Charge Controllers and Max Array Watts
RickR
Registered Users Posts: 2 ✭
I am looking to add a 3rd array to my system. I have 10 Trina 250 watt panels available. I currently use 2 FM60s on my other arrays and have a Mate3 for monitoring/programming. The specs for the FM80 I am looking at, say max array is 2000 watts and max amps are 80.The panels are rated at 8.85amps short circuit current which would exceed the 80amps. I planned to have 5 strings of 2 panels each to come in at 44.25amps. But the array wattage would still exceed the 2000 specified. Would I be safe in going foward?
Under most conditions the 2500W array will only generate ~1900W, the only time it would approach or exceed the rated output is if in extreme cold. The best way to determine the compatibility is to use Outback's string sizing tool1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
The OB FM60 & FM80 CCs also have a maximum total PV Isc Limit of 48 and 64 Amps respectively. These limits are generally fairly difficult to to exceed, without running all PVs in parallel ("strings" of one PV), or really excessive over-PVing the CC.
FWIW, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum.
- 234 Forum & Website
