jamie2020
jamie2020 Registered Users Posts: 1
Hi, am from the remote Baelelea region of Malaita island in Solomon Islands.  Am acquiring a pico hydro 3kW system (correcting for overall efficiency useful power at 2.4kW) to run a community primary school, rural clinic and about 60 households in 4 small rural villages, estimates at 600-700kWh/day consumption. 

I need your help regarding building a battery bank especially to maintain clinic and frozen goods, assumption, two days of autonomy during maintenance of power stations and or necessary shutdowns during thunderstorms. Need to build a battery bank. What capacity should the battery bank be? How many 12V batteries would I need? 

Many thanks, 
Jamie

Comments

  • 706jim
    706jim Solar Expert Posts: 515 ✭✭✭✭
    Options
    First question: How many freezers and how many refrigerators?

    Second question: Rated power consumption for both of these.
    Island cottage solar system with 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter, Outback Flexmax 80 MPPT charge controller 8 Trojan L16's. Insignia 11.5 cubic foot electric fridge. My 30th year.
  • petertearai
    petertearai Solar Expert Posts: 471 ✭✭✭✭
    Options
    3kw  for 60 houses and a school? Did i read that correctly ?
    2225 wattts pv . Outback 2kw  fxr pure sine inverter . fm80 charge controller . Mate 3. victron battery monitor . 24 volts  in 2 volt Shoto lead carbon extreme batterys. off grid  holiday home 
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Options
    If your daily load is 600kwh, and your charger is 2.4kw, you need 250 hours in a day to supply that load ???
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||