Voltage mismatch
electrictrauma
Registered Users Posts: 10 ✭✭
I have an inverter that will only charge up to 60 volts. My battery config is 8s so max voltage is around 68. What is a work around to get the most out of my batteries?
Tagged:
Comments
-
make and model of your charger ?
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Its an outback skybox
-
What type of batteries (sounds like 6 volt * 8 batteries = 48 volts nominal).
For most Lead Acid chemistries, 62-64 volts is fairly aggressive charging (or equalization charge).
I am guessing you are in central California(?) and have warm summers and mild winters (unless your system is in the mountains).
For our friends in the great white north, running a battery bank well below freezing can require >62-64 VDC for nominal charging voltages:- -0.005 volts per cell per C (26C - -16C) * 24 cells = +5.04 volt charging voltage offset for a -16C (3F) 24 cell (48 volt FLA) battery
- 59 volt charging (equivalent to 14.75 volts @ 12 volt) + 5.04 volts 64.04 volts Absorb Setpoint charging
If the Skybox inverter-charger module is limited to 60 VDC... That is very sad. We have tripped over the 60VDC limit in cold weather (and with some industrial batteries needing 62-64 volts for corrective charging at room temperature) many times here... I would have hoped a new system design from a major manufacturer would have done better.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
No they came from an industrial install, each rack has two sets of 8 lithium ion in series, so 68 volts and 68 amp per rack. I’m in the bay area too. I admit I was shocked, just assumed it would be versatile since it was new. I can try to get them to mod the software but not holding my breath. Barring that there must be a clever way to do it. Anyone?
-
I had a thought about running it 48 volt with 4 in series and then putting a fifth in series an connect the five batteries to the lithiums and charge the lithiums with a voltage regulator converter from ac, not sure the current would transfer fast enough.
-
7 modules in series? Gives you 59.5 VDC (and a reduction in bank capacity by 1/8th).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Might work Bill, haven't really gotten into the racks other than to see there are two wired in series. Would be a pain to take them apart and they have 8s bms but its a thought.
-
What type of Li-Ion battery has 7.5v cell voltage? 14s or 16s would be more reasonable. There are likely several hardware reasons the inverter cannot go over 60vdc.
There is an additive to Li-Co that takes their max charge to 4.4 v/cell. For 16s that would take max charge to 70.4v and 14s to 61.4v.
More common are 4.2v and 4.3v / cell max charge. LFP are 3.65v/cell. They don't have to go that high unless you are trying to get the fastest recharge time.
You should find out exactly what type you are dealing with. I personally would not have high AH's of LiCo batteries in my house.
-
They are racks of two 8s connected in series. Took one out and seems to be working fine at the 60v max of the inverter.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed