I cant find a status screen on the KID that shows amps from the panel  BEFORE the KID changes them into a lesser amount..
is there a way to see that on the screen...?

Comments

  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    Just to clarify, the kid will(should) INCREASE amps coming from the panels, by decreasing voltage.  For example, 5a at 36v (180w) from panel bucked to ~10a at 18v charging (made up voltages for easy numbers).
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • ws9876
    ws9876 Solar Expert Posts: 448 ✭✭✭
    I measured 6 amps before I hooked up the KID. But I want to check again. I have an AGM small battery on it for now just for
    learning the KID. But its only bulking at .5 amp and floating at .1 amp roughly. But the battery is not being used so it doesnt get below 14.4 volts. It would be good to see the panel amps without disconnecting the wires.I wonder if it screwed up. I might disconnect the wires and check the amps again. I sure havent seen any 10 amps ...maybe I should drag the battery down and then check it..
  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    edited October 2019 #4
      @ws9876 said  ..maybe I should drag the battery down and then check it..

    That's exactly what you need to do, just adding a load to the battery will prompt the controller to begin production, a load greater than the arrays capacity will reveal the maximum current available.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • ws9876
    ws9876 Solar Expert Posts: 448 ✭✭✭
    its up to 5 amps now....I turned on the inverter....problem solved.