Using Generator Support With The Schneider Conext XW+6848 Inverter
neutronspin
Registered Users Posts: 51 ✭✭
New install on the XW+ inverter and want to do generator testing. What settings are needed to do the test? I suppose enabling the setting "Generator Support Enable" and setting the Generator Support amps are necessary but are there any other settings I may have missed? Right now the inverter is setup in Grid Support mode. What is the procedure for putting the generator online without an AGS doing it manually? Or do I need an AGS box to manually start and test the generator? This system uses an electric start push-button generator to start the unit. Thanks....
Comments
-
The default setting for generator input is 140 amps, which will stall anything but the biggest generator. There are two issues here, what the generator can output, and what the XW will qualify. You'll need to go into the system control panel settings and lower the max charge rate to some initially low setting, say 15-20%. As power is brought in, the XW looks at the voltage/frequency/stability, and decides whether or not the generator power is "qualified" for use by the XW. I have a 6.5kw AC-Delco, and my XW won't qualify more then about 36% from it. That's 36% of 140 amps, which = 50amps, as much as I'd want to go into my batteries. When I want to charge my batteries I use 32%, which is about right for L-16s. You can tell by the sound of the generator if the XW has dropped it. The sound will drop from its "loaded" sound to the sound of it idling.
System 1) 15 Renogy 300w + 4 250W Astronergy panels, Midnight 200 CC, 8 Trojan L16 bat., Schneider XW6848 NA inverter, AC-Delco 6000w gen.System 2) 8 YingLi 250W panels, Midnight 200CC, three 8V Rolls batteries, Schneider Conext 4024 inverter (workshop) -
MichaelK said:The default setting for generator input is 140 amps, which will stall anything but the biggest generator. There are two issues here, what the generator can output, and what the XW will qualify. You'll need to go into the system control panel settings and lower the max charge rate to some initially low setting, say 15-20%. As power is brought in, the XW looks at the voltage/frequency/stability, and decides whether or not the generator power is "qualified" for use by the XW. I have a 6.5kw AC-Delco, and my XW won't qualify more then about 36% from it. That's 36% of 140 amps, which = 50amps, as much as I'd want to go into my batteries. When I want to charge my batteries I use 32%, which is about right for L-16s. You can tell by the sound of the generator if the XW has dropped it. The sound will drop from its "loaded" sound to the sound of it idling.
-
No grid here, but I have my genset settings as follows:
- Generator Support Enable Enabled
- Generator Support amps 13.5 A (each breaker is only @ 120V so both will add, this setting = a limit internally derated to 2515w)
- Generator Support PLUS Enabled
Gen 1 settings- ST5 on lister 6/1
- AC2 Breaker Size 18.5
- Generator Support amps 13.5
Backup generator settings (using a 115lb autotransformer to get 240VAC)- Honda EU2000i spec 13A 1600w cont, 2kw 30 min
- AC2 Breaker Size 9.0
- Generator Support amps 5.0
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
mike95490 said:No grid here, but I have my genset settings as follows:
- Generator Support Enable Enabled
- Generator Support amps 13.5 A (each breaker is only @ 120V so both will add, this setting = a limit internally derated to 2515w)
- Generator Support PLUS Enabled
Gen 1 settings- ST5 on lister 6/1
- AC2 Breaker Size 18.5
- Generator Support amps 13.5
Backup generator settings (using a 115lb autotransformer to get 240VAC)- Honda EU2000i spec 13A 1600w cont, 2kw 30 min
- AC2 Breaker Size 9.0
- Generator Support amps 5.0
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed