Conext ComBox Giving Wrong Battery Output Wattage

Has anyone seen a Conext ComBox give wildly crazy readings for the battery output wattage? All other numbers seem to be reasonable (including wattage INTO the battery when it is being charged), but the output number is ALWAYS crazy. According to this, I would think that it should read 15-16W.
Comments
That's a lotta watts !! Hopefully just a display render error
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
In my wildest dreams! The Volts and Amps displayed below the battery graphic seem to be reasonable/correct. But the displayed wattage is obviously way out of the realm of reality. I have put in a support question to Schneider.
The first suggestion is to cut all power and do a controlled shutdown of the whole system for five minutes then restart {including disconnect of the data bus and Ethernet cables... If you have power over Ethernet).
Bill
I will try this tonight. It's just extremely odd that only one data point is wrong....
All it takes is one bit in the register in the wrong state. If it's in RAM, a cold reboot may fix.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Hard reset on the inverter did nothing to the reporting error of the ComBox application. I'm going to see if a firmware update of the inverter will correct this. The ComBox has the latest firmware already (thankfully, I just purchased it!).
I did discover, however, that I have a faulty charge controller; but that is a subject for another thread! ;-)
Firmware update fixed the reporting issue. Everything looks like it should at this point. Thanks for your thoughts on this.