Connecting battery banks
mountainman
Registered Users Posts: 439 ✭✭
With 2 separate systems. 1 array on 2 gc batteries. And another array charging 2 of the Same type gc batteries. Could I connect all 4 batteries at night?. Or would there be consequences?
2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
Comments
-
Connecting the batteries in parallel that have been charged, possibly discharged seperately, may well be at different state of charge, this may cause massive amounts of cascade current into the bank of lower capacity, causing arcing at the connection points which could result in explosion of hydrogen if done on the terminals of flooded lead acid batteries, or damage to switch gear if done remotely.
The better solution would be to permanently connect the battery banks in parallel, and charge as a single bank with two separate controllers / arrays. The one problem with doing this retrospectively however, is that the batteries may be of different age and residual capacity which would cause imbalances between strings. This configuration is better if done when all batteries are new and identical make and capacity.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
@mountainman, It appears that you have 4 identical GC Batteries. Is that true? Costco sells 6V 208AH GC2 batteries. Is that what you have? Is there a reason why you have two smaller battery banks, and not one large battery bank? How old are these batteries? I don't understand why you decided to parallel connect the batteries at night, but separate the banks during the day.
With two charge controllers on one large bank, verify that you do not equalize twice as often. -
@mvas I have 4 identical us battery 208 ah. Problem is on 1 system I have a 30 mppt that is adjustable. The other systems pwm controller that's not adjustable. In the Morning both controllers play well together.
But by 11-12 the pwm stops. And only the mppt is producing power. So by charging the bank separately only 2 batteries to each controller i get more whs per day. I'm not home during most days so all my power needs are at night. I think the fix is to get 2 of the same adjustable controllers. And no I manually eq only when necessary.2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
Why not connect the panels to 1 large enough controller? That would be simpler.@mcgivor's concern about massive current flow would only be a concern if 1 battery was very close to dead.What you have is actually not a bad way to deal with parallel systems, you can make sure each bank is getting charged up.
-
It probably doesn't make a lot of difference that the pwm stops around noon, just that the other controller is finishing absorb and maybe doing the float. The current required is lower anyway, so as long as the one controller is doing a full absorb, not really an issue.
Even with my two networked classics, one will produce more than the other to absorb/float the bank.
Unless there's some other reason to split the bank, I'd keep it as one. It should take whatever total whs it takes to charge the batteries, and be about the same with the bank split or as one. Assuming the pwm absorb setting isn't optimal for your batteries, it might be better for them to have the controller with more appropriate voltage do the absorb for them all, IMHO.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
@Estragon would it be a good idea to aim the pwm system in a sse direction and leave the highest voltage mppt system in the south position or aim those in a sse position for virtual tracking?
@papab like many people. in the beginning I didn't have a clue what solar could do or how much my loads where.
I looked at grid tie panels and shipping cost more than the panels for a small system.
So free shipping 4 100 watt panels and a pwm cc cost me $500. Then I realized it was over 100 foot from the camper in the shade to where the sun was. So it was cheaper to buy a epever 30 than large pv cables.
Then I added an inverter. TV and box fan then stereo.
I found that 400 watts on 400 ah wasn't enough even for a part time summer system.
I located 2 190 gt used panels local pick-up.
4 36 cell 100 watt panels and 2 60 cell 190 panels where not a good match for 1 controller. And the cost of a 60 amp 150 volt.
Was very expensive.
Since I already had 2 cc I used what I had.
Plus with 2 if 1 broke. I wouldn't be in the dark with no access to power lines.
I located 2 100 foot runs of direct burial 8 awg used house wire for free for the pwm.
That gave me 16.9 volts to the controller.
2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
Having the pwm sse might work well. That would get you current for bulk charging a bit earlier, with the mppt adding more later. Assuming you get to absorb before ~noon, the mppt in full sun could finish absorb then float.
I have shading to the east, and main arrays facing a bit west of south. They're tilted steep, and produce much less later in the day. I also have small pwm arrays tilted vertical and facing more west. The small arrays are mainly for winter if/when the main arrays get snow covered, but also help by providing power to keep banks floating later than would otherwise be the case. Sort of the opposite of your situation, but the same general idea.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Thanks think I'll try the sse on pwm and see how it works out.2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
mountainman said:
I have a 30 mppt that is adjustable. The other systems pwm controller that's not adjustable. In the Morning both controllers play well together.But by 11-12 the pwm stops. And only the mppt is producing power.
Better than having the PWM constantly undercharge 2 batteries, while the other 2 get good charges.
-
The pwm is locked at 2 hours absorb at 14.6. the mppt is limited 3 hours at 14.8. personally I haven't seen a great advantage with mppt vs pwm in output.
Yes much more adjustable better for longer distance pv arrays. And you can use various panels.
But so far I've only used solar for summer. Seems ive read mppt shine's in winter.
2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
Just a random thought. If running different oriented arrays on mppt is a bad idea. With my mppt array facing south.
And my pwm Array all in parelell with 2 panels facing sse and 2 facing ssw work.
2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
PWM can be oriented in any way, and simply parallel to the limits of the controllerThis is so clumsy to try to explain fully, and I'm too tiredPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Thanks Mike2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed