Hey all
I've been using my 200ah 24v battery and 3000watt inverter for about 6 months now in my off grid cabin. The warmer months were perfect. Even with all cabin running including ductless ac from 8am until 10pm the soc will be 80% at the end of the day. So I headed into winter thinking I'm good.
The last couple of times we came to the cabin this winter when night temp drops to 5-10 degrees.. the battery temp, per it's Bluetooth app, was 33f and soc was at 93% upon arrival we then used two 800 watt space heaters to just warm up until woodstove took over.. It dropped to 50% within less than 2 hours. It continued the rapid drop until I had to turn on generator..
Obviously temp is what causing this? I'm thinking to maybe try to try put that 800watt space heater right on battery (safely obviously) to try and warm it up quickly..
Any ideas/tips?
  • Wheelman55
    Wheelman55 Registered Users Posts: 251 ✭✭✭
    Give the team here specs on your system. Battery voltage and size will be especially helpful.
    Off-Grid in Terlingua, TX
    5,000 watt array - 14 CS 370 watt modules. HZLA horizontal tracker. Schneider: XW6048NA+, Mini PDP, MPPT 80-600, SCP. 390ah LiFeP04 battery bank - 3 Discover AES 42-48-6650 48 volt 130ah LiFePO4 batteries
  • Marc Kurth
    Marc Kurth Solar Expert Posts: 1,187 ✭✭✭✭
    edited December 2024 #3
    The first thing that comes to mind is that your 1,600 watts of space heater load plus some inverter overhead, represents close to 17 % or 18% of your battery capacity, per hour that you operate both.
    In very round numbers: 200 ah battery x 50v = 10kWh. Two hours of heater operation is around 3.5kWh including some inverter overhead, which is 35% of your battery capacity.
    So, with your battery bank in brand new condition, starting at 93%, it would be at 58% running the heaters for two hours.
    Dave Angelini Solar Expert Posts: 6,995 ✭✭✭✭✭✭
    A very hard thing to do reliably !  Redesign the system is about all there is.
    Winter is where the pedal hits the metal !  The days are getting longer😉
  • littleharbor2
    littleharbor2 Solar Expert Posts: 2,126 ✭✭✭✭✭
    Now, factor in that it's a 24 volt battery.
  • JRHill
    JRHill Registered Users Posts: 429 ✭✭✭✭
    One of the things that is not allowed in our off grid setup is resistance heat from a hair blow dryer and up. There has to be a better way to get the cabin warmed up without a major system redo? How about one or two of these (on their own grill bottle?) and a ceiling fan or two?
    https://www.lowes.com/pd/ProCom-25000-BTU-Wall-or-Floor-Indoor-Liquid-Propane-Vent-Free-Infrared-Heater/5015729915?store=
    When done for the season you can just store them away until next season. The ceiling fans, if you don't have them already, are useful all year around.
    Off Grid. Two systems: 1) 2925w panels, OB VFXR3648, FM80, FNDC, Victron BMV-712, Mate3s, 240 xformer, four SimpliPHI 3.8; 2) 780w, Morningstar 30a, Grundfos switch, controller and AC/DC pump, 8 T105. Honda EU7000is w/AGS. Champion 3100. HF 4550, Miller Bobcat.
  • 706jim
    706jim Solar Expert Posts: 523 ✭✭✭✭
    Heaters vs batteries = no
    Particularly cold batteries!
  • JRHill
    edited December 2024 #8
    A block heater for 15-30 minutes is an exception. Getting a machine started may be important than getting another layer of clothes on.
  • nyoffgrid
    Yeah. I will be getting a pellet stove instead haha.
  • JRHill
    Will that be faster than a ventless propane? Still again you go to electric appliances in an off grid situation. That pellet thingy has a darn heating coil, screw and mandatory fan. I don't get it. But you can just go back to town....
    BB. Super Moderators, Administrators Posts: 33,689 admin
    edited December 2024 #11
    At 0C/32F, a lead acid battery will lose about 20% of its capacity... And at 93% state of charge (SoC numbers are always a wild card), you would be looking at:
    1.0 SoC (at 25C) * 0.93 SoC (measured) * 0.80 SoC (at 0C) = 0.744 estimated "usable" capacity
    200 AH * 24 volts * 0.774 "actual" capacity/state of charge of your bank = 3,720 WH of usable capacity
    1,600 WH * 2 hour = 3,200 WH of heater usage...
    You would have left 520 WH of capacity after 2 hours of heating... Not a lot left.
    3,000 Watt inverter on a 24 volt and 200 AH Lead Acid battery bank is expecting a lot... Typically on a 200 AH @ 24 volt bank would have been a maximum load of 1,500 Watt suggested.
    Guessing this is some sort of Lead Acid battery bank? Not Lithium Ion?
    PS, forget to add Lead Acid battery bank capacity vs Temperature link:
    https://support.rollsbattery.com/en/support/solutions/articles/5860-temperature-vs-capacity-flooded-lead-acid-batteries
  • Marc Kurth
    Whoops! My mistake.