Erratic voltage from battery pack to charge controller
sultan
Registered Users Posts: 4 ✭
Hello I'm working on a electric conversion of an old John Deere Gator, which is powered with three 300 watt solar panels a Chinese charge controller 60 amp
Going to 16 -3.7 volt lithium ion batteries 185 amp hours, giving me pack voltage of around 50 volts
The DC motor which drives the machine was working fine until 2 days ago, no I'm losing voltage and cannot operate the machine,
When I check with my multimeter at the battery pack shows 51 volts
But the minute I turned on the DC inverter or the solar power to charge it suddenly the voltage is dropping to around 12 volts
When I look at the charge controller screen it's trying to detect the voltage and jumping a radically from 30 volts up to 60 volts and since my charge controller will not charge beyond 55 volts I'm not able to charge it
Any ideas what the problem might be?
Going to 16 -3.7 volt lithium ion batteries 185 amp hours, giving me pack voltage of around 50 volts
The DC motor which drives the machine was working fine until 2 days ago, no I'm losing voltage and cannot operate the machine,
When I check with my multimeter at the battery pack shows 51 volts
But the minute I turned on the DC inverter or the solar power to charge it suddenly the voltage is dropping to around 12 volts
When I look at the charge controller screen it's trying to detect the voltage and jumping a radically from 30 volts up to 60 volts and since my charge controller will not charge beyond 55 volts I'm not able to charge it
Any ideas what the problem might be?
Comments
-
For the voltage to drop that much in such a short time, I'd suspect the wiring. Bad connection or a break or somewhere in the wire itself.Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year.
-
Can you tell us a bit more about your battery pack? Type of cells/voltage range.
Does it have a BMS (battery management system)? If yes, can you give a link to it or discribe it (does it shutdown the bank if over/under voltage, etc.)?
A good place to start is use a voltmeter to measure the drop across each cell under load/under charge (or group or cells) if you have access... With a series connection and dramatic voltage drop, you should be able to isolate it pretty quickly to a cell/disconnect/bad wiring/bad connection.
Use a "simple load" (filament lamps are good for this)... A DC motor, especially if it there is "momentum" such as fan/large rotating mass... If the DC power is "interrupted", then the DC motor can become a generator (and it can even "reverse" the +/- DC terminal voltage).
The changing battery bus voltage can cause issues with a solar charge controller... Many will turn off below 9 volts, and will reboot >9 volts, and measure the bus voltage--Then decide if the bus voltage is 12/24/48 volts. If your controller reboots and "sees" 12 volts--Then it may default to a 12 volt battery bus.
Always connect Vbatt to the controller first, and disconnect last. If you have solar power and Vbatt is disconnected, the controller can reboot "confused" or even default to the wrong bus voltage--And potentially be damaged.
The fact that your system worked for a while... It sounds like the battery bank is "near dead" charge wise. With solar systems, it is pretty common for the system to work well for days or weeks+ at a time, then fail because of under charging (not enough sun for daily loads) or over discharging (more loads than the solar can keep up with).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
sultan said:since my charge controller will not charge beyond 55 volts....Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
thanks for the input
currently i dont have a bms, i plan on putting one on,
when i check the voltage across the individual cells "without a load" they average 3.3 to 3.8v, i havent been able to put a load (dc motor) as the power has been intermittent
but i plan on putting it on a jack and checking each individual cell, i agree that it appears that it is undercharged
the charge controller is the powmr
https://www.amazon.com/PowMr-Controller-Backlight-Battery【Software-Version】/dp/B0719PGGBS
currently i have my solar charge controller directly connected to Positive lead of battery , but the negative lead is connected to the B- of the dc controller rather than directly to the battery
my only other thought was if the dc controller capacitor is somehow sending a voltage to the charge controller tellign it not to charge, or giving it an erratic voltage?
as an update, today it started running again, and showed 57v, but im not sure how accurate that number is under load
scratching my head!
-
@sultan
Reading between the lines, being 3.7V nominal it would appear the cells may be LiPo, if so the low cell voltage of 3.3V is nearing the point of permanent damage, any less than 3.2V they become toasted. Furthermore they seem out of balance, were they ballanced before use or just connected in series?
LiPo cells are amongst the most dangerous chemistries, operating haphazardly without a BMS is a recipe for disaster. Should they in fact be LiPo the voltage required to fully charge would be ~67.2V for 16S, most likely rendering the controller linked unstable for the task.
You really need to submit details because simply saying lithium ion batteries is not enough, the specific chemistry is important, for others to provide any useful feedback.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
thank you
to be honest, im not sure what the exact chemistry is, but i do know they were used for solar batteries, im using them for a vehicle off label
i do have a picture of them, from what i do know they are 3.7v 185AH i beleive they are lifepo4
i have attached picture -
i will def add a bms
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed