Flip top battery vent caps?
ligwyd
Registered Users Posts: 210 ✭✭
Anyone had any experience with flip top battery vents caps?
Seems a little pricey but if they do reduce watering and misting and make it easier to inspect and add water, over time, might be worth it?
The company that makes these caps say that the tallest version of this type of cap can reduce watering even further, due to the larger/longer condensation chamber? Has anyone out there tried both? It seems that people are going for the standard height cap since that is all I can find for sale from different vendors.
Also, reading up on these caps, it is mentioned that they can stay closed even during equalization? It would seem wise to open the caps during EQ but if these caps are designed to re-combine the gas into water even during EQ that sure would be cool?
Any thoughts?
Comments
-
Water Miser caps are just little plastic balls that help collect the mist and drip it back into the battery electrolyte. There are (or at least were, 3 different heights of caps--Taller cap, more "scrubbing of the mist").
https://www.solar-electric.com/batwatmiscap.html
https://www.flowsystemsusa.com/compare.html
As far as I know, there is no reaction inside the caps, so you should not have to open them when EQ charging (unless you have too high of electrolyte level and/or too much EQ current and "boiling water" into the cap itself).
Then there are Hydro Caps... These have a catalyst inside them (some noble metal) that "burns" or recombines the hydrogen and oxygen gasses back into water. During EQ, it is possible to overheat the caps.
Also, even though the catalyst is supposed to not be consumed, in real life, the catalysts do wear out and will only last 5 to possibly 10 years. And the more EQ you do (hydrogen generation), the faster they will wear out:
http://hydrocapcorp.com/contact-us/faq/
Note that many AGM batteries have catalysts internally mounted too... Over charging can make the top of the cell/battery warm/hot. And too much gassing/high voltage charging can wear out the catalysts faster in AGM batteries too.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
These caps came with my GB forklift battery. Each cap has a orange float indicator that shows water level, they work great and can be left closed while EQ ing. the batteries were shipped with water level low so the orange float in picture is down.
George have a nice dayOff grid for 20 years. 5KW panels, Trace sw4024, Bergy XL1 wind generator, 3 EG4 Lifep04 200amphr batteries 3 SQF 2 well pump, 12kw back up gen. Not easy living in the wilderness but it keeps you busy -
Thanks for the info George.Bill, would you say the hydro caps return a lot more water to the battery or do the water miser come pretty close without catalyst?I'll contact hydro cap Mon for prices. Sure can buy a lot of distilled water for the prices of some of these caps?
-
I don't know the comparisons between them.. Hydro caps can be expensive and variable availability (price of pladium?).BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
I used hydrocaps back in the 90's, You do have to remove them while equalizing, saw an advantage right away, but didn't last more than a year or so, but I was new and the batteries do tend to use more electrolyte as they age, I haven't bought them again.
I do use watermisers, I find them very handy! makes quick work of checking levels. I have the medium tall ones. My GB forklift battery didn't come with fancy caps 8 years ago... So say they have a hard time seeing with tall caps. Mine have never been a problem, but I might have gotten use to them.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
As to a comparison, I added the hydrocaps after about a year, don't think I had to add water for most of the first year after, but was back in routine sometime the 2nd year.
Forklift batteries tend to use more electrolyte. I added watermiser caps when I got the battery and I have routinely leveled off month. I only keep electrolyte about 1/4" above the 'splash guards'. I do bring it up when I will be gone for vacation...fwiw.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Do the water miser caps considerably lessen the amount of watering that batteries require (even thought they do not have catalyst?Also, when the batteries are being equalized, if the high hydrogen concentration is not allowed to dissipate isn't that a ticking bomb waiting for a short from an aging battery?
-
Hoppecke claims 99% reduction of water loss with their AquGen caps, at a price €42.4 apiece, perhaps viable using large > 1000Ah 2V cells. The catalyst is probably responsible for much of that, without a catalyst the efficiency would probably be greatly reduced, just a speculation.
Hydrogen is a potentially hazardous as it can ignite without a spark even in the absence of oxygen, this is why it is important to ventilate confined spaces holding lead acid batteries, particularly flooded but not limited to, AGM can also vent if overcharged but the potential is greatly reduced. The gas combination of hydrogen oxygen mix trapped inside flooded cells above the electrolyte is a bomb waiting for a source of ignition and should be treated with respect, even the smallest spark could ruin your day if conditions are met. See attached pdf1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Sounds like it may be wise to let the battery breath during EQ, despite others that claim it is safe not to? Err on the side of caution....?I do have Two power vents that exchange the air in the battery box also. I'll check out the Hoppecke vents. Thanks for the info.
-
My original setup had Hydro Caps. They have a life expectancy too short in my opinion. Mine lasted only 2 years or so. First one would quit (not be warm on charging), then another...soon all were cold. They gave a nice hand grip for removing though. I'm not using them on my L16's, there's not enough room on the top of the battery to comfortably get your hand in for working with them. Just the caps the batteries came with seems to work fine. I have my own distiller for making top up water.
-
ligwyd said:Sounds like it may be wise to let the battery breath during EQ, despite others that claim it is safe not to? Err on the side of caution....?
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed