Array 1-- 12 Sunpower 250, Outback FM 100 3kw
Array 2-- 12 Sunpower 250, Outback FM 100 3kw
Well array 780w, 6 Kyocera 130 w with Grundfos sqflex 11 and cu200 to elevated storage, ( 2- 330 g tanks,) no battery storage at well
10 24 volt Battle Born Lithiums
Outback Flexpower Two, VFXR 3524A 7kw
Comments
-
I have a fp1 36/48 I’m just 120 volt , I connect to my ac in , then there is a setting in the mate for Grid or generator power and watt setting , I don’t see why you can’t connect you generator to one leg of the ac in and charge with just your master inverter charger .A 3000watts generator is not large enough to run both chargers any way .
I charge with a 2800 watt Honda generator and set my ac input to 2000wats so I have some head room to power loads in the house .To run both inverters I believe you do need a generator With 240 out put . JohnOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
If you look at the quick start guide it is pretty clear that there is grid and generator power coming in to the ac in ,and you would need a transfer switch between them .I think all the out back inverters are 120 volt and you need 2 inverters to get 240 volt so your generator should work on on legOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .
-
My Outback VFXs can be stacked in a series (120/240 split phase), OR 120v parallel mode. If needed, the change in mode would be done with a mate display, and I'm pretty sure needs a hub for stacking comms. Did they come with the mate and hub?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
No Please...Depends on if you wire for 240vac directly. Most do BTW."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Thank you all for the advice, I was offline for a couple of days while living on genny and wiring this thing. All seems well. I went 240, and have two extra FM80s hanging for the future expansion.
Off grid, all solar, passive and active (winter wood heat supplements) PV DHW.
Array 1-- 12 Sunpower 250, Outback FM 100 3kw
Array 2-- 12 Sunpower 250, Outback FM 100 3kw
Well array 780w, 6 Kyocera 130 w with Grundfos sqflex 11 and cu200 to elevated storage, ( 2- 330 g tanks,) no battery storage at well
10 24 volt Battle Born Lithiums
Outback Flexpower Two, VFXR 3524A 7kw
-
Sweet looking set upOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .
-
Thanks wellbuilt.
So I'm working out plans for lightning, surge protection at the flexpower2. Adding whole house at the square d service panel. I think I am allowed to double tap a double pole for that?Anyway the inverters have surge protectors factory installed. Good on Outback, but do these somehow protect the charge controllers also? I could crack it open and try to trace wires but I am on the other side of the planet right now. I have a few Delta aresstors left from original install, should I put those on the cc? Also where would you station something on the generator incoming ac?THANKS IN ADVANCE.
BTW I cross posted this on Outback forum yesterday.Off grid, all solar, passive and active (winter wood heat supplements) PV DHW.
Array 1-- 12 Sunpower 250, Outback FM 100 3kw
Array 2-- 12 Sunpower 250, Outback FM 100 3kw
Well array 780w, 6 Kyocera 130 w with Grundfos sqflex 11 and cu200 to elevated storage, ( 2- 330 g tanks,) no battery storage at well
10 24 volt Battle Born Lithiums
Outback Flexpower Two, VFXR 3524A 7kw
-
I added serge protection at my 200amp sq d panel ,
I have a delta SP on my combiner box out side, and one on the Fm 80 inside .I also have one for the ac side of things .My generator is 100 plus feet away but it’s grounded to the ground bar on the ac side of the panel so I think I’m covered there , I
dont get much lightning here but there are a few good storms a year .Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed