Honda generator question

Options
Desert Rat
Desert Rat Solar Expert Posts: 138 ✭✭✭

A neighbor gave me a Honda EU2000i generator. In checking it out, I get 125 VAC with my voltmeter when connected to the HOT and NEUTRAL of the receptacle. But only 62.5 VAC when connected to HOT and GROUND. What gives?

Comments

  • Desert Rat
    Desert Rat Solar Expert Posts: 138 ✭✭✭
    Options

    OK, I realized that Neutral and Ground are not bonded in this generator. Did I answer my own question?

  • BB.
    BB. Super Moderators, Administrators Posts: 33,439 admin
    Options

    Yes