Too Much power?
Belize1
Registered Users Posts: 19 ✭✭
I have two controllers side by side in an off grid residential application in Central America. Each controller handles eight PV panels split into two groups of four. Each panel is 250 watts with a max output of 8.3 amps ( in ideal conditions, as we all understand. The heat of Belize is not ideal for PV output)
With four panels in series they produce 130 volts output. But, what is their combined amp output? In series operating at 130 volts are the four panels producing 32 amps? Or 8 amps? Are the two sets of four (total eight) operating at 130 volts producing a combined output of 16 amps, or 64 amps?
Second question. The total array feeding two Classic 150 controllers is 16 panels for a total of 4kw watts.. Two groups of four on each controller.
Each 150 could be feeding as much as 2000 watts into the system. 2000 watts at a charge voltage of 27 volts would be 74 amps times two chargers for a total of 148 amps to the batteries???
The Batteries are in series at 24 volts. Eight batteries total ( 6 volt) for a total of 460 AH capacity. US Battery recommends charging at ~10% of C20. That would be a max of 43 amps to the batteries. The PV array is clearly capable of charging the batteries at 3 times the recommended rate.
a) Can the two Classic 150 controllers be set to limit their output to some predetermined max to avoid charging the batteries too fast?
b) What is reality on charge rates, i.e. what is happening to the batteries if they recharge at 20% of C20 (86 amps)?
Residential Backup System Midnite Solar MN5048 Inverter/Charger 16) 235AH Crown CR235 8) Hanwha Qcell Peak Duo 350watt
Comments
-
On the panels... When you put them in series, the voltage (Vmp/Voc) adds. When you put the panels in parallel, the current adds (Imp/Ioc/etc.).
You have 250 Watt panels with Imp=8.3 amps:- Vmp = Pmp/Imp = 250 Watts / 8.3 amps = 30.1 Volts Vmp-std conditions (sounds right)
- 4x 30.1 = 120.4 volts Vmp-std conditions (hot panels, hot climates, Vmp-hot falls).
- 1x string is Vmp~120.4 volts @ 8.3 Amps
- 2x parallel strings, Vmp~120.4 volts @ 16.6 Amps
- Rated array 120.4 volts * 16.6 Amps = 1,999 Watts Pmp (2,000 Watts, roundoff error) for 4s x 2p array
- 4 x 6 volts @ 230 Amps = 24 volt @ 230 Amp*Hour battery bank
- 2x parallel strings = 24 volts @ 460 AH battery bank
- 2,000 Watts * 77% panel+controller deratings = 1,540 Watts per "typical" solar array output available for battery/DC bus power
- 1,540 Watts / 56.0 Volts "nominal" battery bank voltage = 27.5 Amps from each controller
- 27.5 amps * 2 controllers/arrays = 55 Amps typical "best case" current from array
Also, solar charge controllers make their charging decisions (charging voltage) based on battery state of charge, temperature, other loads on the DC bus, charging state (bulk, absorb, float), if the panels are all pointing the same direction, if the chargers are "synced" (some charge controllers can be setup to all be in the same bulk/absorb/etc. modes, others will make their own decisions and not switch charge states in sync--Which is fine too.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Belize1 said:...............a) Can the two Classic 150 controllers be set to limit their output to some predetermined max to avoid charging the batteries too fast?b) What is reality on charge rates, i.e. what is happening to the batteries if they recharge at 20% of C20 (86 amps)?a) Yes, you can use the graphic panel or the Local App to set max amps outputb) the batteries heat faster at higher charge rates. This ages them faster.In reality, the batteries self-regulate their current at any specific voltage. When the sun comes up and the batteries are really low, the solar charge rate slowly ramps up because the sun is at a poor angle (usually). By 10am, the batteries are partly charged and won't accept as much amps as they would have earlier in the day. The problem is a foggy or cloudy morning, and then at noon the sun clears and slams lots of amps into low batteries. If it happened every single day, that would be bad for the batteries, if it happens 2x a month, that's not very bad.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Being at the same latitude as Belize the output of the panels will be less than rated due to high ambient temperatures @BB.is correct in his estimate the best I've observed from 6 × 250W panels is around 30A on a cool day, relitivly speaking which is 30°C.
The thing of most important factor, particularly with lead acid batteries is temperature, the life expectancy is dramatically reduced as the temperature is above 25°C, figure on 3 years give or take if 35°C is the normal ambient. Once the water consumption increases significantly it's a sign they are on the way out. Temperature compensation will help to some degree but it is a a reality that temperature is the enemy you are faced with.
How is Belize these days, spent some time there in the late 1990's doing small scale hydro mechanical systems for the Amish community with their woodworking shops. Miss the roadside Jerk chicken, spent most of my tine between Bellomopan and Placencia at a friends farm near Over The Top, it was a great time then but the locals were beggining to complain about the immigrants from Honduras taking the jobs they weren't willing to do in the first place.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Thank you to everyone for the answers. You confirmed I was doing my math correctly. Lots of extra information in these posts is quite helpful.
Mcgivor, Belize is still wonderful. My house is at the very northern tip of the Placencia peninsula. The people continue to be unhurried and able to enjoy life. I don't get to stay in Belize all the time but love the time I get.Residential Backup System Midnite Solar MN5048 Inverter/Charger 16) 235AH Crown CR235 8) Hanwha Qcell Peak Duo 350watt
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed