Wire in Series then all wired together in Parallel
 
            
                
                    ccrisham                
                
                    Registered Users Posts: 2 ✭                
            
                        
            
                    I have a victron mppt 100/20 controller I was wondering about doing a series and parallel connection with my 200w 24v pannels
If I do just 2 in series it will be about
75V
5.4A
So was wondering could I just add a 2nd string and get
75V
11A
I dont see why it would not work but I cant find any info on anyone saying not to do it only thing people say is dont go over the max V
Thank you
                        
        
        
      If I do just 2 in series it will be about
75V
5.4A
So was wondering could I just add a 2nd string and get
75V
11A
I dont see why it would not work but I cant find any info on anyone saying not to do it only thing people say is dont go over the max V
Thank you
            Tagged:
            
        
            Comments
- 
            Wiring 4 panels:
 2 in series
 2 in series
 and then paralleling those 2 groups of panels to get 75V, 11A
 would be just fine for most charge controllers. You have to verify your panels Voc when cold, would
 not exceed the max voltage input for you controller.
 Remember, 75V max power, closer to 95V open circuit on a cool morning. Many charge controllers
 have a sizing tool on their website, to verify you wont exceed the limits
 shorthand: 2S2P for your panel arrangement
 75V, 11A = 825 watts. 12V = 69A output from controller. 24V = 34A output
 Following screen shot shows MPPT controller converting high voltage ( 79.2v) from solar,
 to lower voltage & higher amps to the battery 
 Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
 || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
 || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
 solar: http://tinyurl.com/LMR-Solar
 gen: http://tinyurl.com/LMR-Lister ,
- 
            
 Victron Charge controllers are rated at max input voltage and output amperage. So output is limited to 20 amps, if you have a string of 2 - 200 watt 24 volt nominal panels, you would have an input of 400 watts, but at 12 volt charging around 15 volts, you would have a possiblity of 400 ÷ 15 = 26.66 amps.ccrisham said:I have a victron mppt 100/20 controller I was wondering about doing a series and parallel connection with my 200w 24v pannels
 So an important question is what is your system/ battery bank voltage?Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
 - Assorted other systems, pieces and to many panels in the closet to not do more projects.
- 
            Yes, it would work, but the "typical" best case charging current (a few times a year on cool/clear days around solar noon):- 800 Watt array * 0.77 panel+controller deratings * 1/14.5 volts charging = 42.5 Amps
- 800 Watt array * 0.77 panel+controller deratings * 1/29.0 volts charging = 21.2 Amps
 
 On a 24 volt battery bank--Pretty much maxing out the 20 Amp charge controller (which is just fine--You are losing only a very small amount of total harvest).
 The present controller will work fine--But adding a second array on cool/clear days around noon--You are losing quite a bit of harvest potential. A second 20 amp controller or >~40 Amp MPPT controller would be a better fit long term.
 And as Mike says/asks... How cold of weather are you planning on... If you are in seriously cold weather (well below freezing), your array could easily exceed 100 VDC Voc-array (voltage open circuit) limit of your present charge controller.
 Need the exact Vmp/Imp/Voc/Isc of your panels and what is the minimum temperature your array is expected to experience?
 -Bill
 Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
- 
            Yes battery V is 24 system and I am in central FL so temps dont get too cold.
 I was figuring it would work fine with a 24v system 2 sets of 2 x 200W panels
 I currently only have 2 of the 200W panels but planning to get more and glad I dont need to get a 2nd controller for that set.
 Thank you for your help- Maximum Power(Pmax): 200W
- Maximum Power Voltage(Vmp): 37.6V
- Maximum Power Current(Imp): 5.32A
- Open Circuit Voltage(Voc): 45.4V
- Short Circuit Current(Isc): 5.83A
- Maximum System Voltage(Vmax): 1000V DC
 
Categories
- All Categories
- 232 Forum & Website
- 140 Solar Forum News and Announcements
- 1.4K Solar News, Reviews, & Product Announcements
- 199 Solar Information links & sources, event announcements
- 899 Solar Product Reviews & Opinions
- 256 Solar Skeptics, Hype, & Scams Corner
- 22.5K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.6K Off Grid Solar & Battery Systems
- 428 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 655 Solar Water Pumping
- 816 Wind Power Generation
- 624 Energy Use & Conservation
- 620 Discussion Forums/Café
- 313 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed