Battery charging
mountainman
Registered Users Posts: 442 ✭✭
If in full sun absorb set at 14.8 volts.
after 2 hours showing 1℅ 4 amps on 400 ah Batteries. Why would S.G be 1.250?
2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
What is the fill SG from the manufacturer? Some use lower SG to extend lifespan at the expense of slightly lower capacity.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Us battery states 1.270 minimum S.G.2kw array 6 345 q cells make sky blue 60 cc
18 amp accusense charger. 3650 champion -
Batteries are not using any water. Maybe I should try raising voltage?2kw array 6 345 q cells make sky blue 60 cc
Are you using temperature compensation and are the batteries cold?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Yes I have temp compensation. Batteries are out side. Temps lately have been 35- 40 f at night. 60 f days. Daily useage ~15℅2kw array 6 345 q cells make sky blue 60 cc
Have you checked voltage in absorb at the battery? At ~50°F, it should be higher than the 14.8v setting.
Also, have you measured SG at 1.27 with this meter on these batteries previously? My first meter measured consistently low.Off-grid.
If I'm away for a sunny weekend not running the inverter. SG goes up to 1.27.
checking the absorb voltage on a 40f day
~14.9.2kw array 6 345 q cells make sky blue 60 cc
Assuming that's 14.9 at the battery, sounds about right. If it's at the controller, I'd check at the battery as well.
Are the batteries sort of fizzing a bit with a few "burps" near the end of absorb?Off-grid.
Yes on the battery. Ive looked inside the batteries and they are fizzing and occasionally they will burb. The part that puzzles me is not using water. I bought them July 1 of this year. In the summer daily SG was good unless of course it was over cast.2kw array 6 345 q cells make sky blue 60 cc
My L16s hardly used any water at first. IIRC, well under a gallon in the first 6mos. At 5yrs, they're up to ~2-3gals/season.
If they're bubbling, I wouldn't increase voltage. Assuming the 1% / 4a read was net into the bank (ie not reduced by loads), I don't know why SG would be that low.
Are the cells consistently 1.25?
Could the meter be sticking? Sometimes a bit of crud finds its way in, requiring pretty vigorous rinsing to clear.Off-grid.
Yes end absorb 4 amps 400 ah Batteries with no loads.
Like I said if Im away a couple days not using any power.
SG comes back to 1.2702kw array 6 345 q cells make sky blue 60 cc
My arrays are 380 on mppt range is 20-24 amps on ~70℅ soc. And 400 on pwm 22-24.52kw array 6 345 q cells make sky blue 60 cc