My Batteries are not charging, please help

Hello, I have a 120v battery bank along with 10 solar panels (I don’t know the ratings), a 3KVA inverter and a 60A 48v MPPT charge controller.
The batteries charge fine with normal electricity but do not charge with the solar panel. I’ve checked all the connections and everything seems fine. What else could be the problem???Thanks.
Tagged:
Comments
post more details please, models, Mfg's
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
The batteries are all VRLA 12v 150AH batteries, The charge controller is a Yohako 60A 12/24/36/48v charge controller.
Also, I read that more charge controllers may have to be cascaded to charge the batteries... how many of these charge controllers would I need??
Yes, you can put a 60 volt charger on the "low numbered batteries" and 60 volt charger on the "high number" batteries in series... But not always that simple...
First need to find a 60 VDC rated charger (in reality, need a charger that can output 75 volts or so)... Second, when you have chargers in series like that--Need to make sure that all wiring is protected by fuses, and the "high charger" output leads are rated for 60-150 VDC. Third, if you have any "digital or signal connections from charge controllers (alarms, status, etc.)--The offset in DC voltage can be a big issue too (i.e., your "ground reference is now (possible) 60 VDC for the "high string" charger.
You need to be very careful with these high voltage/high current strings of batteries... The can be very dangerous (both from an electrocution and a fire point of view).
There are (typically) UPS systems that are designed to work with 120 to even 340 VDC battery buses--But that is more often used in commercial/industrial installations.
If your system is a 48 VDC battery bus (typical for home/small commercial systems), then we have to back up and get more information (typically 4x 12 volt batteries in series * X battery strings in parallel). And know more about your loads (WH per day) and charging needs (solar, genset, utilty power, etc.).
-Bill
You will need to know the ratings of the panels to figure out the wiring for your charge controller...
We will need to know the parameters of the charge controller as well, so we can determine the proper wiring of your array.