So I have
6 x 100 watt panels https://www.amazon.co.uk/gp/product/B07YKQZ2N3/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1
I have a 40A controller https://www.amazon.co.uk/gp/product/B07FRM17DM/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1
so the limits on the Amps would be reached on the solar panels if put in parallel and but the voltage would be reached on the controller if put in series. my question
4 of them in series is fine which would work fine. is there any way of putting 2 of them in parallel aswell but have a blocking diode or somthing
so that the current doesnt go though the panels.
so the same question would be how would I put them all in parallel and not reach the amp limit on the panels.
I would like to say thanks in advance for all replys and help
6 x 100 watt panels https://www.amazon.co.uk/gp/product/B07YKQZ2N3/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1
I have a 40A controller https://www.amazon.co.uk/gp/product/B07FRM17DM/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1
so the limits on the Amps would be reached on the solar panels if put in parallel and but the voltage would be reached on the controller if put in series. my question
4 of them in series is fine which would work fine. is there any way of putting 2 of them in parallel aswell but have a blocking diode or somthing
so that the current doesnt go though the panels.
so the same question would be how would I put them all in parallel and not reach the amp limit on the panels.
I would like to say thanks in advance for all replys and help
Comments
-
2 groups of 3 in series, then parallel the 2 groups ? (Just 66Voc)
also noted as 3S2P
Is this for a 12V or a 24V battery ?
600w @ 14V gives you 42A, which, such a slight overload, the controller should not be seriously affected
@ 24V is only 21A, well within the controller specs
From their data sheet:
Overheating power reduction function
780W max input 12V
3S2P should be fine
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
thanks Mike, it is a 12v battery Trojan 1275
yes I was a little confused about this 780w max but its a 40a max which even 600w is over the limit.
the problem with the 3 in 2 groups which is a great idea this would be difficult due to how my setup is
I have 4 that are together and 2 that will be somewhere else and only put in the circuit when needed.
Yes I know its a strange setup.
thanks again Mike you have been very helpful so far
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 652 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed