terminal blocks

Options
ws9876
ws9876 Solar Expert Posts: 440 ✭✭✭
I have an old Franklin well control box for a 2hp submersible pump. It says on it max 14 amps and its 230v.
It has a block in there to join wires coming and going. It looks substantial. Do you think there would be a problem using it in a 120v
circuit requiring 30 amps max.Like a charge controller?

Comments

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Options
    Don't use it.   If it's rated for 14A, why would you think 30A would be safe, that over 100% overload !!
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • rgk1
    rgk1 Solar Expert Posts: 134 ✭✭✭
    Options
    mike95490, this brings up a probably silly question but one I have often had in passing.  In reference to protection, is an amp just an amp no matter the voltage?
    4-Risen 320 watt in series/parallel, 8-215ah 6 volt GC2 batteries in series, Exeltech 1100 watt/48 volt inverter, Tristar 45 MPPT controller.
  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    edited August 2019 #4
    Options
    An amp is an amp, the voltage rating however has to do with dialetric strength, which is why a maximum voltage is used in conjunction with the amp rating. The AC current  rating would not be the same as DC current , DC could sustain an arc in a fuse designed for AC still allowing current to flow even when the element has failed. AC is sinusoidal, meaning  that current and voltage will be at a zero potential 50 or 60 times per second depending on frequency, 50 or 60Hz, it's this cycling that allows the arc to quench, so if there is no specific DC rating and only an AC rating assume it's not compatible 

    With regards to circuit breakers, AC circuit breakers are generally not compatible with DC, there are a few exceptions, if they are rated for both they will have markings stating so, just like fuses.

    Any eloborations welcome.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • littleharbor2
    littleharbor2 Solar Expert Posts: 2,044 ✭✭✭✭✭
    Options
    mcgivor said:

    With regards to circuit breakers, AC circuit breakers are generally not compatible with DC, there are a few exceptions, 
    The Square D QO line of circuit breakers being one exception. There is plenty of documentation online regarding their DC compatibility if you take the time to search the companies website.. The various QO models have varying DC voltage limits.

    2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old  but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric,  460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.

  • icarus
    icarus Solar Expert Posts: 5,436 ✭✭✭✭
    Options
    I believe that the OP is pondering using the TERMINAL strips of the above mentioned Franklin box, not the breaker.  That said, IMHO if the lugs are substantial and fit the wire sized I wouldn’t really have a problem with it.  You can always check the lugs under load with a IR thermometer to see if they are heating abnormally.  I agree 100% about the breaker oversize however if I am wrong on my assumptions.

    Tony