Use & Conservation
- 623 Discussion Forums/Café
- 316 In the Weeds--Member's Choice
- 74 Construction
- 125 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed