Real world power from stated voltage level
softdown
Solar Expert Posts: 3,915 ✭✭✭✭
I'd think there is a bell curve, of sorts, that shows how much power is really available at various voltage levels. For example, the difference between 13 volts and 12.8 volts is almost nothing. Voltage above 12.8 is a "surface charge" and evaporates quickly.
To me it seems like it is pretty easy to draw a battery down to ~12.5 volts. Then the "meat" of the battery power prevents farther voltage drop from occurring so readily. At the other end of the scale, any voltage below ~ 11.6 represents a battery that is pretty well dead.
My suspicion is that ~80% of a typical 12 volt battery charge is found in between ~12.6 volts and 11.6 volts.
My other suspicion is that 12 volts is closer to 50% charge/discharge than 12.2 volts. But I'm a rabble rouser often seeking to challenge "established dogma".
To me it seems like it is pretty easy to draw a battery down to ~12.5 volts. Then the "meat" of the battery power prevents farther voltage drop from occurring so readily. At the other end of the scale, any voltage below ~ 11.6 represents a battery that is pretty well dead.
My suspicion is that ~80% of a typical 12 volt battery charge is found in between ~12.6 volts and 11.6 volts.
My other suspicion is that 12 volts is closer to 50% charge/discharge than 12.2 volts. But I'm a rabble rouser often seeking to challenge "established dogma".
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
Comments
-
This chart begs to differ. Perhaps they are right. This seems to represent established dogma.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
Once you get past the residual surface charge, lead acid has a very linear discharge curve and voltage is a good indicator of SoC. Specific Gravity even better when configuring your system setpoints.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
I think the shape of the curve would also depend on the rate of discharge. At high discharge rates, I'd expect apparent capacity to drop off faster at lower voltage / higher current. At slow discharge rates, I'd expect the apparent capacity to be pretty linear, as in the chart above.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Here is an article about battery voltage vs current (charging and discharging, different C/x values):
https://www.scubaengineer.com/documents/lead_acid_battery_charging_graphs.pdf
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB. said:Here is an article about battery voltage vs current (charging and discharging, different C/x values):
https://www.scubaengineer.com/documents/lead_acid_battery_charging_graphs.pdf
-BillFirst Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Voltages are design specific. I deal with AGM's that show 2.166c/cell @ 100% and 1.75v @ 0% SOC under load.That same battery at 0% SOC will read 1.93v as a standing voltage.Example: If I drag a fully charged 12v battery down to 0%, it will read 10.5v at 0% SOC under load. almost regardless of the size of the load. Extremes like C/0.5 or C/1000 can be corrected for. Remove the load and wait, and that same battery will rebound to 11.6v over time. It is still a dead battery at 0% SOC. WAAAY too many people don't get this part! I can assure you that my customers know it well.The operating voltage at various loads, charge level and temperature is published data from at least one manufacturer that I work with.Properly designed off grid systems allow some level of autonomy, generally 2-3 days depending upon specific needs. The C/1 to C/10 rating would be more tailored to a UPS or industrial type application.Edit to add a rough chart to help explain the conceptMarcI always have more questions than answers. That's the nature of life.
-
13 volt AGMs? Huh. Did they juice up the SG? Or magic pixel dust?First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
softdown said:13 volt AGMs? Huh. Did they juice up the SG? Or magic pixel dust?
You would have to call Concorde to ask about magic dust. Been the same for at least 14 years that I know of and verified by my own experience. Concorde is a respected aircraft battery manufacturer and very engineering oriented. I am not a battery engineer, but I know what their batteries can and cannot do, and how they perform in real life applications.
I always have more questions than answers. That's the nature of life. -
C/X energy design really depends on your electrical needs... Just as an example, say you want to use power in the evenings, 5 hours per night, for 2 nights (poor weather during the day) and 50% maximum discharge... That means 10 hours running * 1/0.50 max discharge = 20 hour discharge rate.
When you run a refrigerator... Say 1/3rd duty cycle (or 20 minutes per hour) for 2 days/50% max discharge:- 1/3 rd duty cycle * 24 hours = 8 hours per day running
- 8 hours * 2 days storage * 1/0.50 max discharge = 32 Hour discharge cycle (to run a fridge, 2 days, 50% discharge, 1/3rd duty cycle)
- 2 hours running * 2 days * 1/0.50 max discharge = C/8 discharge rate...
If you have 24 hour per day loads, 2 days storage * 1/50% discharge * 24 hours = 72 hour discharge rate...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed