Newbie - just need to power refrigerator during power outage
BB. said:Just be aware--More or less the rule of thumb is around 500 Watts per every 100 AH for a FLA @ 24 volt battery bank:
- 7,680 WH / 24 volt = 320 AH battery bus (@ 24 volts)
- 320 AH * 500 Watt inverter * 1/100 AH = 1,600 Watts max suggested AC inverter for 320 AH battery bank
-Bill -
so, you can use a larger inverter to power a small load, but as long as you operate within the range of the battery capacity and wiring that is existing, you are ok.
But really, what's the point here? You have grid power! Why the expense of batteries and their life cycle replacements ? You won't save money, grid power is usually 1/4 the cost of off-grid. If you are looking for a expensive "UPS" to run your fridge, OK.
How often do you have grid failure? If not often a fridge can stay cold for several hours if you keep the doors closed.Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year.
mike95490 said:so, you can use a larger inverter to power a small load, but as long as you operate within the range of the battery capacity and wiring that is existing, you are ok.
A Honda eu2200i costs around $1,050.Ran 2x full size refrigerators (around 20 cuft) and one 17 cuft freezer. Plus a 2000 gallon koi pond pump and air pump and a few lights.All on about 2-2.5 gallons or less of fuel per day.Used an extended run time fuel cap and tank.
Stored two Honda eu2000i (earlier version) for 6-12+ years (drained fuel and carburetor, a small shot of oil in the spark plug hole)--And they started up after a couple of pulls (get the fuel pumped into the carburetor).Got a pair of backup eu3000is (my home, and my in-law's) for more money (electric+manual start, 3.4 gallon internal gas tank).
https://www.homedepot.com/p/Honda-3000-Watt-Gasoline-Powered-Electric-Start-Portable-Generator-with-Eco-Throttle-and-Oil-Alert-EU3000iS/206192156
Got a small (good quality) float charger and wired that to the starting battery (hopefully keep the battery "happy" for a few years in storage).
And they are quiet.-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB. said:A Honda eu2200i costs around $1,050.Ran 2x full size refrigerators (around 20 cuft) and one 17 cuft freezer. Plus a 2000 gallon koi pond pump and air pump and a few lights.All on about 2-2.5 gallons or less of fuel per day.Used an extended run time fuel cap and tank.
And they are quiet.-Bill -
A member (2manytoyz--not too active lately) has a nice set of pictures and talks about DIY solar (and his evolution from small to larger/old home to new home):
http://2manytoyz.com/ (about 1/2 way down the page)
Bus bars are just a place to connect multiple wires to a common connection (battery bus, etc.). In larger installations, the bus bars also can carry the "bulk current/power" through the interior of the electrical panel from point a to b to c.
Bus bars are usually heavy enough that there should be little voltage drop from one end to the other--Very nice when (for example) connecting parallel battery strings together into one large bank.
Here is a nice example of why bus bars:
http://www.2manytoyz.com/hardware/alt/setup_1482.jpg
Bus bars are generally copper or brass. There are aluminum bus bars--But they are not really recommended unless you know what you are doing (the surface aluminum oxidizes in seconds when exposed to air).
Thanks everyone for all your help. My build is all done. Everything works. I couldn’t have done it without the help of this forum. Special thanks to Bill. Now I’m ready for power outages. 1.2kw solar array, 7.68kw battery bank, 2kw psw 48v inverter.I have a friend of a friend (journeyman electrician) who is going to see if I can wire the inverter to the breaker box with a lockout switch.Any tips for me on what to do / what not to do?-Right now, the inverter neutral is bonded to the chassis. I presume that is not what I want if it’s connected to the house. I’ll need to run the neutral and ground to the bus bars in the breaker box, right?Basically, I need to know if I should leave the neutral bonded in the inverter after connecting to the home.
The problem with hooking the inverter to a distribution panel is there needs to be isolation between the two at all times either manual or automatic break before make transfer switch to avoid possibly killing a line worker or grid feeding into the inverter.
The best method would be to have a small load center powering essential loads fed from the main distribution into a transfer switch with grid as prime source inverter as backup, always remember lawsuits are generally more costly than inverters, don't lose either. Play safe.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
mcgivor said:The problem with hooking the inverter to a distribution panel is there needs to be isolation between the two at all times either manual or automatic break before make transfer switch to avoid possibly killing a line worker or grid feeding into the inverter.
- 886 Solar Product Reviews & Opinions
- 651 Solar Water Pumping
- 608 Discussion Forums/Café