Morningstar ts45 issue
Fredthecat
Registered Users Posts: 5 ✭✭
Everything was working fine before. Had the coach running on shore power for a couple weeks when I unplugged I noticed the solar wasn't charging.
If I disconnect the solar wires and take a reading from them directly with a multimeter they are at 18 volts.
When I connect the wires to the ts 45 and check volts at terminals it's only .8 volts. After a few minutes I check it again and it's reading the same voltage as the batteries. 13.3.
If I kill the power and turn it back on its at .8 again.
The remote meter shows no ah no volts.
Welcome to the forum
What is the status of the 3 LED's on the controller, they will indicate a fault or alarm if they are sequencing in any order, in a no fault condition they do not sequence but remain on in various configurations to indicate voltage status.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Solid green unless batteries run down then it's solid green and yellow. Never had any flashing lights.
No faults on the remote meter.
It's just not letting the solar power in. -
On the remote meter what is the status, night, bulk PWM or float. What are the dip switch settings, what battery type are you using and did you install the system?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Yes I installed it, it was working for the last 6 months. After having it plugged in for 2 weeks it decided to not work anymore.
4 battleborn lithiums,,dips 2 off 4 on 2 off per battleborn. Remote just says mppt 0 ah 0 volts. -
Are you using custom settings with MSVIEW, if so what are the settings, what it sounds like is the batteries are at a near fully charged state so not accepting current, try dischargeing to see if the charging resumes or apply a large load, the TS45 should wake up to support it.
The rational behind the being near fully charged statement is they were left for a couple of weeks without discharge I would assume, perhaps they never reached that state before, all speculation based on the lack of details.
MSVIEW has a virtually infinite possibilities so it important to get them correct, that is the reason behind the caution message when entering the setup wizard. Should you still have problems after self diagnosis contact Morningstar support, they are extremely helpful and respond fast to enquiries.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
I discharged down to 11.9 ,still won't charge, calling today.
They are sending me a new controller
Good to hear. I have Morningstar MPPT controller, remove view, and EMC-1. They can be a little tricky for laymen like me - I'm trying to get the EMC working correctly now - but Morningstar support is excellent. They get back to you very quickly.
How did this work out?
- 232 Forum & Website