New to me FLEXpowerTWO
zozomike
zozomike Solar Expert Posts: 134 ✭✭✭
FLEXpowerTWO wiringJPG
Hello, I have been off-grid with one VFX3524 and 2 FM 80s for 8-10 years, (self-assembled). When I started, there were no installers in my remote area, and now the few new ones are shy to come up here. Like many others, I needed to add a third?/fourth string. Anyway, so, Now in transition, and I found a used FLEXpowerTwo, ( 2-VFX3524s) and three FM80s, three years old, went to Arizona, picked the monster up and hung it on the wall. I feel pretty confident about everything until I get to the AC panel out. What seems to confuse me on this diagram I think I attached, is the two hot legs from what is called the AC distribution panel. I am hoping that is shown for a grid-tie application? I am hoping I can just bring my Honda EU3000is into AC leg in, and Neutral/ground and the inverters will charge from that? ( 120/40 vac only from genny) Am I setting up some kind of weird com error? Does the system require 240 VAC for charging? ( say no please)
Off grid, all solar, passive and active (winter wood heat supplements) PV DHW.
Array 1-- 12 Sunpower 250, Outback FM 100 3kw
Array 2-- 12 Sunpower 250, Outback FM 100 3kw
Well array 780w, 6 Kyocera 130 w with Grundfos sqflex 11 and cu200 to elevated storage, ( 2- 330 g tanks,) no battery storage at well
10 24 volt Battle Born Lithiums
Outback Flexpower Two, VFXR 3524A 7kw
  • wellbuilt
    wellbuilt Solar Expert Posts: 763 ✭✭✭✭
    I have a fp1 36/48  I’m just 120 volt , I connect to my ac in , then there is a setting in the mate for  Grid or generator power  and watt setting , I don’t see why you can’t connect you generator to one leg of the ac in and charge with just your master inverter charger .
    A 3000watts generator is not large enough  to run both chargers any way .
     I charge with a 2800 watt Honda generator and set my ac input to 2000wats so I have some head room to power loads in the house .
      To run both inverters I believe you do need a generator With 240 out put . John
  • wellbuilt
    If you look at the quick start guide it is pretty clear that there is grid and generator power coming in to the ac in ,and you would need a transfer switch between them .
      I think  all the out back inverters  are 120 volt and you need 2 inverters to get 240 volt so your generator should work on on leg
  • Estragon
    My Outback VFXs can be stacked in a series (120/240 split phase), OR 120v parallel mode.  If needed, the change in mode would be done with a mate display, and I'm pretty sure needs a hub for stacking comms.  Did they come with the mate and hub?
    Dave Angelini Solar Expert Posts: 7,038 ✭✭✭✭✭✭
    No Please...Depends on if you wire for 240vac directly. Most do BTW.
  • zozomike
    Thank you all for the advice, I was offline for a couple of days while living on genny and wiring this thing. All seems well. I went 240, and have two extra FM80s hanging for the future expansion.
  • wellbuilt
    Sweet looking set up
  • zozomike
    Thanks wellbuilt.
    So I'm working out plans for lightning, surge protection at the flexpower2. Adding whole house at the square d service panel. I think I am allowed to double tap a double pole for that?
    Anyway the inverters have surge protectors factory installed. Good on Outback, but do these somehow protect the charge controllers also?  I could crack it open and try to trace wires but I am on the other side of the planet right now. I have a few Delta aresstors left from original install, should I put those on the cc? Also where would you station something on the generator incoming ac?
    THANKS IN ADVANCE.
    BTW I cross posted this on Outback forum yesterday.
  • wellbuilt
    I added  serge protection at my 200amp sq d panel ,
    I have a delta SP on my combiner box out side, and one on the Fm 80 inside .
     I also have one for the ac side of things .
     My generator is 100 plus feet away but it’s grounded to the ground bar on the ac side of the panel so I think I’m covered there , I
     dont get much lightning here but there are a few good storms a year .