Do you think my SureSine inverter will handle this fridge?
jmiller968
Registered Users Posts: 11 ✭✭
I'm putting a fridge in my cabin. It is a 13.9 cubic foot frigidaire ffht1425vw. Energy star placard states 332 kwh. I did a bit more digging and found: Voltage Rating – 120V/60 Hz/15 Amps
• Max Connected Load (kW Rating) @ 120 Volts = .36kW
• Max Amps @ 120 Volts = 3.0 Amps.
So the sure sine is a 300 watt inverter that can surge to 600 for 15 minutes. Assuming minimal other loads (an LED light or two), do you think that this inverter is enough? If not, what inverter would you recommend?
So the sure sine is a 300 watt inverter that can surge to 600 for 15 minutes. Assuming minimal other loads (an LED light or two), do you think that this inverter is enough? If not, what inverter would you recommend?
Comments
-
Somebody on this board was running a fridge off of a 300 watt Samlex inverter. You would have to search to find the post. Normally, users go with a larger inverter than 300 watts to provide for the starting surge of the compressor. Inverter style fridges have less of a starting surge from what I've read here.Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year.
-
It looks like this is a frost free/self defrosting refrigerators... The heating element may take a fair amount of power to run (larger refrigerators can take 500-600 Watts for the defrost heater). Perhaps this smaller one takes less.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Might work - might not. The compressor surge is unknown. Back in the 90's the biggest units had such large surges that a 1500 watt inverter fell short. Though I suspect the fellows electrician may have "monkeyed stuff up" due to not knowing solar particulars.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
BTW surge is not needed for 15 minutes. More like 5 seconds for my fridge. And can I say once again just how much I love my old transformer couple MSW inverter? Been running great since 1994!Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year.
-
jmiller - those are favorable offgrid energy usage stats. Have useful price and source information? Thanks.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Thanks for the input guys. I bought the fridge at Home Depot on sale last week for 480.
-
I really like the suresine inverter. If the fridge pulls too many watts to work on it, is it possible to stack this inverter? Could I buy another one and parallel them to double the wattage?
-
Good question - looking forward to answers for that one.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
As far as I know, unless the inverter explicitly supports stacking/paralleling, it does not.
At the bottom of the page, are the specifications... But from what I can see, NO it does not support parallel/stacking outputs:
https://www.solar-electric.com/morningstar-si-300-115v-ul-inverter.html
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
And for completeness, it is possible to run some refrigerators and converted chest freezers from a MS-300 Watt AC inverter, our retired poster Wayne has some posts on how to do that:
https://forum.solar-electric.com/discussion/14862/my-latest-freezer-converted-to-fridge-showing-very-good-results/p1
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
My converted upright ~18 ft commercial freezer needs comparatively very little energy to stay at ~45F. About .3kW/day. I have considered making a thread about how important the thickness of the insulation is. Fridges have 1". Freezers have 2".
Keep in mind it is in the garage at ~60F which certainly helps. The controller also allows an ~3F temp range so cycling is reduced. When cooling it uses about 150 watts - which varies some.I would consider betting the freezer part of our fridges use most of the energy. Defrost heating cycle being much of that reason. My Samsung produces no frost on the food but it certainly likes to stay on for prolonged periods between 4am and 7am. At a rated 550kWh/year - it is no energy miser for an 18 ft model. Made in 2008 btw. Nice unit though - I like the outside digital readouts and ability to "fast freeze" and "fast chill".First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
jmiller968 said:I really like the suresine inverter. If the fridge pulls too many watts to work on it, is it possible to stack this inverter? Could I buy another one and parallel them to double the wattage?
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Or try looking for an inverter fridge .2225 wattts pv . Outback 2kw fxr pure sine inverter . fm80 charge controller . Mate 3. victron battery monitor . 24 volts in 2 volt Shoto lead carbon extreme batterys. off grid holiday home
-
Leaving an update for future fridge searchers out there. I got the fridge installed, with a kill-a-watt to monitor usage. As soon as I plugged it in, the inverter failed. Unfortunate, but I had another 2000w pure sinewave just in case. Swapped inverters and tried again...success! The watts jumped to 750 on startup, which explains why the suresine didn’t work. I continued to check power usage. First day was 1600w, but that was of course starting from scratch with a warm fridge and freezer. The next day was in the 900w range. We then left for a week and just returned tonight. We used a total of 4800w over 7.5 days, which comes out to 640w per day. Very impressive #s, and much better than I was expecting. Of course the door stayed closed the entire time, but it was very warm last week, and most importantly, the beer was cold when I got here. All for a measly 26w per hour!
-
Yep... Generally suggest a 1,200 to 1,500 Watt AC inverter minimum for "typical" Energy Star Fridge.
Also... Just to be clear. Watts is a Rate--Like Miles per Hour. And Watt*Hours is an amount (like total miles driven).
So, your 1,600 Watts the first day was actually 1,600 Watt*Hours in first day (total amount of energy used).
And dropped to an average of 640 Watt*Hours per day--Which is not bad at all for a standard fridge.
The 26 Watt "average load" is usually something like a 100 Watt load, running ~1/4 the time, for an average of 26 Watt*Hours of energy per hour (i.e., 100 Watts for ~15 minutes out of 1 hour).
A typical residential fridge runs around 100-120 Watts average load, and >~600 Watts (really VA, but another time) starting (less than 1 or 2 seconds).
Also, if frost free--You could be running a 500-600 Watt defrost heater every 12 to 24 hours or so (just long enough to melt the ice on the inverter "evaporator" (the "cooling coils").
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
My lg inverter 450 l fridge uses .3 kw per day while not in residence . The inverter uses more energy than the fridge .2225 wattts pv . Outback 2kw fxr pure sine inverter . fm80 charge controller . Mate 3. victron battery monitor . 24 volts in 2 volt Shoto lead carbon extreme batterys. off grid holiday home
-
petertearai said:My lg inverter 450 l fridge uses .3 kw per day while not in residence . The inverter uses more energy than the fridge .
That unit keeps getting brought up - mostly by you I think? Yet they seem to have quit making it as I recall?
One way to get really low energy figures is to buy a fridge only unit. It is the defrost on the freezer that seems to use an unseemly amount of energy.
It is interesting to see Costco only stocking monster size fridge/freezers and fewer and fewer very serious bargains. They seem to be losing their way - perhaps like Sears did so many years ago?
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
I have looked it up and it looks to be discontinued. I will have to stop talking about it.2225 wattts pv . Outback 2kw fxr pure sine inverter . fm80 charge controller . Mate 3. victron battery monitor . 24 volts in 2 volt Shoto lead carbon extreme batterys. off grid holiday home
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed